I'm installing some downlights, and whilst drilling the hole I have come very close to a beam.

I am thinking about cutting into the beam slightly to allow for the light, however this will touch the beam when in place, is this acceptable or would it pose a fire risk?

How close can the down light come to the beam? Can it touch?

I am installing fire rated downlights, therefore they have the protective metal sleeving around them.

Attachment:
IMG_1063.JPG
IMG_1063.JPG [ 20.76 KiB | Viewed 767 times ]


Top
 Profile  
 
PostPosted: Thu Dec 22, 2011 1:53 am 
Online
Pro Sparky
User avatar

Joined: Sat Mar 24, 2007 12:24 pm
Posts: 6032
Location: Spondon, Derby
Has thanked: 85 times
Been thanked: 193 times
sorry, that's a definite no no. if i ended up at the side of the beam i wouldn't like it but to cut into it to allow the fitting to fit..definitely not.

the fireproof fitting still gets hot, it's only a time barrier to fire, it doesn't stop heat transfer. apart from which, cutting the beam weakens its integrity.

to give you an idea of how hot halogens are... back when i used to smoke, i actually lit my cigarettes off halogen lamps.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Dec 22, 2011 2:36 pm 
Offline
Newly registered Member

Joined: Wed Feb 09, 2011 11:09 pm
Posts: 26
Has thanked: 4 times
Been thanked: 0 times
What's the recommnded minimum distance the light should be away from a beam?


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Dec 22, 2011 2:57 pm 
Online
Senior Member
User avatar

Joined: Wed May 05, 2010 2:33 pm
Posts: 1913
Location: Oxfordshire
Has thanked: 160 times
Been thanked: 81 times
I am not an electrician but is there not anything on the box/instructions?

_________________
Nick

If UHM's helped then please check out UHM's Nominated charity - http://www.donnasdreamhouse.co.uk/


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Dec 22, 2011 4:50 pm 
Offline
Newly registered Member

Joined: Wed Feb 09, 2011 11:09 pm
Posts: 26
Has thanked: 4 times
Been thanked: 0 times
Just says avoid beams, cables, pipes etc. Nothing about how far they should be from a beam.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Dec 22, 2011 4:52 pm 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 7475
Location: hants/dorset border
Has thanked: 166 times
Been thanked: 612 times
It should say 50 or 100mm away from any insulation/combustible material from memory, I would opt for 100mm to be on the safe side...

_________________
.

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


__________________________________
__________________________________

Verwood Handyman
I Know it says I'm On-line, but I might have just left myself logged in, whilst I'm out....


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Dec 25, 2011 8:23 am 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 427
Location: North Wales
Has thanked: 6 times
Been thanked: 96 times
422.3.1 Except for equipment for which an appropriate product standard specifies requirements, a luminaire shall be kept at an adequate distance from Combustible materials. Unless otherwise recommended by the manufacturer, a small spotlight or projector shall be installed at the following minimum distance from combustible materials:
(i) Rating up to 100 W 0.5 m
(ii) Over 100 and up to 300 W 0.8 m
(iii) Over 300 and up to 500 W 1.0 m
NOTE: A luminaire with a lamp that could eject flammable materials in case of failure should be constructed with a safety protective shield for the lamp in accordance with the manufacturer's instructions.

422.4.2 Except for equipment for which an appropriate product standard Specifics requirements, a luminaire shall be kept at an adequate distance from combustible materials. Unless otherwise recommended by the manufacturer, a small spotlight or projector shall be installed at the following minimum distance from combustible materials:
(i) Rating up to 100 W 0.5 m
(ii) Over 100 and up to 300 W 0.8 m
(iii) Over 300 and up to 500 W 1.0 m
NOTE 1: A luminaire with a lamp that could eject Flammable materials in case of failure should be constructed with a Safety protective shield for the lamp in accordance with the manufacturer's instructions.
NOTE 2: Luminaires marked (F in an inverted triangle) accordance with BS EN 60598-1 are suitable for mounting on a normally flammable surface.

So important there are two regulations saying the same thing.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Dec 25, 2011 8:36 am 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 7475
Location: hants/dorset border
Has thanked: 166 times
Been thanked: 612 times
:scratch: Surely that refers to the distance between the lamp and the surface it would be illuminating??

Otherwise all of those ceiling downlights would be outlawed by the reg, as the ceiling joists run at 400mm apart..??

_________________
.

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


__________________________________
__________________________________

Verwood Handyman
I Know it says I'm On-line, but I might have just left myself logged in, whilst I'm out....


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Dec 25, 2011 11:24 am 
Online
Pro Carpenter
User avatar

Joined: Sat Dec 16, 2006 10:11 pm
Posts: 10509
Location: redhill surrey an auld reekie laddie
Has thanked: 134 times
Been thanked: 468 times
PLEASE never ever remove any material from the bottom or side off any joist or rafter
you are allowed to remove 1/8th from the top and up to 25% by drilling holes horizontally through the center in some restricted areas but NEVER EVER underneath unless you are qualified and able to strengthen the timber appropriately

_________________
we are all ------------------still learning


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Dec 25, 2011 9:18 pm 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 427
Location: North Wales
Has thanked: 6 times
Been thanked: 96 times
wine~o wrote:
:scratch: Surely that refers to the distance between the lamp and the surface it would be illuminating??

Otherwise all of those ceiling downlights would be outlawed by the reg, as the ceiling joists run at 400mm apart..??

In real terms lamps may be able to be mounted closer. But it comes down to "recommended by the manufacturer" and unless the manufacturer says it can be closer then the rule applies. Some lamps Dichroic for example can let as much or more heat to back of lamp as front.

On many a building site quartz halogen lamps have been banned due to the number of fires they cause.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 10 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 6 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum