PostPosted: Sun Apr 15, 2007 6:02 pm    Post subject: More electrical horrors Add User to Ignore List Reply with quote

I have come across all these nasties whilst out and about in, and all in the last year or so Shocked

Enjoy!!

This picture needs very little explanation.



==============================================

I got called to a house by a customer who said her shower stopped working about a week ago, and yesterday she heard a bang and some fizzing in the bathroom.

This is what I found under a floorboard:



It is a white sheathed 6.0mm˛ T&E cable, which was sat in a notch in the top of a joist with a nail through it. The joist and floorboard were charred, and the live, earth and all but three strands of the neutral have vaporised.

It was fed from a non RCD circuit with a 45A rewireable fuse which had not blown, so the cable was still live when I arrived. Shocked

The customer had been stood on the the floor with wet, bare feet after a bath.

=============================================

Breif history:

Extention / loft conversion to a bungalow. Original sparkie went AWOL. He had replaced the consumer unit, but left this under the floorboards below the consumer unit / intake.





The 1.5mm˛ SWA feeds a fairly well loaded 6 way CU in the garage. The joint box is fed in 2.5mm˛ fed from the 32A socket MCB. The armouring is no longer earthed either.

=============================================

This was taken in an under the stairs cupboard which has been converted to a downstairs WC.

The room did not border an external wall, so the soloution for the fan?



=============================================

This picture is of a CU with a loose screw connecting the neutral bars together.


The load was relativly light as the CU fed a portakabin.
There were 2no. 2kW panel heaters, 3no. 4' fluorescents and 4no. twin sockets.


You can see where the burning has been painted over on the trunking and ceiling Shocked












=============================================

This picture is of a fluorescent fitting in a factory.

It is fed from 2no. 1mm˛ red singles in PVC tube. Not a CPC in sight.



==============================================

Here is a 60VA DL transformer which stopped working, and was found sat on a DL lamp.




==============================================

Nice meter tails. 4.0mm˛ rubber twin cable. It had gone all crumbly.
Cutout fuse was a 100A BS 88



==============================================

This picture is of a pull switch.

A studwork wall was put up right where the 2 way pull switch was located.

What to do? Move the pull switch 2 inches? Oh no, that would be far too simple! Lets just cut the string off, and plaster it in to the new wall!

It had been like this for a good long while, and was still live when we arrived to rewire the lights!



============================================

This picture is of a fuse box. It was still live until last week, when the head / meter fell off the wall. The dno arrived and replaced this but refused to reconnect.

Wonder why Laughing

Kitchen fuse box

Note the fused neutrals, asbestos and wooden enclosure Shocked



The kitchen fuse box was fed from this mess



I refused to reconect it too Laughing Laughing

=============================================

This picture is a flush mounted 4 way wylex CU, which is supplied from an external meter box. The tails run through the cavity and enter through an oversized hole in the rear of the CU.

Not a problem until cavity wall insulation was installed!



=============================================

This is a GU10 downlighter.
It is connected to phase and earth only, yet it is on and working.
The neutral can be seen not connected just to the left of the DL.



=============================================

== Metal Clad FCU ==
This MEM FCU has had it's fuse holder retaining screw snapped off, and as these FCUs have a spring loaded fuse carrier it has been wedged in place with a matchstick.



=============================================

== Big Commercial Mess ==
In a cupboard in a nightclub in Leeds. Also feeds 4 offices and a shop above.







=============================================

== DNO cable repair ==
DNO cable accidentally got severed during some building work. Tho DNO attended and repaired it.
It does not feed anything in this building. It feeds the shop above.







=============================================

== Fusebox Fire ==
This is a proteus fusebox (Its a wylex copy)
The circuit fed a 9.5kW shower on a 6.0mm˛ t&e cable. The fuse was a 45A rewireable. These boards are designed for a maximum of 30A per outgoing way.





=============================================

== Hidden Joint Boxes ==
A couple of nasty joint boxes found hidden under floors.





=============================================

== Bath Socket ==
A socket rather close to a bath
(The bath was just being stored there on a new build project, but made for a good photo) Laughing

Back to top
View user's profile Send private message Send e-mail MSN Messenger

You may not be able to see the full post including pictures unless you Register or Log in

   
Hinton Heating
Gas/Heating Expert


Joined: 16 Jan 2006
Posts: 4384
Location: Bournemouth

PostPosted: Sun Apr 15, 2007 6:11 pm    Post subject: Add User to Ignore List Reply with quote

Nice collection of bad electrics!

Good to see they've made it to the rougues gallery!

_________________
www.hintonheating.com

Back to top
View user's profile Send private message Send e-mail
panlid
Senior Member


Joined: 16 Jan 2006
Posts: 3536

PostPosted: Sun Apr 15, 2007 6:15 pm    Post subject: Add User to Ignore List Reply with quote

i think the last one is the worst Shocked Laughing
Back to top
View user's profile Send private message
Hinton Heating
Gas/Heating Expert


Joined: 16 Jan 2006
Posts: 4384
Location: Bournemouth

PostPosted: Sun Apr 15, 2007 6:21 pm    Post subject: Add User to Ignore List Reply with quote

just imagine that, storing a bath next to a plug... I hope the plumber is Part P registered to place a water carrying device, so close to a socket... Was is notified? Laughing
_________________
www.hintonheating.com

Back to top
View user's profile Send private message Send e-mail
bathstyle
BANNED


Joined: 17 Jan 2006
Posts: 926

PostPosted: Sun Apr 15, 2007 6:22 pm    Post subject: Add User to Ignore List Reply with quote

There's no grommet on the back box on the first picture, I'm appalled that you didn't point this out Wink

Laughing
Back to top
View user's profile Send private message
ultimatehandyman
Site Admin


Joined: 16 Jul 2005
Posts: 14323
Location: Darwen, Lancashire

PostPosted: Sun Apr 15, 2007 8:09 pm    Post subject: Add User to Ignore List Reply with quote

That is an awesome collection Thumbright

Some of those pictures are very scary Shocked

_________________
DIY | DIY Video
Back to top
View user's profile Send private message Send e-mail
Hitch
Senior Member


Joined: 16 Jan 2006
Posts: 3209
Location: Somerset

PostPosted: Sun Apr 15, 2007 8:22 pm    Post subject: Add User to Ignore List Reply with quote

I like the extractor fan in the floor Laughing
_________________
Why isn't the number 11 pronounced onety one?
Back to top
View user's profile Send private message
diypeter
Senior Member


Joined: 07 Jan 2007
Posts: 102
Location: scotland

PostPosted: Sun Apr 15, 2007 8:26 pm    Post subject: Add User to Ignore List Reply with quote

sure are some scary things happened there i have come across some frighting sights in the electrics but thankfully nothing as bad as any of these Shocked
_________________
diy is for real not for fun
Back to top
View user's profile Send private message MSN Messenger
skiking
Senior Member


Joined: 13 Sep 2006
Posts: 3558
Location: Cheshire

PostPosted: Sun Apr 15, 2007 8:35 pm    Post subject: Add User to Ignore List Reply with quote

The fan next to the toilet was good....one slip and its 'sh*t hits the fan' Laughing
Back to top
View user's profile Send private message
panlid
Senior Member


Joined: 16 Jan 2006
Posts: 3536

PostPosted: Sun Apr 15, 2007 8:45 pm    Post subject: Add User to Ignore List Reply with quote

Laughing Laughing Laughing
Back to top
View user's profile Send private message
Andrew
Senior Member


Joined: 16 Aug 2006
Posts: 415
Location: Sunny Southend!

PostPosted: Fri Apr 20, 2007 6:23 pm    Post subject: Add User to Ignore List Reply with quote

It's scary how close people can live to death without knowing it. It's not a pleasant thought and supports the argument for regulated working practices, however much they "get in the way".

I'm appalled at this post and can't believe people can do jobs like this and are able to sleep at night. They've got to be absolultely useless, because it doesn't take any longer to do a right correctly.

Shocked
Back to top
View user's profile Send private message
Ducati Jack
Junior Member


Joined: 03 May 2007
Posts: 2
Location: West Sussex

PostPosted: Thu May 03, 2007 7:40 pm    Post subject: Add User to Ignore List Reply with quote

Holy Cow. I'm fairly new to electrical work and have only just passed my
Part P. I can see now why they introduced it !! Shocked
Back to top
View user's profile Send private message
ultimatehandyman
Site Admin


Joined: 16 Jul 2005
Posts: 14323
Location: Darwen, Lancashire

PostPosted: Thu May 03, 2007 8:46 pm    Post subject: Add User to Ignore List Reply with quote

Ducati Jack wrote:
Holy Cow. I'm fairly new to electrical work and have only just passed my
Part P. I can see now why they introduced it !! Shocked


They introduced part p as a stealth tax Wink

_________________
DIY | DIY Video
Back to top
View user's profile Send private message Send e-mail
Hinton Heating
Gas/Heating Expert


Joined: 16 Jan 2006
Posts: 4384
Location: Bournemouth

PostPosted: Thu May 03, 2007 9:34 pm    Post subject: Add User to Ignore List Reply with quote

Part P wont stop bad workmanship like this... most bad DIYers will continue as they always have, and stick 2 fingers up to Part P, just as they do to Corgi!

Can we get this on the 2nd page, as takes ages to scroll thro all those pictures!

_________________
www.hintonheating.com

Back to top
View user's profile Send private message Send e-mail
Hinton Heating
Gas/Heating Expert


Joined: 16 Jan 2006
Posts: 4384
Location: Bournemouth

PostPosted: Thu May 03, 2007 9:34 pm    Post subject: Add User to Ignore List Reply with quote

please! 8-)
_________________
www.hintonheating.com

Back to top
View user's profile Send private message Send e-mail

You may not be able to see the full post including pictures unless you Register or Log in

   
Display posts from previous:   
Post new topic   This topic is locked: you cannot edit posts or make replies.    www.ultimatehandyman.co.uk Forum Index -> Rogues Gallery All times are GMT
Goto page 1, 2  Next
Page 1 of 2

Similar Topics
Topic Author Forum Replies Last Post
This topic is locked: you cannot edit posts or make replies. Sticky: DIY electrical work and the law ban-all-sheds Electric Forum UK 0 Thu Dec 20, 2007 4:50 pm View latest post
ban-all-sheds
This topic is locked: you cannot edit posts or make replies. Bathroom horrors kath Painting & Decorating Forum 10 Wed May 07, 2008 8:41 pm View latest post
Welsh Decorator
This topic is locked: you cannot edit posts or make replies. Oak Electrical Service - Electrical C... hassy General DIY forum 3 Mon Sep 07, 2009 10:44 pm View latest post
17edSparkyJoe
This topic is locked: you cannot edit posts or make replies. electrical asp1 Electric Forum UK 2 Sun Jun 22, 2008 11:29 pm View latest post
Jaeger_S2k
This topic is locked: you cannot edit posts or make replies. Electrical help gaz Electric Forum UK 4 Sat Feb 10, 2007 2:35 pm View latest post
gaz
This topic is locked: you cannot edit posts or make replies. electrical asp1 Electric Forum UK 1 Wed Jun 18, 2008 7:49 pm View latest post
ultimatehandyman


 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You can attach files in this forum
You can download files in this forum

Share/Save/Bookmark

 

click here

 



ultimatehandyman privacy policy

Contact

Powered by phpBB © 2001, 2005 phpBB Group
phpBB SEO

Diy forum - Decking - plastering - Plumbing - DIY - Tiling