wine~o wrote:
les1 wrote:
Interesting, possibly 30 amp at the use box. I have done the swop & fitted a 13 amp plug to the immersion cable it so we shall see. However thanks for the thought.


There is a very good reason that it was wired via a switch (20 Amp) rather than a 13 Amp plug.

Immersion heating elements are normally 3 Kw (3000 Watts) Now at 230 Volts (Nominal supply) that equates to 3000 divide 230 = 13.04 Amps, so not an issue, however that nominal voltage could be + 10% or - 6% at - 6% you are looking at 216 V, 3000 divide 216 = 13.87 Amps which means that the fuse will give out over time/repeated use.

Personally I'd have left it as it was originally installed or put in a dedicated immersion heater time switch (about £70 last time I checked)

I'm sure only me will put me right if I'm wrong



That is not the correct answer.

A 3kW element at 240V should be treated as a resistive load for this calculation. The resistance of the element is the only constant.

P = VI
3000 = 240 x I
I = 3000/240
I = 12.5A

R = V/I
R= 240/12.5 = 19.2 ohms

So the element has a resistance of 19.2 ohms. That is your constant for all calculations with different voltages.

Put 216V across the element and the current is

216/19.2 = 11.25A

As the voltage only changed on paper and most of the UK is still running at 240V all that has happened is that the 240V 3kW element has been rebadged as a 230V 2.7kW element.


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+

For this message the author OnlyMe has received gratitude : wine~o
Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 11, 2018 6:30 pm 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 24006
Location: hants/dorset border
Has thanked: 1503 times
Been thanked: 3801 times
Thanks for correcting me OnlyMe, do you think it is a sensible idea to change the 20A switch for a socket and plug arrangement though ?

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 11, 2018 8:25 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2714
Location: South Yorkshire
Has thanked: 168 times
Been thanked: 582 times
wine~o wrote:
Thanks for correcting me OnlyMe, do you think it is a sensible idea to change the 20A switch for a socket and plug arrangement though ?

No


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 18 posts ]  Go to page Previous  1, 2

 

 




Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO