Hi guys
I'm wanting to wire a new bathroom extractor fan with a timer and I need some more cable. From the isolator switch I believe I need a live, switched live and neutral cables to go direct to the extractor fan. Would this cable be suitable?
https://www.screwfix.com/p/nexans-heat- ... hite/9488t
It's 3 core 1.5mm.
Any advice greatly appreciated
Rach x
Bathroom extractor fan wiring
Moderator: Moderators
-
- Approved Electrician
- Posts: 3087
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 223 times
- Been thanked: 657 times
Re: Bathroom extractor fan wiring
That cable is not suitable for your job.
You need something like
https://www.screwfix.com/p/prysmian-624 ... grey/43415
or
https://www.screwfix.com/p/prysmian-624 ... grey/9678p
You need something like
https://www.screwfix.com/p/prysmian-624 ... grey/43415
or
https://www.screwfix.com/p/prysmian-624 ... grey/9678p
- Someone-Else
- Senior Member
- Posts: 14156
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 42 times
- Been thanked: 2484 times
Re: Bathroom extractor fan wiring
Rachel25 just to add, the reason the cable you listed is wrong is that it is only 3 core, you need 3 core AND earth, not to mention your one is flex, and you should use "rigid" I am not even going to say heat resistance.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
-
- Approved Electrician
- Posts: 3087
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 223 times
- Been thanked: 657 times
Re: Bathroom extractor fan wiring
someone-else wrote:Rachel25 just to add, the reason the cable you listed is wrong is that it is only 3 core, you need 3 core AND earth, not to mention your one is flex, and you should use "rigid" I am not even going to say heat resistance.
Or using the green/yellow as a switched live Although that is not exempt from the regs the exemptions would not apply in this case.