Hi
I have just purchased a new dual fuel cooker and want to attach it to the CCU I had installed over ten years ago. This is connected to a separate 30amp ring main to the the consumer unit. I assume that I need to use 30amp cable. But do I neeed to have a specially rated socket behind where the cooker is going to go or will a normal 13 amp socket do? The square metal casing is already in situ
In terms of wiring I can see where the live and neutral wire connect inside the CCU. Will the earth go in the adjacent hole to where the earth sits at the moment . Please see attached pics. A bit blurred but discernible.
Thanks for your help.
[/img]
Installing Stove dual fuel cooker
Moderator: Moderators
- ultimatehandyman
- Site Admin
- Posts: 24406
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 999 times
- Been thanked: 915 times
Do you have the instructions for the cooker?
It should tell you how many KW the cooker is rated at, we need this information really!
When you say that the CCU is connected to a ring main back to the consumer unit do you mean that the CCU is on it's own dedicated circuit back to the consumer unit ( radial circuit)? if so what was connected to this before and what is the thickness of the cable. What size fuse is protecting the circuit?
If the electrical side of the cooker is less than 3kw then it can be plugged into a socket, if it is more than 3kw then it cannot be plugged into a socket and will require it's own circuit, and will normally be wired into one of these- http://www.screwfix.com/app/sfd/cat/pro ... 6&ts=52834
It should tell you how many KW the cooker is rated at, we need this information really!
When you say that the CCU is connected to a ring main back to the consumer unit do you mean that the CCU is on it's own dedicated circuit back to the consumer unit ( radial circuit)? if so what was connected to this before and what is the thickness of the cable. What size fuse is protecting the circuit?
If the electrical side of the cooker is less than 3kw then it can be plugged into a socket, if it is more than 3kw then it cannot be plugged into a socket and will require it's own circuit, and will normally be wired into one of these- http://www.screwfix.com/app/sfd/cat/pro ... 6&ts=52834
- ultimatehandyman
- Site Admin
- Posts: 24406
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 999 times
- Been thanked: 915 times
shazdog has sent me the pics by e-mail that I will attach and also this information-
The cooker will be wired to a radial circuit dedicated for a cooker. The circuit is protected by 30amp wylex trip fuse. The cable is up to 52 amp. The Richmond 1000DF seems to have a fuse rating of 32 amp. There are two oven and grills with the following ratings
Oven and grill 1: 1.3 and 2.5 Kw
Oven and grill 2: 2.3 and 1.7 Kw
I got these specs from
http://www.stoves.co.uk/Specifications_p31.aspx
as the cooker is due to arrive tomorrow!
Thanks again for your help.
Simon (Shazdog)
The cooker will be wired to a radial circuit dedicated for a cooker. The circuit is protected by 30amp wylex trip fuse. The cable is up to 52 amp. The Richmond 1000DF seems to have a fuse rating of 32 amp. There are two oven and grills with the following ratings
Oven and grill 1: 1.3 and 2.5 Kw
Oven and grill 2: 2.3 and 1.7 Kw
I got these specs from
http://www.stoves.co.uk/Specifications_p31.aspx
as the cooker is due to arrive tomorrow!
Thanks again for your help.
Simon (Shazdog)
- Attachments
-
- cooker-electrics2.jpg (11.69 KiB) Viewed 8408 times
-
- cooker-electrics1.jpg (19.79 KiB) Viewed 8408 times
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Yes you would connect the earth core into the spare terminal next to it , Live and neuttral you know about as you said. Your fuse is a 30A fuse so even though it says 32A on the stoves website it will in practice be fine. Connect the cooker up with 6mm twin and earth ,
Hope this answers your questions
Nick