hi

I have moved my washing machine and freezer to the adajent shed in my house this is more like a conservatory as it totaly sealed and water tight room, i wish to add one socket to power a freezer and the washing machine plus a light would running 2.5mm SWA from comsumer unit outside burried in polypipe (distance 6m) to a connection box with terminals be ok for this and SFU with a 3 amp fuse for the light bulb be suffice. The circuit will be on its own RCD or MCB but whatever is best (please quote).
Would this be ok and when i get a sparks to come and check or would he say it is unsafe?

Any help would be recicved with great thanks.


Top
 Profile  
 
 Post subject: Re: wash room Help
PostPosted: Sun Oct 30, 2011 11:08 am 
Offline
Senior Member

Joined: Sun Jan 24, 2010 1:48 pm
Posts: 4152
Location: Essex
Has thanked: 2 times
Been thanked: 327 times
That falls under part P. You are not able to get an electrician in to certify it as they can only certify there own work and not some one elses.

If you do the work you need to notify the council and then get it inspected by them on completion and they will sign it off.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Re: wash room Help
PostPosted: Sun Oct 30, 2011 11:32 am 
Offline
Newly registered Member

Joined: Sun Oct 30, 2011 9:46 am
Posts: 4
Has thanked: 2 times
Been thanked: 0 times
royaloakcarpentry wrote:
That falls under part P. You are not able to get an electrician in to certify it as they can only certify there own work and not some one elses.

If you do the work you need to notify the council and then get it inspected by them on completion and they will sign it off.


Ok will do but what i am doing is that a sound pratice or Should it be done in a different mannor ?


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Re: wash room Help
PostPosted: Sun Oct 30, 2011 11:42 am 
Offline
UHM Super Moderator
User avatar

Joined: Fri Jan 27, 2006 10:54 pm
Posts: 1089
Has thanked: 30 times
Been thanked: 55 times
Hi Johnboy :welcomeuhm: .you ask about a wash room, which I believe is an Americanism for "utility room"

Where are you posting from?


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Re: wash room Help
PostPosted: Sun Oct 30, 2011 11:42 am 
Online
Senior Member

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 413
Location: South Yorkshire
Has thanked: 7 times
Been thanked: 66 times
:welcomeuhm:

There would be little point in passing the SWA through polypipe. Use proper black ducting or just bury the SWA into the ground.

Electrically a 2.5mm SWA would be fine to power a double socket and a FCU via a 20 RCBO/or RCD protected MCB in your CU. You do need to to know how to terminate SWA properly though to do the job.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Re: wash room Help
PostPosted: Sun Oct 30, 2011 11:59 am 
Offline
Newly registered Member

Joined: Sun Oct 30, 2011 9:46 am
Posts: 4
Has thanked: 2 times
Been thanked: 0 times
OnlyMe wrote:
:welcomeuhm:

There would be little point in passing the SWA through polypipe. Use proper black ducting or just bury the SWA into the ground.

Electrically a 2.5mm SWA would be fine to power a double socket and a FCU via a 20 RCBO/or RCD protected MCB in your CU. You do need to to know how to terminate SWA properly though to do the job.


Ok i belive you terminate on glands wich bond the steel wire as a earth is this correct i was mainly concerned that i needed a CU in the room as well just for these couple of appliances, and that the light would be ok coming off the same feed thats beena great help thanks.

i am posting from Kent in the uk


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Re: wash room Help
PostPosted: Sun Oct 30, 2011 12:07 pm 
Online
Senior Member

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 413
Location: South Yorkshire
Has thanked: 7 times
Been thanked: 66 times
http://electrical.theiet.org/wiring-mat ... m?type=pdf

is worth a read



For this message the author OnlyMe has received gratitude : johnboy
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Re: wash room Help
PostPosted: Sun Oct 30, 2011 12:39 pm 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 427
Location: North Wales
Has thanked: 6 times
Been thanked: 96 times
By using a switched fuse connection unit as the light switch you get around the problem of having a consumer unit for just two circuits.

As already said likely the 2.5mm cable will be ample. However it will not matter if using LABC direct or if using a registored spark you will need to test the loop impedance before anyone can be 100% as to if it will comply.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 8 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: OnlyMe and 31 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling