Installing Electric Wall Heater 1KW or 2KW in Bathroom
Moderator: Moderators
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Installing Electric Wall Heater 1KW or 2KW in Bathroom
Hi
I want to install wall heater in my bathroom which is about 2.7m X 2.8m area size, 1KW will do but most fan heaters are 1KW/2KW adjustable on installation.
I have a cable unused behind an unused mirror in the bathroom and there is a spur fuse above which I believe belongs to it. I have never used this cable and haven't checked the fuse.
My questions are:
1. Is this cable safe enough/sufficient for 2KW heater? if not how about 1KW heater? 9A against 4.5A.
2. How do I check if the cable is live safely?
Photo of cable and spur attached.
Thanks
I want to install wall heater in my bathroom which is about 2.7m X 2.8m area size, 1KW will do but most fan heaters are 1KW/2KW adjustable on installation.
I have a cable unused behind an unused mirror in the bathroom and there is a spur fuse above which I believe belongs to it. I have never used this cable and haven't checked the fuse.
My questions are:
1. Is this cable safe enough/sufficient for 2KW heater? if not how about 1KW heater? 9A against 4.5A.
2. How do I check if the cable is live safely?
Photo of cable and spur attached.
Thanks
- Attachments
-
- IMG_2591.JPG (82.94 KiB) Viewed 5009 times
-
- IMG_2590.JPG (52.99 KiB) Viewed 5009 times
- wine~o
- Senior Member
- Posts: 26176
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 3992 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
I assume you don't have a multimeter so easiest way to test for live is to wire in a bulb holder and see if the lamp works. If so then it's live.
Question ... are there any markings on the cable coming from the wall such as 1.0 1.5 or 2.5 ?
Next with the bulb lit switch off any circuits of 6 A ( marked lighting) at the consumer unit, Does the light stay on or go off ?
Question ... are there any markings on the cable coming from the wall such as 1.0 1.5 or 2.5 ?
Next with the bulb lit switch off any circuits of 6 A ( marked lighting) at the consumer unit, Does the light stay on or go off ?
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
Yes I have multimeter, I will check for V ac between L and N for mains voltage, I will do that tomorrow easier than bulb.wine~o wrote:I assume you don't have a multimeter so easiest way to test for live is to wire in a bulb holder and see if the lamp works. If so then it's live.
Question ... are there any markings on the cable coming from the wall such as 1.0 1.5 or 2.5 ?
Next with the bulb lit switch off any circuits of 6 A ( marked lighting) at the consumer unit, Does the light stay on or go off ?
No marking on cable, spurs has 13A fuse, safe to assume 1.5mm?
Can't see 6A on CU, assume it is the 10A lighting you're referring to, photo attached.
- Attachments
-
- IMG_2592.JPG (273.92 KiB) Viewed 4979 times
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
This cable was added later by previous owner, I believe. So I don't think it is taken from the lighting circuit but will check, probably wire and bulb method is easier to check on which rcd.wine~o wrote:
Next with the bulb lit switch off any circuits of 6 A ( marked lighting) at the consumer unit, Does the light stay on or go off ?
I understand fan heater should not be on lighting circuit?
- wine~o
- Senior Member
- Posts: 26176
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 3992 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
That's basically what I was getting at, if a lighting circuit then no heater, if a ring main then good to go assuming that the cable from the FCU to the heater is up to the job.yartin wrote: I understand fan heater should not be on lighting circuit?
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
Got it, I will check this weekend, many thanks.wine~o wrote:That's basically what I was getting at, if a lighting circuit then no heater, if a ring main then good to go assuming that the cable from the FCU to the heater is up to the job.yartin wrote: I understand fan heater should not be on lighting circuit?
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
Just checked this morning, the cable is live and the spur fuse works and it is connected to a B16 Socket RCD, second from left RCD in my previous photo, I turned all rcds off and connected the bulb as in pic, then turned on one rcd at a time until bulb lit. So its done properly and not to a light circuit.wine~o wrote:That's basically what I was getting at, if a lighting circuit then no heater, if a ring main then good to go assuming that the cable from the FCU to the heater is up to the job.yartin wrote: I understand fan heater should not be on lighting circuit?
The cable measures about 11mm width including the white sleeves and seems thick enough not easy to bend so at least 1.5mm and should be safe for 2KW heater? also fitted with 13A fuse to justify this. Though I will use the 1KW option on installation.
Is it safe to assume the cable is coming down from the loft so I can drill any where below or beside where the cable comes out of the wall to fix heater into wall?
- Attachments
-
- IMG_2593.JPG (58.98 KiB) Viewed 4931 times
-
- Senior Member
- Posts: 5293
- Joined: Wed Feb 26, 2014 9:35 pm
- Has thanked: 100 times
- Been thanked: 1022 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
Never safe to assume. Since you are going to be covering the cable with a heater, enlarge the hole a little bit so you can see where the cable runs.
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
How about cable detector? Are cheap ones around £5-10 reliable?Rorschach wrote:Never safe to assume. Since you are going to be covering the cable with a heater, enlarge the hole a little bit so you can see where the cable runs.
-
- Senior Member
- Posts: 5293
- Joined: Wed Feb 26, 2014 9:35 pm
- Has thanked: 100 times
- Been thanked: 1022 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
I have never found one that works.yartin wrote:How about cable detector? Are cheap ones around £5-10 reliable?Rorschach wrote:Never safe to assume. Since you are going to be covering the cable with a heater, enlarge the hole a little bit so you can see where the cable runs.
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
I am getting a fan which plugs to wall socket, (it is a bathroom fan IP23, zone 3 but which bathroom has wall socket?!), this mean I will have to cut the cable discard plug and connect to my wall cable and use PVC trunking, which connector should I use which will hide in the trunks?
Unless I will be able to feed my cable inside the casing of the heater, won't know until I see it.
Unless I will be able to feed my cable inside the casing of the heater, won't know until I see it.
- wine~o
- Senior Member
- Posts: 26176
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 3992 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
I would hazard a guess that the supply runs horizontally from the fcu to where the cable comes out of the wall
But do check as Rorsasch says.
Unusual to have a bathroom heater that comes with a plug, does it have a pull cord for switching on and off ?
Oh and Zone 3 no longer exists, zones 0, 1 and 2 do exist, outside of that is no longer zone 3, just "outside of the zones"
But do check as Rorsasch says.
Unusual to have a bathroom heater that comes with a plug, does it have a pull cord for switching on and off ?
Oh and Zone 3 no longer exists, zones 0, 1 and 2 do exist, outside of that is no longer zone 3, just "outside of the zones"
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
Yes it has pull cord, they have UK office so not a grey import, will call them next week, screen photo from the manual attached.wine~o wrote:I would hazard a guess that the supply runs horizontally from the fcu to where the cable comes out of the wall
But do check as Rorsasch says.
Unusual to have a bathroom heater that comes with a plug, does it have a pull cord for switching on and off ?
Oh and Zone 3 no longer exists, zones 0, 1 and 2 do exist, outside of that is no longer zone 3, just "outside of the zones"
- Attachments
-
- zone 3.png (315.12 KiB) Viewed 4918 times
-
- Senior Member
- Posts: 1161
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 139 times
- Been thanked: 113 times
Re: Installing Electric Wall Heater 1KW or 2KW in Bathroom
I had a closer look today, pics attached, is it safe to say white cable coming from the ceiling? So I can drill anywhere under and to the left or right safely to fix fan?