PostPosted: Sat Jan 14, 2012 11:20 am 
Offline
Newly registered Member

Joined: Sat Jan 14, 2012 9:37 am
Posts: 2
Has thanked: 0 times
Been thanked: 0 times
Hello,
I have a storage heater in the lounge (Dimplex CXLN), which two days ago decided not to work, although the convector is working.
I have looked through this site and found previous posts regarding the thermal reset switch which may need resetting, however, mine doesn't seem to have activated for me to reset.

This is the odd bit - I have an electric key meter and have recently noticed that instead of the meter using the electricity it's starting to add it. For example, there was £1.20 at night, then 70p in the morning which rose to 87p, it keeps increasing and now it is at £5.92. This happened at the same time the heater stopped working, but we didn't notice the heater cold until the following evening. The water heater is working ok on the same economy 7 system although a separate circuit I believe.

I will check the usual - elements, circuit breaker (I have a Wylex with the B16 breakers).

Has anyone encountered this before or can any suggestions be made.

Thanks

Mike


Top
 Profile  
 
PostPosted: Sat Jan 14, 2012 8:02 pm 
Offline
Senior Member
User avatar

Joined: Mon Mar 15, 2010 11:49 pm
Posts: 2316
Location: Oban
Has thanked: 62 times
Been thanked: 217 times
I have one suggestion - sell me that meter..... :lol:

For the meter to 'go backwards' you will be feeding it in reverse therefore the standard rate electricity must be getting though somewhere. Is the heater on it's own cable or shared with something else?

_________________
This post may contain nuts


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sat Jan 14, 2012 10:19 pm 
Offline
Newly registered Member

Joined: Sat Jan 14, 2012 9:37 am
Posts: 2
Has thanked: 0 times
Been thanked: 0 times
Thanks for the reply.

It's very strange, I've googled this meter subject but can't find anything.

The heater (storage) along with the hall heater (now removed) is on a separate unit/breaker. I have now tested all 4 elements and the circuit breaker at the board. The 20amp wall plates and the flex, all ok.

I may need to contact Southern Electric as it maybe the cheap rate switch side.

Mike


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 3 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling