I have a separate fuse box in a workshop away from the house, the box, all the wiring and sockets etc were installed by an extremely competent electrician a few years back. During the past 6 months the socket breaker has tripped a few times. I've never been able to find a problem and its always happily returned to the 'on' position. This morning it again tripped, but despite removing all plugs from the sockets it still trips every time the power is switched on. I can't believe that there is a problem with the wiring, could it be the circuit breaker itself?

It is a: Merlin Gerin multi 9 C6OH RCB0 30mA C32 R30 26861


Attachments:
ResizerImage1029X1474.jpg
ResizerImage1029X1474.jpg [ 234.97 KiB | Viewed 594 times ]
Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Tue May 22, 2018 5:41 pm 
Offline
Senior Member

Joined: Mon Oct 27, 2008 11:23 am
Posts: 653
Location: Dronfield
Has thanked: 210 times
Been thanked: 148 times
So with nothing connected in the workshop it still trips?

Has any works been carried out recently anywhere?

Sent from my HUAWEI VNS-L31 using Tapatalk


Top
 Profile  
Reply with quote  
PostPosted: Tue May 22, 2018 5:48 pm 
Offline
Newly registered Member

Joined: Thu Apr 26, 2018 10:08 am
Posts: 7
Has thanked: 2 times
Been thanked: 0 times
Hi,
Nothing at all switched on, or even plugged in, and no work done at all except when the British Gas chap serviced the boiler in the house a few months back, but that is on a different fuse box.
The lights work OK, its only the sockets breaker that is tripping.


Top
 Profile  
Reply with quote  
PostPosted: Tue May 22, 2018 5:49 pm 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 23924
Location: hants/dorset border
Has thanked: 1485 times
Been thanked: 3791 times
They can weaken over time, particularly when they get tripped regularly.

If tripping with nothing connected then it can only be a wiring fault, whether that be water ingress/condensation/ rodent damage etc or say an unsleeved earth at a socket.

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/



For this message the author wine~o has received gratitude : chunya
Top
 Profile  
Reply with quote  
PostPosted: Tue May 22, 2018 5:50 pm 
Offline
Senior Member

Joined: Mon Oct 27, 2008 11:23 am
Posts: 653
Location: Dronfield
Has thanked: 210 times
Been thanked: 148 times
There must be a fault on that circuit then.

Sent from my HUAWEI VNS-L31 using Tapatalk


Top
 Profile  
Reply with quote  
PostPosted: Tue May 22, 2018 5:59 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7932
Has thanked: 45 times
Been thanked: 1356 times
Everyone has missed the obvious.

1) The correct term is circuit breaker, not socket breaker

2) You have not got ordinary circuit breakers, you have got RCBO's


An RCBO is cross between a circuit breaker and a RCD. One trips if too much current is drawn the other trips if there is current leaking to earth.

I suspect you have an earth fault.

Is any thing damp or wet? (switch the power off and open the sockets and have a look.

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here



For this message the author someone-else has received gratitude : chunya
Top
 Profile  
Reply with quote  
PostPosted: Tue May 22, 2018 6:24 pm 
Offline
Newly registered Member

Joined: Thu Apr 26, 2018 10:08 am
Posts: 7
Has thanked: 2 times
Been thanked: 0 times
Many thanks, I'll take a look at all the sockets tomorrow.
I don't think that damp is a problem ... rodent damage I can't even guess at, I'd have to check behind all the plaster board to see if that is a problem.
If everything seems OK, then might it be the RCBO?


Top
 Profile  
Reply with quote  
PostPosted: Tue May 22, 2018 6:27 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7932
Has thanked: 45 times
Been thanked: 1356 times
No, the rcbo is doing its job, you have to find the cause of the problem.

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

 

 




Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO