Posted: Wed Jul 21, 2010 1:31 pm |
|
 |
| Newly registered Member |
Joined: Wed Jul 21, 2010 1:13 pm Posts: 4 Has thanked: 2 times Been thanked: 0 times
|
|
So here's my problem. Running the shower for it seems any longer than about 10 minutes turns the boiler off. It's a bit random, but it's ptretty much always takes at least 10 minutes of being in the shower for this to happen. When I say the boiler turns off, I mean the pilot light goes out as well, which led me to think it's a boiler problem . However, after a couple callouts they think the problem lies with the shower unit and not the boiler (has had full service), as it does not happen with any other taps (left it running hot for almost an hour and boiler still working).
The shower I have is a Mira 415 mixer shower (not sure what generation it is). When running it, it gets hot just fine and apart from swinging to a bit hot or cold sometimes, runs pretty well, until the boiler turns off and of course it just goes cold again.
For reference, my boiler is a Ferroli Optima 901 combi boiler (yes I've heard it's a bad boiler, but it's actually in very good condition according to the Engineers).
Could anyone give me some advice on what potentially the problem is, and how to go about fixing it? I'm pretty good with DIY and happy to replace the shower myself if needed, I just don't know what I'd need to buy (preferably the minimum to fix it). Oh also, the shower is now dripping, so I think I might have to replace the main mixer unit anyway.
Any help would be really appreciated. I've attached a photo of the mixer unit so maybe someone can tell me what generation it is.
| Attachments: |

IMG_0395.jpg [ 38.11 KiB | Viewed 689 times ]
|
|
|
| Top |
|
 |
|
thescruff
|
Posted: Wed Jul 21, 2010 1:52 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39986 Has thanked: 187 times Been thanked: 2114 times
|
|
The 415 is a pressure balancing mixer valve pre 1988.
A good service and a new pressure balancing cartridge assembly (902 91) should do the trick.
You may want to type the shower doctor into google, where you should find the schematic, and be able to order the part,
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
gas4you
|
Posted: Wed Jul 21, 2010 1:58 pm |
|
 |
| Senior Member |
Joined: Mon Apr 13, 2009 8:03 pm Posts: 3577 Has thanked: 51 times Been thanked: 230 times
|
|
Have you tried running another hot tap at a very slow rate for 10 mins or so, to repliacte the shower working?
It coulbe be the shower, or maybe the boiler isn't modulating down properly. Could be the max/minimum burner pressure has not been set properly.
_________________ Dave
www.drlgas.co.uk
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
sureshk
|
Posted: Wed Jul 21, 2010 2:21 pm |
|
 |
| Newly registered Member |
Joined: Wed Jul 21, 2010 1:13 pm Posts: 4 Has thanked: 2 times Been thanked: 0 times
|
|
Tried running a hot tap at a slower rate, but if its too slow the boiler doesn't even kick in, but when the boiler is on (even at reasonably slow flow rate) it stays on just fine.
Just another quick question, would I be right in assuming that if could replace the whole unit with the same model and as long as the cartridge assembly on the replacement is working fine, it should fix the problem? Reason I ask is I can hopefully get a used replacement pretty cheap - a lot cheaper than cartridge assembly anyway.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Wed Jul 21, 2010 2:27 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39986 Has thanked: 187 times Been thanked: 2114 times
|
|
If you get the same model and it works ok, just change the lot.
Assuming the boiler is old ish, has the problem recently started and getting worse.
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
sureshk
|
Posted: Wed Jul 21, 2010 2:30 pm |
|
 |
| Newly registered Member |
Joined: Wed Jul 21, 2010 1:13 pm Posts: 4 Has thanked: 2 times Been thanked: 0 times
|
|
problem started about a month ago, not really getting any worse. has had the full service and a few parts replaced since but this problem wasn't resolved.
thanks for all the help by the way, really impressed with the quick responses! :D
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Wed Jul 21, 2010 2:33 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39986 Has thanked: 187 times Been thanked: 2114 times
|
|
It's almost certainly the cartridge.
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
Razor
|
Posted: Wed Jul 21, 2010 2:59 pm |
|
 |
| Senior Member |
 |
Joined: Wed Nov 14, 2007 10:21 pm Posts: 5141 Location: Northampton Has thanked: 76 times Been thanked: 373 times
|
Or a blocked showerhead 
_________________ As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference. donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Wed Jul 21, 2010 3:05 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39986 Has thanked: 187 times Been thanked: 2114 times
|
Razor wrote: Or a blocked showerhead  Or a blocked rose (showerhead) good point Razor 
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
sureshk
|
Posted: Wed Jul 21, 2010 4:53 pm |
|
 |
| Newly registered Member |
Joined: Wed Jul 21, 2010 1:13 pm Posts: 4 Has thanked: 2 times Been thanked: 0 times
|
|
Hmm showerhead seems fine, no visible blockages and water comes out just fine.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
Steve the Gas
|
Posted: Wed Jul 21, 2010 5:27 pm |
|
 |
| Senior Member |
 |
Joined: Fri May 30, 2008 7:50 am Posts: 3306 Location: Notts/Derbys Has thanked: 0 times Been thanked: 32 times
|
The shower has eco conscience and is trying to make you shower in less time, therefore help save the planet. Why can't you shower in less than 10mins anyway - busy eh? 
_________________ Sciatica is a pain in the Ar5e ............ and leg
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
OhmMyDog
|
Posted: Thu Jul 22, 2010 5:26 pm |
|
 |
| Newly registered Member |
Joined: Fri Jun 04, 2010 5:39 pm Posts: 57 Location: North London Has thanked: 2 times Been thanked: 3 times
|
|
This happens to my boiler too when using my thermostatic Mira shower, the plumber reckons my water flow is so low the boiler can not reduce the flame strength enough to keep the water temperature below the 65C safety trip out. The flow rate is terrible, I can only run one tap at a time in the house.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
OhmMyDog
|
Posted: Wed Aug 04, 2010 3:16 pm |
|
 |
| Newly registered Member |
Joined: Fri Jun 04, 2010 5:39 pm Posts: 57 Location: North London Has thanked: 2 times Been thanked: 3 times
|
|
Did the poster get to the bottom of this? As my boiler has a similar problem it would be interesting to find out your solution. Shorter showers are fine for me but the misses like to shower for 30 mins! I've tried to convince her that she's no cleaner than she was 10 minutes into the shower!
At the moment the gas supply is turned down as on full filt it the boiler shuts off after 2 minutes. The hi/low gas regulation is set for CH only (upon install), hot water gas flows are factory set according to the manual. (Heatline S24) I do have very low water flow which is what the last plumber blamed the problem on - surely a boiler should be able to regulate the gas enough to cater for that?
I need to get this fixed before winter as the turned-down gas bodge will affect the central heating. PS I do have a carbon monoxide alarm - I'm aware that restricting the gas flow may alter the way the boiler burns, affecting CO emissions.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Wed Aug 04, 2010 3:25 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39986 Has thanked: 187 times Been thanked: 2114 times
|
First if you expect an answer you don't bodge Gas, end of thread. Your problem is not the same as the Op so start another with details. What is the mains pressure/flow in Ltrs/min.
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|