Intergas HRE 24/28 & Nest 3

Post by BSF75 »

Hi

I have an Intergas HRE 24/28 & was looking to purchase a Nest 3 & I was looking for some advice please

From the reading I have done - I need to ensure there is power to L & N in the Heat Link & wire OT1 & OT2 in the Heat Link to X4 11 & 12 in the boiler - removing any other connections in X4 in the boiler.

I then set the nest to open therm in the settings

This seems fairly simple & I feel like I am missing something

Can anyone advise

Thanks for any help you can give

Many Thanks

Brett
User avatar
Razor
Senior Member
Posts: 8760
Joined: Wed Nov 14, 2007 10:21 pm
Location: Northampton
Has thanked: 483 times
Been thanked: 1251 times

Re: Intergas HRE 24/28 & Nest 3

Post by Razor »

It depends how old the boiler is. You don't always remove all other connections on X4 - if it's an ERP model you could disconnect the power to the pump!!

Is the pump round or oblong?
I think I'll take two chickens...
User avatar
wine~o
Senior Member
Posts: 26165
Joined: Sat Jan 10, 2009 3:49 pm
Location: hants/dorset border
Has thanked: 1413 times
Been thanked: 3988 times

Re: Intergas HRE 24/28 & Nest 3

Post by wine~o »

I was just about to say Razor will know for sure...

Too slow Wine~o
These users thanked the author wine~o for the post:
Razor
Rating: 7.14%
Verwood Handyman

_____________________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk
BSF75
Newly registered Member
Posts: 3
Joined: Thu Mar 08, 2018 6:53 pm
Has thanked: 0
Been thanked: 0

Re: Intergas HRE 24/28 & Nest 3

Post by BSF75 »

Hi

thanks for the quick replies

the pump is round

In the X4 I have a link between 4 & 5 & connections to 6 & 7 for the old thermostat

thanks again

Brett
User avatar
Razor
Senior Member
Posts: 8760
Joined: Wed Nov 14, 2007 10:21 pm
Location: Northampton
Has thanked: 483 times
Been thanked: 1251 times

Re: Intergas HRE 24/28 & Nest 3

Post by Razor »

Perfect!!

Leave the link between 4/5 on X4 and remove the old stat wires then proceed as you said in your first post :salute: :salute:
I think I'll take two chickens...
BSF75
Newly registered Member
Posts: 3
Joined: Thu Mar 08, 2018 6:53 pm
Has thanked: 0
Been thanked: 0

Re: Intergas HRE 24/28 & Nest 3

Post by BSF75 »

much obliged thank you for taking the time

Brett