 Post subject: rcd randomly tripping
PostPosted: Thu Oct 19, 2017 3:30 pm 
Offline
Newly registered Member

Joined: Mon Jun 05, 2017 6:14 am
Posts: 10
Has thanked: 0 times
Been thanked: 3 times
Hi chaps.
A few weeks ago i had a new consumer unit installed along with a new kitchen ring circuit and a new circuit for the range cooker. The reason for this is that I've swapped the lounge with the kitchen.
The range is all electric and is 6 years old but has been in storage for 4.
The rcd for the circuits that include the cooker (there are 2 rcds on the board) keeps tripping- coincidentaly when the cooker is used. When its running and the right side oven is switched on it trips immediately.
The electrician came back and tested the circuits which are ok. When he tested the cooker circuit his megger showed zero resistance when the right side oven was switched on. This would point to an element fault if i am not mistaken.
However, the cooker wall switch has now been disconnected with one blue wire and the mcb is off- but the rcd tripped only moments after they left.
Could the faulty element short to earth this still tripping the rcd?
I'm not an electrician but would like advice on this if possible.
Thanks.


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 19, 2017 4:11 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 6560
Has thanked: 32 times
Been thanked: 1100 times
Its possible.

The "problem*" with a RCD is you must isolate Live AND Neutral to say some thing is isolated. If the neutral touches earth it can cause an RCD to trip

*Its actually a good thing most of the time.

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 19, 2017 4:26 pm 
Offline
Newly registered Member

Joined: Mon Jun 05, 2017 6:14 am
Posts: 10
Has thanked: 0 times
Been thanked: 3 times
Update.
I have completely removed the cooker switch and it still tripped. I have now turned off my 1980's hifi and it hasn't tripped yet.. Let's see..


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 19, 2017 4:40 pm 
Online
Senior Member
User avatar

Joined: Wed Feb 25, 2015 7:20 pm
Posts: 2977
Has thanked: 897 times
Been thanked: 885 times
You can get different leaks on circuits adding up until you get a "cumulative" trip. An existing slight earth leak on something can be an amount that doesn't quite trip the RCD, then another leaky item will cause a trip. You need the two on together for the RCD to trip.
A fridge and a cooker for example.


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 19, 2017 5:23 pm 
Offline
Newly registered Member

Joined: Mon Jun 05, 2017 6:14 am
Posts: 10
Has thanked: 0 times
Been thanked: 3 times
Thankyou for the replies. So far-after a few hours with the cooker switch disconnected and the hifi off everything seems ok. I will turn the hifi on soon as I've had a San Miguel so fancy a dance.. If it trips then, well it's goodbye retro.
I think a new element is definitely required for one of the ovens anyway.


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 19, 2017 7:21 pm 
Online
Senior Member
User avatar

Joined: Wed Feb 25, 2015 7:20 pm
Posts: 2977
Has thanked: 897 times
Been thanked: 885 times
Remember that most circuits and equipment will have some inherent leakage. Again it can add up.
If any cooker elements or rings are looking rough that'd be my next move.


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 19, 2017 9:28 pm 
Offline
Newly registered Member

Joined: Mon Jun 05, 2017 6:14 am
Posts: 10
Has thanked: 0 times
Been thanked: 3 times
When you say looking rough what do you mean? I've just ordered a new element for the oven that showed the fault but that particular oven has actually only been used once in 6 years. It would seem that the insulation has broken down over time sat around in the garage.
Well, that's the theory anyway.
So far, with the hifi off and cooker disconnected the rcd has not tripped all evening. In the morning I shall ramp up the radio and see what happens.


Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 20, 2017 7:27 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2367
Location: South Yorkshire
Has thanked: 136 times
Been thanked: 496 times
Your electrician is making hard work of this.

Yes an element in your cooker has failed[1]. However to isolate the cooker and exclude it as a possible cause of the second RCD trip he only needed to switch it off at the double pole switch - there was no need to remove cables from the switch.

Now you have a dual RCD CU.

What happens if the hifi is plugged into a socket fed from the other RCD? Does the other RCD trip?

[1] Depending where stored (ie damp places) the elements insulator which is made from magnesium oxide will absorb water and become magnesium hydroxide



For this message the author OnlyMe has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 20, 2017 8:47 pm 
Offline
Newly registered Member

Joined: Mon Jun 05, 2017 6:14 am
Posts: 10
Has thanked: 0 times
Been thanked: 3 times
The hifi does not trip the rcd. Today I removed the back of the cooker and to my suprise found that there are two elements (one above and one below) that heat the oven. I had the element that was visible inside delivered today so I thought I would do some investigating..
The resistance on the top element and the newly delivered one were identical on my meter where as the reading was lower on the bottom element. I disconnected them one at a time and each time turned the oven on. Every time the rcd tripped- even with no elements connected.
The good news is that the rcd hasn't tripped all afternoon and I'm not going to turn the oven on as I know it will. I've got an appliance repair chap coming tomorrow to sort it as I've got other things to do.



For this message the author themoog has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Sat Oct 21, 2017 8:56 am 
Offline
BANNED

Joined: Wed Jun 14, 2017 8:38 am
Posts: 204
Has thanked: 696 times
Been thanked: 28 times
Did your electrician issue a certificate if so he would done an insulation resistance test on all circuits although cooker elements are common failures so is faulty wiring, you cannot measure element correctly with a multimeter, I have replaced oven elements in the past, whenever I replace consumer units I ensure all is working before leaving also did he do ramp test on rcd ?

Sent from my LG-K100 using Tapatalk


Top
 Profile  
Reply with quote  
PostPosted: Sat Oct 21, 2017 3:43 pm 
Offline
Newly registered Member

Joined: Mon Jun 05, 2017 6:14 am
Posts: 10
Has thanked: 0 times
Been thanked: 3 times
Yes I got all the certs.
It seems to be fixed now anyway- both elements on one of the ovens were toast. Leaking to earth apparently. The top and me has been replaced and the lower is on order and will be installed in a few days.
So far nothing has happened since the chap was here..



For this message the author themoog has received gratitude : multiman
Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 11 posts ] 


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO