Rachel25
Newly registered Member
Posts: 61
Joined: Sat Dec 17, 2016 12:29 pm
Has thanked: 69 times
Been thanked: 0

Bathroom extractor fan wiring

Post by Rachel25 »

Hi guys

I'm wanting to wire a new bathroom extractor fan with a timer and I need some more cable. From the isolator switch I believe I need a live, switched live and neutral cables to go direct to the extractor fan. Would this cable be suitable?

https://www.screwfix.com/p/nexans-heat- ... hite/9488t

It's 3 core 1.5mm.

Any advice greatly appreciated :help: :help:

Rach x
OnlyMe
Approved Electrician
Posts: 3087
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 223 times
Been thanked: 657 times

Re: Bathroom extractor fan wiring

Post by OnlyMe »

These users thanked the author OnlyMe for the post:
Rachel25
Rating: 7.14%
Rachel25
Newly registered Member
Posts: 61
Joined: Sat Dec 17, 2016 12:29 pm
Has thanked: 69 times
Been thanked: 0

Re: Bathroom extractor fan wiring

Post by Rachel25 »

Thank you kindly :salute:
User avatar
Someone-Else
Senior Member
Posts: 14156
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 42 times
Been thanked: 2484 times

Re: Bathroom extractor fan wiring

Post by Someone-Else »

Rachel25 just to add, the reason the cable you listed is wrong is that it is only 3 core, you need 3 core AND earth, not to mention your one is flex, and you should use "rigid" I am not even going to say heat resistance.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
OnlyMe
Approved Electrician
Posts: 3087
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 223 times
Been thanked: 657 times

Re: Bathroom extractor fan wiring

Post by OnlyMe »

someone-else wrote:Rachel25 just to add, the reason the cable you listed is wrong is that it is only 3 core, you need 3 core AND earth, not to mention your one is flex, and you should use "rigid" I am not even going to say heat resistance.

Or using the green/yellow as a switched live :wink: Although that is not exempt from the regs the exemptions would not apply in this case.