Further to my post yesterday, I have now replaced the air pressure switch but I still cannot get the boiler to ignite.
The ignition sparks if I blow down the tube to the APS but soon goes out.
I have also checked the heat exchanger and this is very clean.


Top
 Profile  
 
 Post subject:
PostPosted: Mon Jan 25, 2010 2:48 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
It's pointless and confusing to start another thread. ::b

Is the fan going to high speed.

Is the flue blocked.

Is the pump working.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Sabre 25HE not Igniting
PostPosted: Mon Jan 25, 2010 8:40 pm 
Offline
Newly registered Member

Joined: Tue Dec 29, 2009 11:37 am
Posts: 8
Has thanked: 0 times
Been thanked: 0 times
Pump working, fan working. Can only get ignition when I blow on tube from Air Pressure Switch.
Not sure what to do next apart from disassemble flue and check that nozzles to Venturi are not blocked.
Boiler is not very old and the PCB and thermistors have already been changed in the last couple of years.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Mon Jan 25, 2010 10:22 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
Yes, but does the fan run without blowing in the tube.

When you changed the APS did you connect the tubes in the right order.

Are the tubes split or damaged.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Sabre 25HE not igniting
PostPosted: Tue Jan 26, 2010 6:11 am 
Offline
Newly registered Member

Joined: Tue Dec 29, 2009 11:37 am
Posts: 8
Has thanked: 0 times
Been thanked: 0 times
Fan runs without blowing down tube and both tubes are in perfect condition.
When you switch on the boiler the start up sequence is as normal, the only thing that does not happen is the ignition spark and ignition. I am sure that I fitted the APS correctly but I will switch the tubes just to make sure.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Sabre 25HE not igniting
PostPosted: Tue Jan 26, 2010 3:16 pm 
Offline
Newly registered Member

Joined: Tue Dec 29, 2009 11:37 am
Posts: 8
Has thanked: 0 times
Been thanked: 0 times
Tubes to APS checked and are correct, and actually you cannot swap the tubes around due to the length of one of them. Removed fan assembly and checked venturi, both clean. Flue also free from muck and intake quite clear.
I am thinking that maybe there is a problem with the igntion pcb although I am loath to fork out on such an expensive part.

I am not really sure what to do next.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Tue Jan 26, 2010 3:42 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39986
Has thanked: 187 times
Been thanked: 2114 times
A boiler go through a sequence.

The pump has to run, then fan, if it gets that far everything is ok, so you are left with the ignition.

If you look in the fault finding section it will give a couple of options.

Electrode, lead, pcb.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: Sabre 25HE not igniting
PostPosted: Thu Jan 28, 2010 4:34 pm 
Offline
Newly registered Member

Joined: Tue Dec 29, 2009 11:37 am
Posts: 8
Has thanked: 0 times
Been thanked: 0 times
Electrode, lead and PCB all exchanged and still no ignition!

I have ordered a High Limit thermostat as this figures on the fault diagram a couple of times. Something is actively stopping ignition.

If this doesn't work, I am going to attack it with a club hammer.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 8 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling