Hi
I installed a pump for hot water only for the whole house, taken directly from the hot water cylinder. Cold is mains set at 2 bar via PRV.
The pump noise is fine but feels vibration in the floorboards when standing on them where the hot water pipes run under. Also all hot copper pipes in and out of pump feels vibration and not smooth when I touch them. I have spoken to pump manufacturer and followed installation guidelines. I have rubber mat then concrete slab then another rubber mat where the pump sits. I have used slow bend elbows. The plumping is all copper no plastic either compression or solder. Hot Cylinder Temp below 60degC.
The hot and cold pipes run under floor boards rested on joists which I believe is normal. I did put lagging where ever I reached between pipes and joists.
The cold water as said is main reduced to 2 bar has its pipes running under floor boards too but causes no vibration at all. But the pumped hot water does cause vibration and doesn't feel smooth flow.
Is there any way to get rid of this vibration? Or is it something to live with?


Last edited by yartin on Wed Jul 19, 2017 4:02 pm, edited 1 time in total.

Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Wed Jul 19, 2017 3:53 pm 
Offline
Senior Member

Joined: Fri Aug 01, 2014 9:57 am
Posts: 563
Location: Essex
Has thanked: 122 times
Been thanked: 125 times
Try a piece of foam under the rubber mat?

Mike

_________________
If it ain't broke, don't fix it!!


Top
 Profile  
Reply with quote  
PostPosted: Wed Jul 19, 2017 4:16 pm 
Offline
Senior Member

Joined: Fri Jun 09, 2017 12:55 pm
Posts: 127
Has thanked: 11 times
Been thanked: 11 times
London mike 61 wrote:
Try a piece of foam under the rubber mat?

Mike


I have heavy duty foam on floor board and rubber on concrete slab. There is no vibration at that part of the floorboards under the pump.

I now believe the source of the vibration is the pipes around the pump, in from cylinder and out of pump and even the cylinder overflow pipe which goes up to loft tank, when I touch them all same flow is not smooth and feels vibrating.
Could the pump be faulty?!


Top
 Profile  
Reply with quote  
PostPosted: Wed Jul 19, 2017 7:02 pm 
Offline
Senior Member

Joined: Fri Jun 09, 2017 12:55 pm
Posts: 127
Has thanked: 11 times
Been thanked: 11 times
I emailed pump manufacturer again today, they said: "In terms of the pump installation it sounds like you have done everything you can to try and limit the noise. You are increasing the pressure of water so we would expect there to be some vibration in the pipes."

It would have been different if it was concrete floor but airing cupboards and hot water cylinders are on first floors. Or more than twice the price for Megaflow but too late for me. Would I recommend pumps? It does great job relatively cheap but not sure.

I am lucky I use mains for the cold water and not another pump, otherwise more vibration every time turn the cold and when flushing WCs.

BTW the pump is the most renowned and expensive brand.

So it is the case to live with it.


Top
 Profile  
Reply with quote  
PostPosted: Wed Jul 19, 2017 7:21 pm 
Offline
Senior Member
User avatar

Joined: Mon Jan 12, 2015 6:42 pm
Posts: 685
Has thanked: 130 times
Been thanked: 196 times
Are the pipes securely clipped to the joists, walls, etc, for the whole system? If they're loose, I'd expect them to rattle about a fair bit.

_________________
Haste is the enemy of quality.


Top
 Profile  
Reply with quote  
PostPosted: Wed Jul 19, 2017 7:46 pm 
Offline
Senior Member

Joined: Fri Jun 09, 2017 12:55 pm
Posts: 127
Has thanked: 11 times
Been thanked: 11 times
chrrris wrote:
Are the pipes securely clipped to the joists, walls, etc, for the whole system? If they're loose, I'd expect them to rattle about a fair bit.


Yes all secured, I was repairing the floorboards so all lifted, and all pipes are fixed secure and no movement whatsoever, very solid fix , I even put laggings. No rattling in pipes. I turned pump while floorboards out and pipes don't budge at all.

I am now in the conclusion that vibration are by the pump in and out pipes is being propagated to pipes under floorboards which are rested on joists so you would feel the flow when I am standing on these boards otherwise you don't feel it. Does this make sense?


Top
 Profile  
Reply with quote  
PostPosted: Wed Jul 19, 2017 11:34 pm 
Offline
Senior Member
User avatar

Joined: Mon Jan 12, 2015 6:42 pm
Posts: 685
Has thanked: 130 times
Been thanked: 196 times
yartin wrote:
pipes under floorboards which are rested on joists so you would feel the flow when I am standing on these boards otherwise you don't feel it. Does this make sense?

The pipes should be clipped to the joists, not resting on them and the floorboards shouldn't be resting on the pipes at all. Difficult to say exactly how much practical difference this would make to the vibration you're feeling through the floorboards without being there to see how it is at the moment -- definitely "some difference", but possibly not enough to warrant lifting all the boards, possibly deepening the notches (in accordance with the rules on notching joists, obv), and relaying the pipework. It may be easier to put up with the vibration, at least until you have to change the pipework for some other reason.

All locally pumped water has some amount of vibration, as the output from the impeller has peaks and troughs, although modern pumps do have all sorts of fancy computer-designed channels that the water flows through to minimise this (looks a bit like a wobbly maze of channels etched into a plastic disc inside the impeller housing). If everything is done right, pipework wise, you have a decent modern pump, and the floor is structurally sound, then it shouldn't really be so bad that you can feel vibrations through the floor. But you do often find, especially in older installs, that the pipework is resting, unsecured, on the joists and floorboards are resting on the tops of the pipes. So the pipes vibrate against the floorboards.

You can get "joist pipe clips" that are lower profile than ordinary clips. They're particularly useful for clipping 22mm pipes in 1" notches (which is ordinarily the most you can take out of an 8" joist without weakening it too much). Clipping 15mm pipes into 8" joists isn't usually too much drama. But do make sure you check the regs on notching joists if you're intending to deepen any existing notches or add new ones.

_________________
Haste is the enemy of quality.


Top
 Profile  
Reply with quote  
PostPosted: Thu Jul 20, 2017 5:55 am 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 7353
Location: Northampton
Has thanked: 294 times
Been thanked: 903 times
A picture might help. Are the flexible hoses that connect the pump to the pipework straight or bent at all?

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html


Top
 Profile  
Reply with quote  
PostPosted: Thu Jul 20, 2017 10:29 am 
Offline
Senior Member

Joined: Fri Jun 09, 2017 12:55 pm
Posts: 127
Has thanked: 11 times
Been thanked: 11 times
Razor wrote:
A picture might help. Are the flexible hoses that connect the pump to the pipework straight or bent at all?


All pipes straight with slow bend elbows, photo attached.


Attachments:
IMG_1622.JPG
IMG_1622.JPG [ 110.4 KiB | Viewed 1093 times ]
Top
 Profile  
Reply with quote  
PostPosted: Thu Jul 20, 2017 10:39 am 
Offline
Senior Member

Joined: Fri Jun 09, 2017 12:55 pm
Posts: 127
Has thanked: 11 times
Been thanked: 11 times
chrrris wrote:
yartin wrote:
pipes under floorboards which are rested on joists so you would feel the flow when I am standing on these boards otherwise you don't feel it. Does this make sense?

The pipes should be clipped to the joists, not resting on them and the floorboards shouldn't be resting on the pipes at all. Difficult to say exactly how much practical difference this would make to the vibration you're feeling through the floorboards without being there to see how it is at the moment -- definitely "some difference", but possibly not enough to warrant lifting all the boards, possibly deepening the notches (in accordance with the rules on notching joists, obv), and relaying the pipework. It may be easier to put up with the vibration, at least until you have to change the pipework for some other reason.

All locally pumped water has some amount of vibration, as the output from the impeller has peaks and troughs, although modern pumps do have all sorts of fancy computer-designed channels that the water flows through to minimise this (looks a bit like a wobbly maze of channels etched into a plastic disc inside the impeller housing). If everything is done right, pipework wise, you have a decent modern pump, and the floor is structurally sound, then it shouldn't really be so bad that you can feel vibrations through the floor. But you do often find, especially in older installs, that the pipework is resting, unsecured, on the joists and floorboards are resting on the tops of the pipes. So the pipes vibrate against the floorboards.

You can get "joist pipe clips" that are lower profile than ordinary clips. They're particularly useful for clipping 22mm pipes in 1" notches (which is ordinarily the most you can take out of an 8" joist without weakening it too much). Clipping 15mm pipes into 8" joists isn't usually too much drama. But do make sure you check the regs on notching joists if you're intending to deepen any existing notches or add new ones.


I have checked all pipes under floorboards, all have metal clips and are very tight, pipes don't move or shift at all when I try to by hand.
Its not exactly vibration. It is more you feel water flow when standing immediately above the joists and floorboards where pipes are running, otherwise you don't feel it anywhere else. And it is only when the pumped hot water is running not when mains cold water is on. Hot and cold copper pipes are next to each other under floorboards.


Top
 Profile  
Reply with quote  
PostPosted: Thu Jul 20, 2017 7:31 pm 
Offline
Senior Member
User avatar

Joined: Mon Jan 12, 2015 6:42 pm
Posts: 685
Has thanked: 130 times
Been thanked: 196 times
Sounds like you've done everything you possibly can then. The only thing I can think is trying a different pump, but that's a potentially expensive proposition and might not make any difference at all.

_________________
Haste is the enemy of quality.


Top
 Profile  
Reply with quote  
PostPosted: Thu Jul 20, 2017 7:54 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 7353
Location: Northampton
Has thanked: 294 times
Been thanked: 903 times
I'd cut in one of these: https://www.toolstation.com/shop/Plumbi ... lve/p17726

and try to balance the noise against the output a little. You may find a point that gives great water and is quiet!

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html


Top
 Profile  
Reply with quote  
PostPosted: Fri Jul 21, 2017 9:14 am 
Offline
Senior Member

Joined: Fri Jun 09, 2017 12:55 pm
Posts: 127
Has thanked: 11 times
Been thanked: 11 times
chrrris wrote:
Sounds like you've done everything you possibly can then. The only thing I can think is trying a different pump, but that's a potentially expensive proposition and might not make any difference at all.


The one I have is ST 3.0 bar is a powerful pump and hence more noise and vibration. 1.5 bar would have been enough for me. But when shopping, I saw an offer and was very cheap and difference of £40 so went for it. It was a mistake because it is too much water if on full and not needed at all.


Last edited by yartin on Fri Jul 21, 2017 9:27 am, edited 1 time in total.

Top
 Profile  
Reply with quote  
PostPosted: Fri Jul 21, 2017 9:22 am 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 7353
Location: Northampton
Has thanked: 294 times
Been thanked: 903 times
If you check the ST website it says you can restrict the pump by up to 30% as I said above. Obviously on the output side not on the feed :thumbleft:

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html


Top
 Profile  
Reply with quote  
PostPosted: Fri Jul 21, 2017 9:33 am 
Offline
Senior Member

Joined: Fri Jun 09, 2017 12:55 pm
Posts: 127
Has thanked: 11 times
Been thanked: 11 times
Razor wrote:
If you check the ST website it says you can restrict the pump by up to 30% as I said above. Obviously on the output side not on the feed :thumbleft:


I have been in constant communication with ST for the last 2 months, several emails and suggestions but never mention of this. They do give good support plus 5 year warranty. I will check, sounds promising. do you have the link?
TBH I do struggle to control shower hot water as too much water, I am using thermostatic mixer
Cheers


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 16 posts ]  Go to page 1, 2  Next


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO