PostPosted: Mon Sep 27, 2010 8:53 am 
Offline
Newly registered Member

Joined: Mon Sep 27, 2010 8:39 am
Posts: 2
Has thanked: 1 times
Been thanked: 0 times
Hi, please can some one help me????

I own a Vaillant eco tec plus Combi boiler that both provides my central heating and hot water.
The hot water works fine pressure all ok, but my central heating is not working? the digital thermostat (Drayton Digistat+2rf) i have is working fine. There are no faults showing on the boiler display. the only thing not showing is the radiator symbol (Heating mode active symbol)?

Many Thanks Alison


Top
 Profile  
 

You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Sep 27, 2010 1:49 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 6539
Location: Northampton
Has thanked: 158 times
Been thanked: 588 times
When you say the digistat is ok is the green light (top one) on the receiver actually lit?

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
PostPosted: Mon Sep 27, 2010 5:21 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 4706
Has thanked: 135 times
Been thanked: 397 times
If the radiator symbol is not showing, then it seems the boiler is not getting a call for heat.

When you think the boiler should be on for heating, press the 'i' button and tell us what 'S' code is displayed.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
 
PostPosted: Mon Sep 27, 2010 9:43 pm 
Offline
Newly registered Member

Joined: Mon Sep 27, 2010 8:39 am
Posts: 2
Has thanked: 1 times
Been thanked: 0 times
Yes the green light is on the receiver, i have gone through all the checks with the manual to pair up as below. When i i get down to No 3, override button the green light comes on but the boiler will not fire up?
And the code on the boiler is displaying S30. I can press both the +- buttons to fire up the boiler but this only works for a short time.

Thanks Alison

No 1. Turn off the power supply to the Digistat SCR (receiver unit)
and leave for 5 seconds.
2. Turn on power to SCR unit and check red light is on.
3. Press override button No.2 and check the green light comes
on and boiler fires.
4. Press & hold down button No.1 (Keep depressed), then
press No.2 and keep depressed. {The Red LED light will flash
a couple of times and then it will go out}
5. Now release both the buttons – {the two LED lights should
come back on}
6. Get the Digistat+2RF/+3RF unit and stand two metres away
from the SCR unit with the Digistat+2RF/+3RF unit in your hand.
7. Remove the battery cover and fit the batteries.
8. The Red LED light on the SCR will now flash for approx. 7
seconds.
9. This confirms that the radio signal is being sent and
received.
10. The Digistat+2RF/+3RF and the SCR are now successfully
linked by a dedicated RF address.
11. Install the Digistat+2RF/+3RF as follows:
COMMISSIONING THE DIGISTAT +2RF or
+3RF ‘WIRELESS SYSTEM’
IMPORTANT: MULTIZONE


Top
 Profile  
 
PostPosted: Mon Sep 27, 2010 10:43 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 4706
Has thanked: 135 times
Been thanked: 397 times
S30 is 'no call for heat from external controls'.

I think the problem lies with your room stat/programmer etc.

If you feel competent, you can switch off ALL power to the boiler and heating system, open the boiler up, remove the pcb cover and link terminals 3 & 4 on the pcb. Turn boiler back on.

If the boiler fires, this then proves it to be an external control fault.

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : Alisonc76
Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 5 posts ] 



Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 



phpBB SEO