PostPosted: Sat Jun 24, 2017 7:13 pm 
Offline
Newly registered Member

Joined: Wed Feb 17, 2016 11:51 am
Posts: 51
Location: Wiltshire
Has thanked: 2 times
Been thanked: 1 times
Hello.

A support and floorboards downstairs are rotten. I have removed them and will replace soon.

I've left a gap for it to dry out.

This is where the dining room becomes the utility room.

The issue is there is no ventilation.

There used to be a vent - this was cemented up because the previous owner "knew better".

I have removed the cement but air only now goes into the cavity of the wall (better than nothing I guess) - there is no gap in the inner brick layer for air to enter.

I have laminate flooring so taking that up and the floorboards to take out a brink or two isn't going to happen.

Any other options?

So far:

1) Holesaw or similar a hole in my laminate floor, penetrating the floorboards and fitting a vent. However, hitting a rafter or cable is likely.

2) Fit a vent where the current gap is (this seems the easiest although not ideal).

Many thanks.


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Sat Jun 24, 2017 7:42 pm 
Offline
Newly registered Member

Joined: Thu Mar 24, 2016 6:44 pm
Posts: 20
Has thanked: 0 times
Been thanked: 3 times
I imagine the air brick you're referring to is a cavity vent for pre-insulation days. There is probably a corresponding airbrick at about soffit level. If cavity insulation put in retrospectively then they will have cemented or silicon sealed them up so the insulation doesn't come out.
There should be other air bricks (double sized) that go all the way through to vent the subfloor. Can't quite picture what you mean about taking up laminate floor as it sounds like you have the affected area already lifted? I'd say drill a few bricks out and install some airbricks. Do usual check soil isn't heaped over existing airbricks outside. Check rubble and soil aren't touching timbers in the subfloor. Check any honeycomb brick structures are free of debris to allow air flow.

Sent from my SM-G935F using Tapatalk


Top
 Profile  
Reply with quote  
PostPosted: Sat Jun 24, 2017 7:43 pm 
Offline
Senior Member
User avatar

Joined: Thu Mar 09, 2017 4:47 pm
Posts: 531
Location: East Riding of Yorkshire
Has thanked: 11 times
Been thanked: 150 times
Your first action is go back to the vent which was 'cemented' up and look at removing a brick from the inner brick wall across the cavity. This should be easily achieved by hand using a suitable long cold chisel and a lump hammer. A suitable chisel would be about 450mm long or longer.
Remove the inner brick completely and fit a clay or plastic cavity sleeve which will bridge the cavity between the holes.
Then fit an air brick in the external hole.
You then need to check that other Vent holes have not been closed off too.
Just so you are aware, the void under the floor has to have cross ventilation in order for the floor timbering to remain sound.
If other vents have been closed, you need to address those too in the manor described above.

davyp1


Top
 Profile  
Reply with quote  
PostPosted: Sat Jun 24, 2017 11:20 pm 
Offline
Senior Member

Joined: Fri Nov 01, 2013 9:36 am
Posts: 560
Has thanked: 2 times
Been thanked: 95 times
can you go under the suspended floor?
knocking out bricks for air bricks you need to open up right throug the wall.
dont drill holes throgh the laminate.do you have a picture where the floor is open


Top
 Profile  
Reply with quote  
PostPosted: Mon Jun 26, 2017 7:35 pm 
Offline
Newly registered Member

Joined: Wed Feb 17, 2016 11:51 am
Posts: 51
Location: Wiltshire
Has thanked: 2 times
Been thanked: 1 times
portera86 wrote:
If cavity insulation put in retrospectively then they will have cemented or silicon sealed them up so the insulation doesn't come out.

There should be other air bricks (double sized) that go all the way through to vent the subfloor. Can't quite picture what you mean about taking up laminate floor as it sounds like you have the affected area already lifted? I'd say drill a few bricks out and install some airbricks. Do usual check soil isn't heaped over existing airbricks outside. Check rubble and soil aren't touching timbers in the subfloor. Check any honeycomb brick structures are free of debris to allow air flow.



No cavity insulation has been put in.

I have three other vents ground-floor level. These are fine and not blocked.

Re/ the area already being lifted - I can lift a small portion of floor in the Utility Room (which is lino) and I have indeed done this.

Then, we are onto the laminate floor.

davyp1 wrote:
Your first action is go back to the vent which was 'cemented' up and look at removing a brick from the inner brick wall across the cavity.

davyp1


This is the issue - gaining access to the inner bricks.

wes56 wrote:
can you go under the suspended floor?
knocking out bricks for air bricks you need to open up right throug the wall.
dont drill holes throgh the laminate.do you have a picture where the floor is open


I will get a picture together soon.


Top
 Profile  
Reply with quote  
PostPosted: Mon Jun 26, 2017 7:38 pm 
Offline
Newly registered Member

Joined: Wed Feb 17, 2016 11:51 am
Posts: 51
Location: Wiltshire
Has thanked: 2 times
Been thanked: 1 times
Also, to add more context, my air bricks are staggered.

Like this:

Image


Top
 Profile  
Reply with quote  
PostPosted: Tue Jun 27, 2017 3:55 pm 
Offline
Senior Member
User avatar

Joined: Thu Mar 09, 2017 4:47 pm
Posts: 531
Location: East Riding of Yorkshire
Has thanked: 11 times
Been thanked: 150 times
davyp1 wrote:
Your first action is go back to the vent which was 'cemented' up and look at removing a brick from the inner brick wall across the cavity.

davyp1


This is the issue - gaining access to the inner bricks.



I will get a picture together soon.[/quote]

I do not see what your problem is in taking an inner brick out in each case!
If necessary two/three or more bricks would be removed from the external leaf of brickwork just to access the inner leaf.
Once a brick was removed to the inner wall a clay cavity sleeve would be cut to the right length and both walls repaired and an air-brick fitted to the outer leaf at the same time.
I assure you, it's not rocket science. Also, I doubt it would be necessary to remove more than a couple of external bricks in order to gain access to remove the inner brick.

This work needs doing in order to provide cross ventilation as mentioned earlier.

davyp1


Top
 Profile  
Reply with quote  
PostPosted: Tue Jun 27, 2017 5:13 pm 
Offline
Senior Member
User avatar

Joined: Thu Mar 09, 2017 4:47 pm
Posts: 531
Location: East Riding of Yorkshire
Has thanked: 11 times
Been thanked: 150 times
otronics wrote:
Also, to add more context, my air bricks are staggered.

Like this:

Image


Perhaps ignore my earlier reply!
Your sketch is indicative of "a telescopic" vent.
If this is the case and only the Air-brick has been cemented up, can you not just clear the cement or replace the air-brick?

davyp1


Top
 Profile  
Reply with quote  
PostPosted: Tue Jun 27, 2017 10:41 pm 
Offline
Newly registered Member

Joined: Wed Feb 17, 2016 11:51 am
Posts: 51
Location: Wiltshire
Has thanked: 2 times
Been thanked: 1 times
davyp1 wrote:
otronics wrote:
Also, to add more context, my air bricks are staggered.

Like this:

Image


Perhaps ignore my earlier reply!
Your sketch is indicative of "a telescopic" vent.
If this is the case and only the Air-brick has been cemented up, can you not just clear the cement or replace the air-brick?

davyp1


Correct - a telescopic vent.

I have removed all the cement from the outer air brick - no issues there.

My problem is that the inner section was bricked up and I have no access to it.


Top
 Profile  
Reply with quote  
PostPosted: Tue Jun 27, 2017 11:33 pm 
Offline
Senior Member
User avatar

Joined: Thu Mar 09, 2017 4:47 pm
Posts: 531
Location: East Riding of Yorkshire
Has thanked: 11 times
Been thanked: 150 times
otronics wrote:
davyp1 wrote:
otronics wrote:
Also, to add more context, my air bricks are staggered.

Like this:

Image


Perhaps ignore my earlier reply!
Your sketch is indicative of "a telescopic" vent.
If this is the case and only the Air-brick has been cemented up, can you not just clear the cement or replace the air-brick?

davyp1


Correct - a telescopic vent.

I have removed all the cement from the outer air brick - no issues there.

My problem is that the inner section was bricked up and I have no access to it.


Make an access then by removing a couple of bricks lower down!
Remove mortar around the bricks with a 'plugging chisel' and lump hammer. Keep at it steadily and you would have two bricks out in 15 minutes or so. Then address the removal of the bricked up inner hole!
You may damage the telescopic vent and have to replace it.

davyp1


Top
 Profile  
Reply with quote  
PostPosted: Wed Jun 28, 2017 10:55 am 
Offline
Newly registered Member

Joined: Wed Feb 17, 2016 11:51 am
Posts: 51
Location: Wiltshire
Has thanked: 2 times
Been thanked: 1 times
davyp1 wrote:

Make an access then by removing a couple of bricks lower down!
Remove mortar around the bricks with a 'plugging chisel' and lump hammer. Keep at it steadily and you would have two bricks out in 15 minutes or so. Then address the removal of the bricked up inner hole!
You may damage the telescopic vent and have to replace it.

davyp1


I think you are right and that this is the way forward.

I have some rendering to contend with too and I need to double-check heights but this should be OK.

Thanks.


Top
 Profile  
Reply with quote  
PostPosted: Wed Jun 28, 2017 11:12 am 
Offline
Senior Member
User avatar

Joined: Thu Mar 09, 2017 4:47 pm
Posts: 531
Location: East Riding of Yorkshire
Has thanked: 11 times
Been thanked: 150 times
otronics wrote:
davyp1 wrote:

Make an access then by removing a couple of bricks lower down!
Remove mortar around the bricks with a 'plugging chisel' and lump hammer. Keep at it steadily and you would have two bricks out in 15 minutes or so. Then address the removal of the bricked up inner hole!
You may damage the telescopic vent and have to replace it.

davyp1


I think you are right and that this is the way forward.

I have some rendering to contend with too and I need to double-check heights but this should be OK.

Thanks.


You mention rendering!
You need to check the level of your DPC and that no one has rendered over it!
Please check and come back.

davyp1


Top
 Profile  
Reply with quote  
PostPosted: Wed Jun 28, 2017 11:53 am 
Offline
Newly registered Member

Joined: Wed Feb 17, 2016 11:51 am
Posts: 51
Location: Wiltshire
Has thanked: 2 times
Been thanked: 1 times
Quote:

You mention rendering!
You need to check the level of your DPC and that no one has rendered over it!
Please check and come back.

davyp1


Very good point.

I shall have a look later and put up some photos.


Top
 Profile  
Reply with quote  
PostPosted: Wed Jun 28, 2017 3:29 pm 
Offline
Senior Member
User avatar

Joined: Thu Mar 09, 2017 4:47 pm
Posts: 531
Location: East Riding of Yorkshire
Has thanked: 11 times
Been thanked: 150 times
otronics wrote:
Quote:

You mention rendering!
You need to check the level of your DPC and that no one has rendered over it!
Please check and come back.

davyp1


Very good point.

I shall have a look later and put up some photos.


Ok

davyp1


Top
 Profile  
Reply with quote  
PostPosted: Thu Jun 29, 2017 12:11 pm 
Offline
Newly registered Member

Joined: Wed Feb 17, 2016 11:51 am
Posts: 51
Location: Wiltshire
Has thanked: 2 times
Been thanked: 1 times
Images.


Attachments:
File comment: For reference - the other side of the blocked vent, where the laminate is fitted.
Inside.JPG
Inside.JPG [ 610.9 KiB | Viewed 418 times ]
File comment: The unblocked vent. The rendering is from the ground to the window ledge (you can see where it stops behind the chairs).
Outside.JPG
Outside.JPG [ 710.28 KiB | Viewed 418 times ]
File comment: Rotten rafter and floorboards removed. It has left this gap. I will cut wood, treat and fit. This is where the dining room becomes the utility room. (The rot/damp has damaged some of the door frame too so I will need to repair that).
Gap.JPG
Gap.JPG [ 659.76 KiB | Viewed 418 times ]
Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 21 posts ]  Go to page 1, 2  Next


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO