 Post subject: Kitchen wiring
PostPosted: Wed Apr 04, 2018 9:15 pm 
Offline
Newly registered Member

Joined: Tue Nov 08, 2016 1:49 pm
Posts: 8
Has thanked: 0 times
Been thanked: 0 times
I am planning a refit of some rooms in the house and will have the ceilings down, so i want to take the opportunity to run new wiring ready for when i do the kitchen later this year.

Intention is to have an electric induction hob, integrated electric oven, integrated matching microwave and an extractor hood.

My question is whether to run a single 6mm feed for the appliances or whether they need to be on two separate ones.

The hob and the extractor will be at the opposite end of the kitchen (about 5m) from the oven and microwave.

I haven’t confirmed exactly which appliances yet but likely to be from Ikea.

Oh...there will also be a fridge but i assume I can just plug that into a socket on the ring main, or at worst run a fused spur to it.

Can anyone advise please?

Thanks.


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
 Post subject: Re: Kitchen wiring
PostPosted: Wed Apr 04, 2018 9:28 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7684
Has thanked: 44 times
Been thanked: 1303 times
It will depend on what you actually get as to cable size.
I would run 6mm for each, better safe than sorry (yes it shouldn't need it but that's now.........)
Oh do yourself a favour, don't have an integrated microwave. Build a cupboard with ventilation at the back and a nice trim. Then when the microwave packs up you can easily change it.

I hate most integrated stuff. I never wanted it but we have hob (gas) and oven / grille and fridge and Freezer.

Freezer packed up years ago, hob only half works, and don't even mention integrated washing machine

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
 Post subject: Re: Kitchen wiring
PostPosted: Wed Apr 04, 2018 9:53 pm 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 2643
Location: North Wales
Has thanked: 64 times
Been thanked: 541 times
If an appliance is protected with a 13A fuse be it in a plug or a FCU then the size of the MCB/RBCO/Fuse feeding the socket does not matter, as long as it protects the cable. However once over 13A we have no reasonable sized disconnection units able to disconnect in the event of a fault, so the protective device size is controlled by what the appliance manufacturer says.

The standard size for a cooker is 32A however some people today do fit 45A supplies, with everything on with my cooker looking at somewhere around 50A, so with stand alone units 45A is reasonable, however with separate oven and hob it is possible that the oven can have a 16A limit, in mothers kitchen a SWA cable feeds a mini consumer unit with 4 RBCO's oven, hob, sockets, and boiler, however it does not look really good stuck in the kitchen.

So some one needs to design, this could be 6 bunched cables going to main consumer unit, or a mini consumer unit, or some other option, but the main thing about design is you need to know what you are supplying. Of course one can over engineer and use 10mm cable for two positions where the cooker may go, and if it does not go there then simply swap the RBCO/MCB, personally I would use 4 or 6 mm and limit the supply to 25 or 32 amp.

But we can't design anything without knowing exactly what is to be fitted.


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO