PostPosted: Mon Jan 23, 2012 2:46 pm 
Offline
Newly registered Member

Joined: Mon Jan 23, 2012 2:20 pm
Posts: 5
Has thanked: 0 times
Been thanked: 0 times
About a Week ago i noticed that two of my downstairs radiators were barely warm on the top and cold on the bottom. I tried bleeding them, but nothing. Tried turning off the other downstairs rad, but this didnt work. It has steadilly got worse. Have now drained down the whole system and and flushed out one radiator downstairs and replaced the pump. I now have a hot radiator in the bathroom,(this is the first rad in the run, and warmth in two of the bedroom radiators. My system is being fed by a glow worm back boiler inset BBU 40 on a one pipe system. Archaic i know, but until a week ago it was working fine. Hope this is enough information for you. If not please ask. Any suggestions would be great! Many thanks.


Top
 Profile  
 
PostPosted: Mon Jan 23, 2012 3:04 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Going to need a lot of information.

What radiator valves do you have for a start.

Has any work been done prior to the problem.

Wont be in much today but will pick up as and when.

Taking the rads outside and flushing them would be a good start.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 23, 2012 3:06 pm 
Offline
Senior Member

Joined: Thu Jul 07, 2011 11:42 am
Posts: 773
Location: london
Has thanked: 57 times
Been thanked: 99 times
When you flushed out the one radiator was the much rubbish/black water,if so why did you just flush the one ?
You say bathroom rad hot and bedroom warm are down stairs now cold cold ?

_________________
If you have found help on the UHM's forums,why not help out the UHM's Nominated Charity,find out more here

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 23, 2012 3:10 pm 
Offline
Senior Member
User avatar

Joined: Wed Mar 23, 2011 6:54 pm
Posts: 388
Location: South London & Surrey
Has thanked: 4 times
Been thanked: 39 times
As Scruff says. Also have you noticed any kettling or banging noises coming from the boiler?
When was the boiler last serviced.?
Has the temperature setting on the boiler been altered?

_________________
Your problem is now our problem


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 23, 2012 3:31 pm 
Offline
Newly registered Member

Joined: Mon Jan 23, 2012 2:20 pm
Posts: 5
Has thanked: 0 times
Been thanked: 0 times
Normal valves fitted to all but one radiator. A thermostatic valve on one bedroom rad. Had no problems with the boiler prior to this and no noise or banging. The one radiator was flushed because at the time it was the last one in the run that had any heat so thought there mat have been a blockage, and need to change a leaking valve on it. Yes there was really black water coming out of it. The boiler temperature seems to make no difference, tryed it high low and in the middle. The three downstairs rad are stone cold. Thanks for the replies so far.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 23, 2012 3:35 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
You need to flush all the rads out then the loops with the rads off, two hose pipes, one on a draincock and the other mains water is the easiest way

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 23, 2012 8:18 pm 
Offline
Senior Member
User avatar

Joined: Wed Mar 23, 2011 6:54 pm
Posts: 388
Location: South London & Surrey
Has thanked: 4 times
Been thanked: 39 times
When you flush the rads give them a bang with the back of an old shoe - helps shift the s**t. :thumbright:

_________________
Your problem is now our problem


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 23, 2012 8:53 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 30, 2011 11:58 pm
Posts: 398
Has thanked: 9 times
Been thanked: 62 times
Toffee27 wrote:
About a Week ago i noticed that two of my downstairs radiators were barely warm on the top and cold on the bottom. I tried bleeding them, but nothing. Tried turning off the other downstairs rad, but this didnt work. It has steadilly got worse. Have now drained down the whole system and and flushed out one radiator downstairs and replaced the pump. I now have a hot radiator in the bathroom,(this is the first rad in the run, and warmth in two of the bedroom radiators. My system is being fed by a glow worm back boiler inset BBU 40 on a one pipe system. Archaic i know, but until a week ago it was working fine. Hope this is enough information for you. If not please ask. Any suggestions would be great! Many thanks.


Toffee27 wrote:
Normal valves fitted to all but one radiator. A thermostatic valve on one bedroom rad. Had no problems with the boiler prior to this and no noise or banging. The one radiator was flushed because at the time it was the last one in the run that had any heat so thought there mat have been a blockage, and need to change a leaking valve on it. Yes there was really black water coming out of it. The boiler temperature seems to make no difference, tryed it high low and in the middle. The three downstairs rad are stone cold. Thanks for the replies so far.


one pipe and TRV i would check to see if its stuck



For this message the author LordCross has received gratitude : Demon
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Tue Jan 24, 2012 3:44 pm 
Offline
Newly registered Member

Joined: Mon Jan 23, 2012 2:20 pm
Posts: 5
Has thanked: 0 times
Been thanked: 0 times
Still no luck! Took off all the radiators today and flushed them all out, and all the pipe work. I am now left with a lovely hot bathroom rad (the first one on the run) and that is it. The chill has been taken off the second one. The rest are completely cold. :dunno: Any more suggestions would be great. Many thanks again.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Tue Jan 24, 2012 4:01 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Ok have you shut that one down on the lockshield valve.

Is the loops getting hot.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Tue Jan 24, 2012 5:41 pm 
Offline
Newly registered Member

Joined: Mon Jan 23, 2012 2:20 pm
Posts: 5
Has thanked: 0 times
Been thanked: 0 times
Have shut the lockshield to the first one. Most of the heat has now gone, but there is still not that much heat in the second rad. The pipes are hot coming out from the pump, after that they are under the floorboards. The pipes that are visible from the second one on are cold.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Tue Jan 24, 2012 6:01 pm 
Offline
Senior Member
User avatar

Joined: Wed Mar 23, 2011 6:54 pm
Posts: 388
Location: South London & Surrey
Has thanked: 4 times
Been thanked: 39 times
Take the head off the TRV first to see if that makes a difference.

_________________
Your problem is now our problem


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Tue Jan 24, 2012 9:47 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
if the loop isn't getting cold then there's a circulation fault.

Has any valves been closed (not the rads)

Check the pump is turning.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 30, 2012 1:05 pm 
Offline
Newly registered Member

Joined: Mon Jan 23, 2012 2:20 pm
Posts: 5
Has thanked: 0 times
Been thanked: 0 times
There definately was a circulation problem. Over the weekend we managed to connect up a couple of hose and back flush the system along different points of the system. Was quite surprising how much was rattling about in there. I am now glad to say that i have a fully working heating system. I would like to take this opportunity to thankyou all for the advise given. Many thanks again.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Mon Jan 30, 2012 6:34 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 30, 2011 11:58 pm
Posts: 398
Has thanked: 9 times
Been thanked: 62 times
well done chap!!!


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 15 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 3 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum