PostPosted: Thu Nov 24, 2011 3:42 pm 
Offline
Newly registered Member

Joined: Tue Oct 20, 2009 8:27 pm
Posts: 15
Has thanked: 2 times
Been thanked: 0 times
Hi,

I'm about to install a heatmiser system with two zones. I've done the plumbing and set up two zones (upstairs & downstairs) using the above motorised valve, as per Heatmiser's recomendation.

I've drawn up a wiring diagram for my exact setup and sent it to Heatmiser for their review.

I understood the MV to require LNE connections and two auxillary connections (hence the 5 core cable). I believed the MV needed a continuous supply, and the aux connections were used to signal the valve to open or close. Heatmiser have said that I don't need the auxillary connections as the UH1 takes care of it from the boiler enable.

The V4035H is normally closed, so does that mean that a voltage will open the valve, meaning a constant voltage to keep the valve open?

If this is the case, what do the auxillary connections do?

My diagram is below. The connections in question are 1.1, 1.3, 2.1 & 2.3.

Image

Many thanks

W.


Attachments:
File comment: Heatmiser Wiring Schematic.
HeatMiserSystemDetailed.pdf [18.79 KiB]
Downloaded 28 times
Top
 Profile  
 
PostPosted: Thu Nov 24, 2011 3:53 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Yes power on the brown will open the valve and the controller should do the rest.

Follow the sketch.

Is the yellow the orange.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 4:07 pm 
Offline
Newly registered Member

Joined: Tue Oct 20, 2009 8:27 pm
Posts: 15
Has thanked: 2 times
Been thanked: 0 times
Hi thescruff,

Superfast reply!

Do you mean that I should be showing the orange cable as yellow?

Thanks

W


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 4:08 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Just checked the boiler.

Remove the link between bk 1 and bk2.

then connect bk 2 to the greys and bk 1 to the oranges.

The brown in the MV's are switched by the control.

The theory.

The brown opens the valve, and the micro switch connects the grey and orange to fire the boiler.

No the orange shows yellow in the pic.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 5:28 pm 
Offline
Newly registered Member

Joined: Tue Oct 20, 2009 8:27 pm
Posts: 15
Has thanked: 2 times
Been thanked: 0 times
Hi again,

Finally get the yellow. Changed to a deeper shade of orange.

I now understand the theory. Thank you.

I hope I've understood your instructions correctly, as per the updated diagram?

Attachment:
File comment: Heatmiser wiring schematic for Baxi Duo-tec.
HeatMiserSystemDetailed.V.0.2.jpg
HeatMiserSystemDetailed.V.0.2.jpg [ 218.95 KiB | Viewed 746 times ]



I've also included the manufacturers wiring diagram. From what Baxi has shown, I can largly ignore the remote clock, frost stat and room stat as the Heatmiser system takes care of those three functions. They've just shown it for clarity.

Many thanks for your time and help.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 5:41 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Yes that looks better.

Just one thing park the oranges and greys in terminal connectors.

Do you have a pdf or link the UH1

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html



For this message the author thescruff has received gratitude : woter324
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 5:48 pm 
Offline
Newly registered Member

Joined: Tue Oct 20, 2009 8:27 pm
Posts: 15
Has thanked: 2 times
Been thanked: 0 times
The UH1 wiring diagram?
http://www.heatmiser.co.uk/web/index.php/docs/finish/62-uh1-wiring-diagrams/151-heatmiser-uh1-wiring-diagarm

Interestingly, the diagram shows two wires (grey & orange) labeled as going to the boiler enabler.

"Park the orange and greys in terminal connections"? From the MVs? Because the cable is 5 core, but I only use the LN&E. Will do. The MVs only come with a meter lenght so I have to use terminals anyway. I was going to use the round black / brown type.


Thanks again.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 5:56 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Yes you don't want them lying around if the have current.

Are heatmiser saying you don't need the greys and oranges that is show in their drawing :scratch:

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 6:06 pm 
Offline
Newly registered Member

Joined: Tue Oct 20, 2009 8:27 pm
Posts: 15
Has thanked: 2 times
Been thanked: 0 times
Absolutly!

Question to Heatmiser:
"I've put together a wiring diagram that I'd be very grateful if you could review and confirm if it is correct. It is connecting to a Baxi Duo-Tec Combi Boiler. I've used your wiring schematic and reading the wiring diagram (The wiring diagram is inset in my diagram above)., I understand the PRT-NTS acts as the Room Stat, External Clock and Frost Thermostat.

Specifically, can you confirm if the connections 1.3, 2.3 should go to the boiler enable IN and 1.2, 2.2 goes to boiler enable OUT."



Reply: As the boiler isn't our equipment I can not verify the connections to this. The rest of the diagram seems correct but you can loose the auxilary wires from you motorised valves as the boiler will fire from the boiler enable swith on the UH1.


Confused. Me too!


Last edited by woter324 on Thu Nov 24, 2011 6:11 pm, edited 1 time in total.

Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 6:10 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Yes that is saying you don't need them.

Stick them in a connector strip so they are safe.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 6:21 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Just one question.

bk1 in the boiler is out. and bk2 in the boiler is the switch live.

The UH1 is shown the other way round, can you confirm with HM which is the supply and which is the switch live.

Edit.

Just found a circuit diagram for the UH1, and it is correct as you show it.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 6:53 pm 
Offline
Newly registered Member

Joined: Tue Oct 20, 2009 8:27 pm
Posts: 15
Has thanked: 2 times
Been thanked: 0 times
I think it's me that's got it wrong. HM's UH1 diagram has a note "To boiler switched live" coming from the "Boiler Enable OUT" terminal.
Also, their diagram shows a connection between live and "Boiler Enable IN". I guess this can be wired to bk1 also. (bk1 is the perminant live?)

Corrected my diagram accordingly:

Attachment:
File comment: Heatmiser wiring schematic V.0.3
HeatMiserSystemDetailed.V.0.3.jpg
HeatMiserSystemDetailed.V.0.3.jpg [ 218.41 KiB | Viewed 726 times ]


Thanks again.


BTW I've found their stuff a little cheaper here:
http://www.inspiredheating.co.uk/acatalog/HEATMISER_TEMPERATURE_CONTROL_SYSTEMS.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 6:57 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
No, see my edit it was right before.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 7:02 pm 
Offline
Newly registered Member

Joined: Tue Oct 20, 2009 8:27 pm
Posts: 15
Has thanked: 2 times
Been thanked: 0 times
As you said, bk2 is the switched live. What about the note on the UH1 wiring diagram. "To boiler switched live"?

:dunno:


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Thu Nov 24, 2011 7:24 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
No see my edit and follow this drawing.


Attachments:
UH1-2.jpg
UH1-2.jpg [ 105.4 KiB | Viewed 720 times ]

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html

For this message the author thescruff has received gratitude : woter324
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 17 posts ]  Go to page 1, 2  Next


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: WHSales and 8 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling