It is currently Sat May 18, 2013 5:28 pm
PostPosted: Mon Aug 17, 2009 9:34 pm
I have a problem with a potterton performa 24 eco he I've been though the fault finding and still can't find the problem. It is coming on, the fan is running the, air pressure switch is making, the pump is running, the pressure differential is working and triggering the micro switch but it fires for around 10 sec then stops in the 10sec the ignition is still sparking but the burner on light doesn't come on. It does this 3 time then goes to flame fault.
I've so far changed the heat sensing electrode, PCB and igniter/gas valve cable but it still not working!! ::b
Could any one shed any light on it for me any help would be appreciated!!
 Post subject:
PostPosted: Mon Aug 17, 2009 10:02 pm
Has thanked: 95 times
Been thanked: 441 times
I take it you mean the flame sensing electrode?
Have you checked continuity of the lead from here back to the board?
Are the grommets in place to stop the electodes shorting out?
 Post subject:
PostPosted: Mon Aug 17, 2009 10:11 pm
Yeah the flame sensing electrode and the grommets are fine. Ill check the continuity.
I'm at a loss now.
 Post subject:
PostPosted: Mon Aug 17, 2009 10:38 pm
Has thanked: 85 times
Been thanked: 327 times
Anyone been out to check the burner pressures?
Dave
www.drlgas.co.uk
 Post subject:
PostPosted: Mon Aug 17, 2009 10:41 pm
Has thanked: 226 times
Been thanked: 2626 times
Has anyone checked the gas meter/valve.
Wont be the first time I was called out and there's no money on the card, or someones turn the valve off.