HI

I recently had an Ideal Logic 30+ combi boiler fitted as a replacement.Since the installation the boiler pressure has slowly risen from 1bar to 2bar, and I have to vent the rads every 3/4 days to get rid of air, once went to nearly 3bar, this time I had to vent the rads to reduce the pressure.
The rads also become noisy when they require venting(2 of the 5 rads never need venting,there are 2 upstairs and 3 downstairs, 4 are fitted with TRVs)

The installer was called back but left scratching his head.

The boiler is under warranty but I'd like a bit more info. before calling them out.
Any help would be much appreciated

Thanks
Tony


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
 

You may not be able to see the full post including pictures unless you register or log in

PostPosted: Wed Feb 16, 2011 5:58 pm 
Offline
Senior Member
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 45947
Has thanked: 254 times
Been thanked: 2931 times
What type of system open vent or sealed.



For this message the author thescruff has received gratitude : microgreen
Top
 Profile  
 
PostPosted: Wed Feb 16, 2011 6:02 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 6695
Location: Northampton
Has thanked: 180 times
Been thanked: 621 times
Scruff it's a combi boiler at 3 bar what sorta system do you think it might be :roll: :lol:

Haven't fitted a Logic although I haven't heard terrible things about them it'll be a long time before hey put their reputation behind them.

Has it got a built in filling loop or an external one? I'd expect to find the filling loop passing water into the system somewhere.

The only way I would expext air to get in their would be from corrosion was the system flushed?

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html



For this message the author Razor has received gratitude : microgreen
Top
 Profile  
 
PostPosted: Wed Feb 16, 2011 6:09 pm 
Offline
Senior Member
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 45947
Has thanked: 254 times
Been thanked: 2931 times
Razor wrote:
Scruff it's a combi boiler at 3 bar what sorta system do you think it might be :roll: :lol:

Haven't fitted a Logic although I haven't heard terrible things about them it'll be a long time before hey put their reputation behind them.

Has it got a built in filling loop or an external one? I'd expect to find the filling loop passing water into the system somewhere.

The only way I would expect air to get in their would be from corrosion was the system flushed?


A tall building :lol:

I was thinking about the air, more than the boiler.

Don't sound to good.


Top
 Profile  
 
PostPosted: Wed Feb 16, 2011 8:36 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 4758
Has thanked: 146 times
Been thanked: 406 times
Make sure the filling loop is shut both ends, or remove it, but i think it is built in on these.

Stupid question, but did the installer remove any old filling loop that may have been fitted, as this could be letting by.

If that is ok, all I can think of is the plate HE has a pin hole in it.

I quite liked the look of these at the Ideal product/go kart evening a while back.

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : microgreen
Top
 Profile  
 
PostPosted: Thu Feb 17, 2011 3:54 am 
Offline
Gas/Heating Expert

Joined: Tue Dec 18, 2007 1:20 am
Posts: 2845
Location: London/Midlands
Has thanked: 25 times
Been thanked: 253 times
You never told me about any go-cart evening, Dave.

I went to Spain a long while ago with my wife on a package and we surprised the tour because we both won the go-cart competition.

[ When I say we both won, of course I mean that I won and she came second, the rest came behind us ]

There is a very simple reason why we won and thats because I sussed out a simple fact whilst watching and told her about it.

Tony



For this message the author Agile has received gratitude : microgreen
Top
 Profile  
 
PostPosted: Thu Feb 17, 2011 3:55 am 
Offline
Gas/Heating Expert

Joined: Tue Dec 18, 2007 1:20 am
Posts: 2845
Location: London/Midlands
Has thanked: 25 times
Been thanked: 253 times
Razor wrote:

Scruff it's a combi boiler at 3 bar what sorta system do you think it might be :roll: :lol:



I was just about to say an open vent in a nine story building but Scruff told you first!


Top
 Profile  
 
PostPosted: Fri Feb 18, 2011 7:22 pm 
Offline
Newly registered Member

Joined: Wed Feb 16, 2011 5:07 pm
Posts: 3
Has thanked: 4 times
Been thanked: 0 times
Razor/thescruff/gas4you/Agile

Yes it does have a filling loop built in - I've removed it and fitted the screw-on caps back ,still the pressure increases :scratch:
I don't know if the system was flushed or not.
Prior to the boiler being changed I didn't need to vent the rads very often.
One other thing I forgot to mention is that when DHW is called for there is water dribbling from the flue,I know it's cold but this happens when the heating has been running,I would have thought that the flue would be warm enough for steam not to condense??

The man from Ideal is coming on Monday,maybe he will sort it.

I'll report back his findings if it's of interest to you

Thanks
Tony


Top
 Profile  
 
PostPosted: Fri Feb 18, 2011 7:45 pm 
Offline
Senior Member
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 45947
Has thanked: 254 times
Been thanked: 2931 times
Is the pressure rising when the boiler is off.

Always interested in the end results.


Top
 Profile  
 
PostPosted: Fri Feb 18, 2011 8:22 pm 
Offline
Gas/Heating Expert

Joined: Tue Dec 18, 2007 1:20 am
Posts: 2845
Location: London/Midlands
Has thanked: 25 times
Been thanked: 253 times
The flue outside should be horizontal or just sloping slightly back to the boiler.

Which way does yours slope?

Did the installer complete the Benchmark?

Tony


Top
 Profile  
 
PostPosted: Fri Feb 18, 2011 11:10 pm 
Offline
Newly registered Member

Joined: Wed Feb 16, 2011 5:07 pm
Posts: 3
Has thanked: 4 times
Been thanked: 0 times
thescruff and Agile

Yes the pressure rises when the boiler is off.I don't know if the flue is horizontal or sloping back slightly,it looks horizontal, and yes the installer completed the Benchmark

Can't thank you enough for your prompt replies,much appreciated

Tony
ps thescruff
If you mean by OAP your retired - me too!


Top
 Profile  
 
PostPosted: Fri Feb 18, 2011 11:13 pm 
Offline
Senior Member
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 45947
Has thanked: 254 times
Been thanked: 2931 times
Don't feel like retired, I do more work now for nothing than I did for wages when I was working :roll:

Sounds like you have a leak between the hws and htg. if the filler is disconnected.


Top
 Profile  
 
PostPosted: Sat Feb 19, 2011 12:53 am 
Offline
Gas/Heating Expert

Joined: Tue Dec 18, 2007 1:20 am
Posts: 2845
Location: London/Midlands
Has thanked: 25 times
Been thanked: 253 times
There is a mains water isolating valve under the boiler. Turn ON a hot tap and leave it open. It should stop dripping after a few minutes.

Reduce the system pressure with a rad bleed screw down to 1.0 Bar when the heating system.

Leave it off for a few hours and then turn off the heating until it cools.

If there is no rise then it would seem to be a leak inside the boiler.

Tony


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 13 posts ] 



Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 



phpBB SEO