Hi, I was wondering If there was a limit to how long a trailing socket cable can be?, as I cant find one long enough so wouold have to fit a new cable to one of the trailing sockets I have.

thanks in advance

Gordon


Top
 Profile  
 
PostPosted: Thu Jan 19, 2012 7:10 pm 
Offline
Senior Member
User avatar

Joined: Mon Mar 15, 2010 11:49 pm
Posts: 2315
Location: Oban
Has thanked: 62 times
Been thanked: 217 times
The limit depends on the cable being used. For a 'standard' 1.5mm c.s.a. cable you can use it for up to 3kW load at around 50m length. USe a 'thicker' cable (say 2.5mm c.s.a) and the length increases considerably.

Bear in mind that, to use the cable lengths at these ratings they CANNOT be coiled onto a drum during use as they act as 'heaters' and can melt the cable :shock:

_________________
This post may contain nuts


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Fri Jan 20, 2012 9:07 pm 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 427
Location: North Wales
Has thanked: 6 times
Been thanked: 96 times
What one has to ensure is if there is a short circuit the protective device will open. This includes both line to neutral and line to earth. The latter can be covered by using a RCD.

So what we look at is the loop impedance. A 13A fuse can have a loop impedance as high as 2.42 ohms and a 3A fuse would be 16.4 ohms. Since the socket (assuming normal ring main) is allowed 1.44 ohms for a 13A extension lead you can have 0.98 ohms so round figures 1 ohm.

1.5mm cable is around 0.029 ohms per meter so simple maths 33.7 meters maximum. With 2.5mm at 0.018 ohms per meter this goes to 54.4 meters. In real terms one would not want to go to limit as also there would be a volt drop problem.

Using smaller fuses one could go longer but the problem is to ensure it is never replaced for a bigger one so the fuse size needs to be well marked. Also of course where radial supplies are used the the socket supplied from a 16A MCB could be rated 2.875 ohms take that from the 13A fuse of 2.42 and you end up with a minus figure. Hence why so many are against Part P which is making people use extension leads rather than a proper extension.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 3 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling