Brand new roof leaking

Post by mamalovesmambo »

Hi,

I've had my roof replaced with the following :
Slate
Breathable membrane
25mm air space below
Kingspan between & under the rafters
plasterboard

On new years day we discovered 2 damp patches on the wall where the wall meets the roof in the room that's built into the roof.
These disappeared within a few days, then reappeared a few days later.

Picture of the damp patches
http://i553.photobucket.com/albums/jj36 ... 12ed86.jpg

The roofers came round to have a look.
They said it couldn't be a conventional leak as the roof is solid, and I guess as I agree as it hasn't been raining.
They speculated that since it's been very cold, that water vapour in the air had found a cold spot and condensed.
This must've happened on the underside of the breathable membrane,
then dripped onto the foil covered insulation and run down to where the roof meets the wall and caused the damp patch.
They also said this sort of thing is more likely to happen in an unheated space (the room is unheated at the moment while interior diy is happening)
they said when we turn the heating on this shouldn't happen again, and implied that they don't want to/won't do anything about this.

Does anyone know if this could be an explanation of what happened?

1) I thought condensation happened when warm air meets a cold surface, so saying that it's more likely to happen in an unheated room sounds wrong to me?
2) Surely the double layer of insulation should be stopping warm air from escaping, I know it's not going to stop all warmth escaping, but surely it should stop enough so that this doesn't happen?
3) I also thought the membrane was breathable, so that water could exit without causing problems like this
4) If it is water condensing on the underside and running down to where the roof meets the wall, then surely there should be a mechanism so that it doesn't just empty onto the wall and soak into it? If there is a possibility that this can happen surely there should be an outlet for condsensed water? Have the roofers constructed something incorrectly? It seems crazy that they can come along and say "condsendation happens", without having built something into the roof design to deal with this condensation.
5) It seems like it's too much water to be caused by condensation, how much water would cause this amount of damp patch?
6) If it is condensation then why has it only appeared in these 2 places, wouldn't condensation be more likely to cause a wet line running along where the roof meets the wall? There's also no damp patches in the other room at the back of the house that's also unheated. Why would the condensation form in 2 particular places and not elsewhere?
7) If it's not condensation running down, does anyone have any other theories on where this damp could have come from?
8) We've just spend a load of money replacing the roof and are unhappy at the roofers just washing their hands of this and not wanting to do anything about it. I know the damp patches have disappeared but how do I know they won't come back and be worse?

The chimney is at the other end of the room, so it's not being caused by a chinmney problem.

The stepped skirting (see the picture linked above) is a saniflow toilet outlet which comes from the next room, through this room and to the outside. So that's got nothing to do with the leak either.

Any advice would be greatly appreciated.
User avatar
thescruff
Senior Member
Posts: 49685
Joined: Mon Mar 10, 2008 12:46 am
Location: Bath
Has thanked: 360 times
Been thanked: 3734 times

Post by thescruff »

Looks like a leak to me.

Can we have a pic above and a roof shot.
Attachments
140109a.jpg
140109a.jpg (24.19 KiB) Viewed 1526 times
User avatar
big-all
Pro Carpenter
Posts: 23420
Joined: Sat Dec 16, 2006 10:11 pm
Location: redhill surrey an auld reekie laddie
Has thanked: 731 times
Been thanked: 2303 times

Post by big-all »

i am assuming the wet patches are at around 400 centers

my guess would be

the water is running down the membrain anywhere upstream [could be as far up as the ridge] then dropping onto the last bit of kingspan [or simply exiting onto the joists] at the bottom then finding its way acrross to the edges by the bottom

edit
ok more thoroughly read your answer plus the comments on d i y s n o t

if you have moisture in the void you will get condensation because your black roof will raise the temperature to say 8 degees in the sun absorbing moisture from the wood then at night when it cools to say minus 6you get condensation now membrane is the coolest surface so condensation forms underneath

now because the moisture is now the other side off the cold zone the problem should cure its self unless the moisture is being replenished

if you have spot lights peircing the kingspan they may introduce moisture as the plaster dried!!!
we are all ------------------still learning