It is currently Fri Sep 21, 2018 1:00 pm
 Post subject: Live neutral reversed
PostPosted: Mon Oct 02, 2017 3:22 pm
Hi, I have added 3x double sockets to the ring main downstairs. The first socket is fine, when tested with a socket tester. The other 2 are showing a live neutral reverse, but work. When i use my meter to check polarity all is fine. All connections are correct, continuity is correct, so i'm a little stumped. When i get home later, i'm going to plug a lamp into the socket with out a lamp to see if get a permanent live when the socket is switched off. Any other tests i can do? if the cables are faulty, then it is more than one. Could i be that unlucky?
PostPosted: Mon Oct 02, 2017 6:05 pm
Has thanked: 64 times
Been thanked: 541 times
Not sure how socket testers reference, I have seen where a disconnected earth can give odd readings on test equipment showing line - neutral reversal rather than no earth. Sockets will work with no earth and with line - neutral reversible, however with the UK system it is not safe, in some countries they use double pole MCB's but not in UK.
Using a loop impedance tester we actually draw current so any poor earth will be highlighted, without the loop test which some plug in tester do, you can get all sorts of bad readings.
For this message the author ericmark has received gratitude : Dave54
PostPosted: Mon Oct 02, 2017 6:19 pm
Has thanked: 1484 times
Been thanked: 3785 times
Can you describe exactly how you have extended the ring ?
PostPosted: Tue Oct 03, 2017 9:30 am
Hi, i removed a socket on the existing ring, took 1x cable to the first new socket (which shows no faults) then looped out/in to the 2nd & 3rd, then connected back in to the other cable from the original removed socket
The test with the lamp was fine. There was no permanent live when the socket was switched off
PostPosted: Tue Oct 03, 2017 3:51 pm
Has thanked: 1119 times
Been thanked: 1034 times
Are you sure you have connected to the correct connections int he back of the sockets? Some can look similar, but are different.
Do the other sockets already on the ring test OK?
If they do then it's probably either something you have done or a fault with the cable or sockets.
I say "probably" because without more thorough testing with the right kit, (as Eric says above) and knowledge of how your particular socket tester works, then it can be difficult to find a fault like this via a forum.
PostPosted: Tue Oct 03, 2017 3:54 pm
yes, all connections are fine. I'm steering towards faulty cable,too.
PostPosted: Tue Oct 03, 2017 3:58 pm
Long shot though I'm afraid.
Possibly mechanically damaged when pulling in somehow.
PostPosted: Tue Oct 03, 2017 5:54 pm
Has thanked: 45 times
Been thanked: 1334 times
"faulty" is often used when it should not be used.
How do you suppose the cable is "faulty" if there was a fault it would have gone bang. If L & N really are reversed it has been connected wrong.
Why not post pictures of the back of all sockets concerned and the "tester" used.
PostPosted: Tue Oct 03, 2017 6:59 pm
Could be a neutral /Earth fault, down to a sharp edge or something when pulling in.
Disconnect cable and test, although you need a Megger really.
Depends how the socket tester works.
ETA Disregard that. You need to check the wiring again.
PostPosted: Tue Oct 03, 2017 8:09 pm
Approved Electrician
Has thanked: 165 times
Been thanked: 578 times
Double pole or single pole switched sockets?
PostPosted: Wed Oct 04, 2017 9:51 am
hi, the only other connections i haven't checked again are the junctions under the floor where the old socket was, all others are correct, i don't need to send pics.
My sockets are single pole btw.
I forgot to mention i have had readings from N to E of 40v, but I have had my meter on these connections 20 plus times, and the vast majority of times it reads 0v.
Pic attached to show the sockets are wired