So here's my problem. Running the shower for it seems any longer than about 10 minutes turns the boiler off. It's a bit random, but it's ptretty much always takes at least 10 minutes of being in the shower for this to happen. When I say the boiler turns off, I mean the pilot light goes out as well, which led me to think it's a boiler problem . However, after a couple callouts they think the problem lies with the shower unit and not the boiler (has had full service), as it does not happen with any other taps (left it running hot for almost an hour and boiler still working).

The shower I have is a Mira 415 mixer shower (not sure what generation it is). When running it, it gets hot just fine and apart from swinging to a bit hot or cold sometimes, runs pretty well, until the boiler turns off and of course it just goes cold again.

For reference, my boiler is a Ferroli Optima 901 combi boiler (yes I've heard it's a bad boiler, but it's actually in very good condition according to the Engineers).

Could anyone give me some advice on what potentially the problem is, and how to go about fixing it? I'm pretty good with DIY and happy to replace the shower myself if needed, I just don't know what I'd need to buy (preferably the minimum to fix it). Oh also, the shower is now dripping, so I think I might have to replace the main mixer unit anyway.

Any help would be really appreciated. I've attached a photo of the mixer unit so maybe someone can tell me what generation it is.


Attachments:
IMG_0395.jpg
IMG_0395.jpg [ 38.11 KiB | Viewed 689 times ]
Top
 Profile  
 
PostPosted: Wed Jul 21, 2010 1:52 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
The 415 is a pressure balancing mixer valve pre 1988.

A good service and a new pressure balancing cartridge assembly (902 91) should do the trick.

You may want to type the shower doctor into google, where you should find the schematic, and be able to order the part,

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html



For this message the author thescruff has received gratitude : sureshk
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 1:58 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 3577
Has thanked: 51 times
Been thanked: 230 times
Have you tried running another hot tap at a very slow rate for 10 mins or so, to repliacte the shower working?

It coulbe be the shower, or maybe the boiler isn't modulating down properly. Could be the max/minimum burner pressure has not been set properly.

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : sureshk
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 2:21 pm 
Offline
Newly registered Member

Joined: Wed Jul 21, 2010 1:13 pm
Posts: 4
Has thanked: 2 times
Been thanked: 0 times
Tried running a hot tap at a slower rate, but if its too slow the boiler doesn't even kick in, but when the boiler is on (even at reasonably slow flow rate) it stays on just fine.

Just another quick question, would I be right in assuming that if could replace the whole unit with the same model and as long as the cartridge assembly on the replacement is working fine, it should fix the problem? Reason I ask is I can hopefully get a used replacement pretty cheap - a lot cheaper than cartridge assembly anyway.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 2:27 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
If you get the same model and it works ok, just change the lot.

Assuming the boiler is old ish, has the problem recently started and getting worse.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 2:30 pm 
Offline
Newly registered Member

Joined: Wed Jul 21, 2010 1:13 pm
Posts: 4
Has thanked: 2 times
Been thanked: 0 times
problem started about a month ago, not really getting any worse. has had the full service and a few parts replaced since but this problem wasn't resolved.

thanks for all the help by the way, really impressed with the quick responses! :D


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 2:33 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
It's almost certainly the cartridge.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 2:59 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 5141
Location: Northampton
Has thanked: 76 times
Been thanked: 373 times
Or a blocked showerhead :wink:

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 3:05 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
Razor wrote:
Or a blocked showerhead :wink:


Or a blocked rose (showerhead) good point Razor :thumbright:

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 4:53 pm 
Offline
Newly registered Member

Joined: Wed Jul 21, 2010 1:13 pm
Posts: 4
Has thanked: 2 times
Been thanked: 0 times
Hmm showerhead seems fine, no visible blockages and water comes out just fine.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Jul 21, 2010 5:27 pm 
Offline
Senior Member
User avatar

Joined: Fri May 30, 2008 7:50 am
Posts: 3306
Location: Notts/Derbys
Has thanked: 0 times
Been thanked: 32 times
The shower has eco conscience and is trying to make you shower in less time, therefore help save the planet.
Why can't you shower in less than 10mins anyway - busy eh? :wink:

_________________
Sciatica is a pain in the Ar5e ............ and leg


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Jul 22, 2010 5:26 pm 
Offline
Newly registered Member

Joined: Fri Jun 04, 2010 5:39 pm
Posts: 57
Location: North London
Has thanked: 2 times
Been thanked: 3 times
This happens to my boiler too when using my thermostatic Mira shower, the plumber reckons my water flow is so low the boiler can not reduce the flame strength enough to keep the water temperature below the 65C safety trip out. The flow rate is terrible, I can only run one tap at a time in the house.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Aug 04, 2010 3:16 pm 
Offline
Newly registered Member

Joined: Fri Jun 04, 2010 5:39 pm
Posts: 57
Location: North London
Has thanked: 2 times
Been thanked: 3 times
Did the poster get to the bottom of this? As my boiler has a similar problem it would be interesting to find out your solution. Shorter showers are fine for me but the misses like to shower for 30 mins! I've tried to convince her that she's no cleaner than she was 10 minutes into the shower!

At the moment the gas supply is turned down as on full filt it the boiler shuts off after 2 minutes. The hi/low gas regulation is set for CH only (upon install), hot water gas flows are factory set according to the manual. (Heatline S24) I do have very low water flow which is what the last plumber blamed the problem on - surely a boiler should be able to regulate the gas enough to cater for that?

I need to get this fixed before winter as the turned-down gas bodge will affect the central heating. PS I do have a carbon monoxide alarm - I'm aware that restricting the gas flow may alter the way the boiler burns, affecting CO emissions.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Aug 04, 2010 3:25 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
First if you expect an answer you don't bodge Gas, end of thread. ::b

Your problem is not the same as the Op so start another with details.

What is the mains pressure/flow in Ltrs/min.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 14 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 22 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling