 Post subject: Shower and combi
PostPosted: Wed May 23, 2018 5:06 pm 
Offline
Newly registered Member

Joined: Wed May 23, 2018 7:16 am
Posts: 3
Has thanked: 0 times
Been thanked: 1 times
Hi,
I have a question regarding combi boilers and showers. We had a new combi boiler installed around the end of last year. The shower used to run from a water tank in a cupboard upstairs which fed a pump and the temperature of the shower could be controlled from a dial on the front.

After the combi was installed the pump and tank were removed as the plumber said it could now come straight off the mains. The shower was then scalding hot. The plumber returned and fitted a pressure reducing valve in the loft. The shower then took around an hour to get up to a suitable temperature and this was after the water temperature was raised to the maximum(65’C)on the front of the boiler and once scalding adjusted to a lower setting (40’C)There was also no control from the shower front anymore as this just made the shower go ice cold.

Last week the shower stopped drawing hot water as the boiler wouldn’t come on when the shower was turned on. Another plumber came and had a look and said we have to rip out all the pipe work from the bathroom to the loft as this is the wrong type of shower( mixer shower) for a combi boiler.

Does anyone have a simpler solution to this problem?

Thanks


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+

For this message the author Lc1 has received gratitude : instash28
Top
 Profile  
Reply with quote  
 Post subject: Re: Shower and combi
PostPosted: Wed May 23, 2018 5:15 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 7459
Location: Northampton
Has thanked: 316 times
Been thanked: 960 times
65 degrees? Sounds familiar; what make is the boiler?

Is the cold supply to the shower also off the mains or is it still on the old cistern?

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html


Top
 Profile  
Reply with quote  
 Post subject: Re: Shower and combi
PostPosted: Thu May 24, 2018 5:07 am 
Offline
Newly registered Member

Joined: Wed May 23, 2018 7:16 am
Posts: 3
Has thanked: 0 times
Been thanked: 1 times
Hi,
Boiler is an independent combi 30.
I’m not quite sure where the cold water is coming from but the second plumber did mention that the bathroom toilet may also need some work as the first plumbers must have made some adjustments.

In the cupboard where the original tank was the shower hoses are plumbed to the existing pipes, I assume one is the hot water from the boiler but I am not sure where the cold water comes from, mains or other.

Shower is a triton.

Thanks


Top
 Profile  
Reply with quote  
 Post subject: Re: Shower and combi
PostPosted: Thu May 24, 2018 8:15 am 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6840
Has thanked: 826 times
Been thanked: 899 times
Do you still have a tank in the loft full of water?

If so is there a pipe from it that is not capped off anywhere?

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
 Post subject: Re: Shower and combi
PostPosted: Thu May 24, 2018 8:28 am 
Offline
Newly registered Member

Joined: Wed May 23, 2018 7:16 am
Posts: 3
Has thanked: 0 times
Been thanked: 1 times
Hi,
Yes there is a tank full of water in the loft. I believe it has black padding around it. Not sure if any pipes have been capped off I will have to check.

Thanks.


Top
 Profile  
Reply with quote  
 Post subject: Re: Shower and combi
PostPosted: Thu May 24, 2018 8:07 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6840
Has thanked: 826 times
Been thanked: 899 times
Sounds as if the cold may still be from the loft tank then.

If so this is completely wrong and would explain your combi problems.

All hot and colds must come from the cold mains supply on a combi.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO