monder007
|
Posted: Sat May 23, 2009 10:07 pm |
|
 |
| Newly registered Member |
Joined: Mon May 18, 2009 9:44 pm Posts: 19 Has thanked: 1 times Been thanked: 0 times
|
|
hi
I've just installed two new sockets on a ring main, but when turning power back on to them the RCD trips.
if i just link up to one socket still trips, back to original RCD ok.
Check all wiring and all ok.
Anybody have any ideas?? do i need to get a higher rating RCD??
Currently 80A or 30mA i think thats right.
thanks
|
|
| Top |
|
 |
|
ban-all-sheds
|
Posted: Sun May 24, 2009 12:04 am |
|
 |
| BANNED |
 |
Joined: Fri Oct 27, 2006 6:40 pm Posts: 418 Has thanked: 0 times Been thanked: 1 times
|
monder007 wrote: Check all wiring and all ok.
Check again, because clearly it is not.
_________________
I'm sorry - I can't come in to work today, the voices are telling me to stay at home and clean the guns.
.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
monder007
|
Posted: Sun May 24, 2009 12:44 am |
|
 |
| Newly registered Member |
Joined: Mon May 18, 2009 9:44 pm Posts: 19 Has thanked: 1 times Been thanked: 0 times
|
|
thanks for the reply.
should it be okay though if all wiring is okay??
are there any particular wires that i should check to see if they are loose?
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
sparkydude
|
Posted: Sun May 24, 2009 8:34 am |
|
 |
| Senior Member |
 |
Joined: Sat Aug 13, 2005 8:11 pm Posts: 2071 Location: Staffordshire Has thanked: 2 times Been thanked: 99 times
|
|
Check in your new socket that you have not pinched any cables against the backbox and shorted out the neutral to the earth. How and what have you wired ??? is the socket you have come off of on the ring main ? what cable have you used to add your socket .
Nick
_________________ If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
monder007
|
Posted: Sun May 24, 2009 11:41 am |
|
 |
| Newly registered Member |
Joined: Mon May 18, 2009 9:44 pm Posts: 19 Has thanked: 1 times Been thanked: 0 times
|
|
hi
yer the socket i have put the two new sockets on is on the ring main because their are only two cable coming in and out of it.
i've used 2.5mm2 wiring.
i've put a socket on the plug on the circuit and another socket off that.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
Rich-Ando
|
Posted: Sun May 24, 2009 11:50 am |
|
 |
| Pro Sparky |
 |
Joined: Sat Mar 24, 2007 12:24 pm Posts: 6033 Location: Spondon, Derby Has thanked: 85 times Been thanked: 193 times
|
|
starting from scratch then, how did you do the installation? a step by step guide may help us help you.
as stated though, look for the obvious, cables caught on the screw at the back of the box or trapped onto the box screw eyes/lugs. failing that, a daft one but, make sure you have the polarity correct.
if all of that fails, make sure you havn't caught the cables when putting your floor back down.
finally, how did you clip the cables? there is a reason i ask it.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
monder007
|
Posted: Sun May 24, 2009 11:57 am |
|
 |
| Newly registered Member |
Joined: Mon May 18, 2009 9:44 pm Posts: 19 Has thanked: 1 times Been thanked: 0 times
|
|
i've have a new socket which run's off the socket in the circuit, along the wall and up to the socket. then from that socket to the other socket.
i can't lift the floor boards up as the floor boards run in a different direction to the place i want the plugs.
i can't see any cables caught, and covered the with the pvc covering. i've nail that on but can't see if i have caught any of the wires, the nails are to far away from the wire
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
sparkydude
|
Posted: Sun May 24, 2009 1:50 pm |
|
 |
| Senior Member |
 |
Joined: Sat Aug 13, 2005 8:11 pm Posts: 2071 Location: Staffordshire Has thanked: 2 times Been thanked: 99 times
|
|
have you got a multimeter? if so disconnect the cables you have added and test between all the individual cores, my betting is you have aught a cable when nailing the capping on. You have made the ring back up havent you ??? as in you have broken the two cables at the existing socket then conected one old with one new and then joined the other old set to the new set with crimps.
Please draw a sketch or take a photo showing what you have done and then we can assist further.
Nick
_________________ If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
monder007
|
Posted: Sun May 24, 2009 2:04 pm |
|
 |
| Newly registered Member |
Joined: Mon May 18, 2009 9:44 pm Posts: 19 Has thanked: 1 times Been thanked: 0 times
|
|
sketch
| Attachments: |
File comment: sketch

sockets.JPG [ 8.23 KiB | Viewed 510 times ]
|
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
sparkydude
|
Posted: Sun May 24, 2009 4:17 pm |
|
 |
| Senior Member |
 |
Joined: Sat Aug 13, 2005 8:11 pm Posts: 2071 Location: Staffordshire Has thanked: 2 times Been thanked: 99 times
|
|
What fuse/mcb protects this circuit?? if it is a 30 or 32A then you have created a potentially dangerous situation by spurring off of a spur. You are only allowed one unfused spur off of a ring main at one point ie one double socket or switched spur wired with one cable from a socket on the ring. You need to get another cable from your last socket back to the first socket in the ring main to enable you to make it safe. Or you can install a fused spur next to your ring socket and then wire the 2 new ones as the load from that spur bearing in mind that you will only be able to draw 13A from the two double sockets.
Nick
_________________ If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
Rich-Ando
|
Posted: Sun May 24, 2009 5:10 pm |
|
 |
| Pro Sparky |
 |
Joined: Sat Mar 24, 2007 12:24 pm Posts: 6033 Location: Spondon, Derby Has thanked: 85 times Been thanked: 193 times
|
|
fully concur with Sparkydude, that is why i asked for a step by step guide to what you have done.
just for info, it doesn't matter which way the floor boards run, you can get to where you want with them running either way, we do all the time.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
monder007
|
Posted: Sun May 24, 2009 10:18 pm |
|
 |
| Newly registered Member |
Joined: Mon May 18, 2009 9:44 pm Posts: 19 Has thanked: 1 times Been thanked: 0 times
|
|
hi
problem sorted nail in one of the wires.
its protected by an rcb 80A
sockets work ok
do you mean wire another wire from my last socket to the existing socket??
would this add it in to the circuit is instead of creating a spur??
so the existing socket will have four wires in it?? is this right??
thanks
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
Sparky James
|
Posted: Sun May 24, 2009 10:25 pm |
|
 |
| Senior Member |
 |
Joined: Wed Dec 31, 2008 9:23 am Posts: 1152 Location: Down on the Farm Has thanked: 10 times Been thanked: 75 times
|
|
No.. wire from another socket or inbetween the ring and the first new socket fit a 13a fused plate. The risk is in your wiring the firts piece of cable could in theory be over loaded if you had some high current appliances in your new sockets.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
monder007
|
Posted: Sun May 24, 2009 10:32 pm |
|
 |
| Newly registered Member |
Joined: Mon May 18, 2009 9:44 pm Posts: 19 Has thanked: 1 times Been thanked: 0 times
|
|
is the following possible??
| Attachments: |

sockets.JPG [ 9.7 KiB | Viewed 483 times ]
|
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
mikew1972
|
Posted: Sun May 24, 2009 10:58 pm |
|
 |
| Senior Member |
Joined: Sun Jan 27, 2008 5:54 pm Posts: 1051 Location: North West Has thanked: 0 times Been thanked: 69 times
|
|
This is what you need to do:
| Attachments: |
File comment: Correct way

sockets_177.jpeg [ 9.88 KiB | Viewed 479 times ]
|
_________________ Mike
|
|
| Top |
|
 |