Intergas HRE 24/28 & Nest 3

Questions about central heating and boiler questions in here please.

Moderator: Moderators

Post Reply
BSF75
Newly registered Member
Posts: 3
Joined: Thu Mar 08, 2018 6:53 pm
Has thanked: 0
Been thanked: 0

Intergas HRE 24/28 & Nest 3

Post by BSF75 » Thu Mar 08, 2018 7:03 pm

Hi

I have an Intergas HRE 24/28 & was looking to purchase a Nest 3 & I was looking for some advice please

From the reading I have done - I need to ensure there is power to L & N in the Heat Link & wire OT1 & OT2 in the Heat Link to X4 11 & 12 in the boiler - removing any other connections in X4 in the boiler.

I then set the nest to open therm in the settings

This seems fairly simple & I feel like I am missing something

Can anyone advise

Thanks for any help you can give

Many Thanks

Brett
User avatar
Razor
Senior Member
Posts: 7514
Joined: Wed Nov 14, 2007 10:21 pm
Location: Northampton
Has thanked: 284 times
Been thanked: 878 times

Re: Intergas HRE 24/28 & Nest 3

Post by Razor » Thu Mar 08, 2018 7:07 pm

It depends how old the boiler is. You don't always remove all other connections on X4 - if it's an ERP model you could disconnect the power to the pump!!

Is the pump round or oblong?
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html
User avatar
wine~o
Senior Member
Posts: 24690
Joined: Sat Jan 10, 2009 3:49 pm
Location: hants/dorset border
Has thanked: 1325 times
Been thanked: 3632 times

Re: Intergas HRE 24/28 & Nest 3

Post by wine~o » Thu Mar 08, 2018 7:08 pm

I was just about to say Razor will know for sure...

Too slow Wine~o
These users thanked the author wine~o for the post:
Razor
Rating: 7.14%
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk
BSF75
Newly registered Member
Posts: 3
Joined: Thu Mar 08, 2018 6:53 pm
Has thanked: 0
Been thanked: 0

Re: Intergas HRE 24/28 & Nest 3

Post by BSF75 » Thu Mar 08, 2018 7:22 pm

Hi

thanks for the quick replies

the pump is round

In the X4 I have a link between 4 & 5 & connections to 6 & 7 for the old thermostat

thanks again

Brett
User avatar
Razor
Senior Member
Posts: 7514
Joined: Wed Nov 14, 2007 10:21 pm
Location: Northampton
Has thanked: 284 times
Been thanked: 878 times

Re: Intergas HRE 24/28 & Nest 3

Post by Razor » Thu Mar 08, 2018 7:56 pm

Perfect!!

Leave the link between 4/5 on X4 and remove the old stat wires then proceed as you said in your first post :salute: :salute:
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html
BSF75
Newly registered Member
Posts: 3
Joined: Thu Mar 08, 2018 6:53 pm
Has thanked: 0
Been thanked: 0

Re: Intergas HRE 24/28 & Nest 3

Post by BSF75 » Thu Mar 08, 2018 11:07 pm

much obliged thank you for taking the time

Brett
Post Reply

Return to “Central Heating & Boilers”