I fitted new boiler, and when firing up no fire, :cb led fault came up with dry fire! System is piped correctly and filled, pump runs fine and when i link the flow switch out for just a few seconds it fires but kettles, so i'm guessing faulty flow switch, but if pump is running where is the flow of system water going as its not going through boiler?
Any thoughts would be helpful thanks.
 Post subject:
PostPosted: Sat Aug 30, 2008 6:29 pm
Has thanked: 422 times
Been thanked: 3903 times
Has the boiler been commissioned by an RGI.
What are the led lights doing, which are on and or flashing.
 Post subject:
PostPosted: Sat Aug 30, 2008 6:42 pm
Hi Scruff and thanks for the quick reply.
Power led is on and the other two are flashing.
I'm the RGI but haven't come across this before so i thought 2 or more heads are better than 1.
 Post subject:
PostPosted: Sat Aug 30, 2008 7:27 pm
Have you unplugged the 5way pcb and checked for continuity between H the bottom two connections.
Have you checked the flow switch for blockage and continuity.
Another stupid suggestion is the impeller attached to the rotor in the pump
 Post subject:
PostPosted: Sat Aug 30, 2008 7:44 pm
Yes electrics are all good, not checked for blockage yet as it involves another drain down, and its not a silly question as i thought that myself but removed the pump centre screw and you can see the spline spinning and hear water going through it just confused me as to where it was going if its not going through the flow switch! I think i will drain down and check for blockage and probably change pump anyway as looks very old and scaled up! Typical Potterton ::b
 Post subject:
PostPosted: Sat Aug 30, 2008 8:00 pm
I would definitely check the flow switch for blockage or stuck paddle.
 Post subject:
PostPosted: Sat Aug 30, 2008 8:12 pm
Cool will let you know the outcome.
Thanks again Scruff :thumbright:
 Post subject:
PostPosted: Mon Sep 01, 2008 9:28 pm
Hi Scruff
Just to let you know problem solved! (In the end).
I drained down,stripped the flow switch which seemed clear and free, fitted new pump and still wouldn't fire, in the end after filling and draining about 4 times it finally kicked in to life :-P
I think there must of been some sort of blockage in the system but filled up with cleaner and is now running like a new one.............. oh it is a new one!!!!
 Post subject:
PostPosted: Mon Sep 01, 2008 9:59 pm
There may have been a bit of package stuck in the pipe or something.
Glad your sorted :thumbright: