Slight electric shock
Today I was changing some sockets, just a like for like replcament and so I switched off the mcb for that circuit and the RCD as well.
When removing one of the sockets I received an uncomfortable tingle from one of the neutrals
Any ideas why ?
When removing one of the sockets I received an uncomfortable tingle from one of the neutrals
Any ideas why ?
- ultimatehandyman
- Site Admin
- Posts: 24407
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 999 times
- Been thanked: 915 times
-
- BANNED
- Posts: 2136
- Joined: Wed Jan 18, 2006 10:48 pm
- Location: Leicestershire
- Has thanked: 0
- Been thanked: 1 time
-
- Senior Member
- Posts: 376
- Joined: Sun Jul 17, 2005 11:38 am
- Location: Newcastle
- Has thanked: 0
- Been thanked: 0
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
- ultimatehandyman
- Site Admin
- Posts: 24407
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 999 times
- Been thanked: 915 times
I bought an house 6 years ago and it had a socket wired into the consumer unit, I am pretty sure that the live was on the rcd side and the neutral was on the non rcd side. Or perhaps they were the other way around ?
It never tripped out once!
One day I was installing some more sockets and switched off the rcd, not sure about the mcb, but probably that too! and I got a tingle from the neutrals, I asked the sparks at work and he told me to check the consumer unit and I found the wire that was wired to the wrong side.
I thought that honeymonsters problem could of been something similar
It never tripped out once!
One day I was installing some more sockets and switched off the rcd, not sure about the mcb, but probably that too! and I got a tingle from the neutrals, I asked the sparks at work and he told me to check the consumer unit and I found the wire that was wired to the wrong side.
I thought that honeymonsters problem could of been something similar
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
Hiya Chezultimatehandyman wrote:I bought an house 6 years ago and it had a socket wired into the consumer unit, I am pretty sure that the live was on the rcd side and the neutral was on the non rcd side. Or perhaps they were the other way around ?
It never tripped out once!
One day I was installing some more sockets and switched off the rcd, not sure about the mcb, but probably that too! and I got a tingle from the neutrals, I asked the sparks at work and he told me to check the consumer unit and I found the wire that was wired to the wrong side.
I thought that honeymonsters problem could of been something similar
If the neutrals were on the RCD and the live wasn't, You then switched off the RCD, meaning the neutral was isolated and the live was still on then yes you would get a belt from the neutral, because the live is still there. But if HM was correct in what he is stating then he should not have felt anything.
Only other thing would cause it is a neutral borrowed from another circuit.
- ultimatehandyman
- Site Admin
- Posts: 24407
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 999 times
- Been thanked: 915 times
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
The other thing with the RCD. It works by monitoring the live and neutral for imbalances. So for a 30ma RCD Any imbalances which equates to 30ma of fault current would be monitored by the RCD and trip out.
So having the live on one side and neutral on the other would cause an imbalance between live and neutral and trip out.
I've seen it more often than enough after consumer unit changes with kitchen fitter wiring etc.
So having the live on one side and neutral on the other would cause an imbalance between live and neutral and trip out.
I've seen it more often than enough after consumer unit changes with kitchen fitter wiring etc.
- ultimatehandyman
- Site Admin
- Posts: 24407
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 999 times
- Been thanked: 915 times
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
-
- Senior Member
- Posts: 376
- Joined: Sun Jul 17, 2005 11:38 am
- Location: Newcastle
- Has thanked: 0
- Been thanked: 0
-
- BANNED
- Posts: 418
- Joined: Fri Oct 27, 2006 5:40 pm
- Has thanked: 0
- Been thanked: 2 times
Get your RCD checked.
If you have L&N wired to different sides of the split then you are absolutely 100% cast-iron copper-bottomed scout's-honour guaranteed to get an imbalance and a trip.
If you have L&N wired to different sides of the split then you are absolutely 100% cast-iron copper-bottomed scout's-honour guaranteed to get an imbalance and a trip.
I'm sorry - I can't come in to work today, the voices are telling me to stay at home and clean the guns.