Hi all

We're in the process of modernising mother-in-law's house.

The house has recently got its first ever gas connection and now has full central heating supplied by a Baxi Duo-Tec 33 combi boiler..

The heating thermostat is a Hive 2.

What I can't get my head around (we don't have a combi at our own house) is the purpose of the central heating temperature dial on the boiler - I understand what the hot water temperature dial is for. If you're using a thermostat (Hive or any type), wouldn't you just set this dial all the way to maximum (80) so the house heats up quicker and then the house thermostat will switch the heating off?

What I also notice happening is that when the heating is on, the boiler is constantly firing to maintain the temperature set by that dial. So, you set it to 60, it gets up to 60 and cuts out, the display then drops to 59 and it fires up again. Is this what you would expect to happen?

As I said - new to combis - we have a system boiler- so apologies if I'm missing something obvious.

Cheers.

Ian


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Sat Nov 04, 2017 7:00 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6304
Has thanked: 723 times
Been thanked: 762 times
Your system boiler has a temperature control as well.

With the duotec if you can, run the temperature around 60-65c.

Yes, if you set it to 80 the rads get hotter and heat the room quicker, but the boiler will hardly be in condensing mode, which is how a modern boiler achieves its extra efficiency.

Although dew point is technically a variable, in heating systems a figure of 56c is generally quoted, the return water temperature needs to be below this to maximise condensing mode.

To achieve this, new complete heating systems will have slightly larger radiators so a lower flow temperature will heat the rooms up just as quick due to the larger heat emitting surface.

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Sat Nov 04, 2017 7:04 pm 
Offline
Newly registered Member

Joined: Sat Oct 14, 2017 6:44 pm
Posts: 10
Has thanked: 0 times
Been thanked: 1 times
Thanks for your quick reply Dave - I appreciate it.

So the constant firing on and off should be expected?

Ian


Top
 Profile  
Reply with quote  
PostPosted: Sat Nov 04, 2017 7:11 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6304
Has thanked: 723 times
Been thanked: 762 times
The boiler will cycle on and off regularly, just to keep itself up to the set temperature, but this should stop when the room thermostat turns off.

However, most modern boilers have an anti cycling software built in that often limits this to around every 3 minutes.

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Sat Nov 04, 2017 7:47 pm 
Offline
Newly registered Member

Joined: Sat Oct 14, 2017 6:44 pm
Posts: 10
Has thanked: 0 times
Been thanked: 1 times
Thanks again Dave. Yes it does stop firing when stat is up to temperature. But when it is on it can be switching on and off every 30 seconds. I'll run it by the installer next week.


Top
 Profile  
Reply with quote  
PostPosted: Sun Nov 05, 2017 2:10 pm 
Online
Senior Member

Joined: Tue Oct 02, 2007 11:45 am
Posts: 1247
Has thanked: 24 times
Been thanked: 130 times
up_north wrote:
... when it is on it can be switching on and off every 30 seconds. ...

It does that because it cannot modulate low enough to produce the heat required.

Your boiler will modulate between 9kW and 29kW. You may not need more than 15kW to heat your house when it is very cold (-3C) - unless it is very large and old without decent insulation. In the current relatively mild weather (10C), you may only require about 7-8kW to heat the house. But your boiler cannot modulate this low so it has to turn on and off to maintain the required water temperature.

This is one of the disadvantages of a combi boiler. It has to be powerful enough to heat cold water instantly from 10C to 50C or 60C, which means that it is normally over powered for heating the house.



For this message the author D Hailsham has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Sun Nov 05, 2017 3:26 pm 
Offline
Newly registered Member

Joined: Sat Oct 14, 2017 6:44 pm
Posts: 10
Has thanked: 0 times
Been thanked: 1 times
Thanks - that's genuinely interesting. But the manual states this:
-----
2. Once main burner ignites the fan speed controls the gas rate to maintain the heating temperature measured by the temperature sensor.
3. When the flow temperature exceeds the setting temperature, a 3 minute delay occurs before the burner relights automatically (anti-cycling). The pump continues to run during this period.
-----
So doesn't this mean it shouldn't fire more often than every three minutes?

I understand that when a combi ignites it can release a bit of gas but becuase ours is igniting so frequently there's a really strong smell of gas near the flu.

Is there anything I can do with the other controls - thermostat, TRVs etc to 'help' the boiler?

Thanks again.

Ian


Top
 Profile  
Reply with quote  
PostPosted: Sun Nov 05, 2017 4:12 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6304
Has thanked: 723 times
Been thanked: 762 times
In theory the boiler should start the spark fractionally before opening the gas valve.

The 3 minute anti cycle will be broken if a hot tap is used during the process.

Ignition electrodes were a problem on these, but I thought they had sorted this for the new ones, so get your engineer to check them out.

The 33Kw is very powerful for an average house, but combi's are usually sized for HW use.

These boilers do not have the facility to range rate the heating side as far as I am aware, so are relying on the built in software to keep the burner modulated down. Your boiler should be able to modulate down to around 10-11Kw, but if several of the thermostatic valves have closed, this will still be way too high.

I would suggest you experiment with different settings of the main room thermostat to 'learn' what is a good setting so all the rooms are a comfortable temperature when the main stat turns off.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
PostPosted: Sun Nov 05, 2017 11:03 pm 
Offline
Newly registered Member

Joined: Sat Oct 14, 2017 6:44 pm
Posts: 10
Has thanked: 0 times
Been thanked: 1 times
Thanks Dave. Unfortunately no hot tap was in use.

I vidoed it - unfortunately it looks like I can't embed it but the url is:
https://youtu.be/y8eo6o69llA

Dial on boiler was set to 60. Room stat set to 23 - had reached 19 when I filmed this. All TRVs fully open. All rads except towel rail have a TRV. Heating had been on for approx 45 minutes.

Ian



For this message the author up_north has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 8:00 am 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6304
Has thanked: 723 times
Been thanked: 762 times
I have to admit I've never seen one doing that before.

From here I wouldn't have a clue why its doing it that often.

Hopefully your installer can shed some light on it, being there, or possibly put a call in to Baxi.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 5:25 pm 
Offline
BANNED

Joined: Wed Jun 14, 2017 8:38 am
Posts: 204
Has thanked: 696 times
Been thanked: 28 times
You should not smell any gas is your installer gas safe registered did he issue certificate and tests you can upload certificate and place paper over personal details

Sent from my LG-K100 using Tapatalk


Top
 Profile  
Reply with quote  
PostPosted: Thu Nov 09, 2017 5:12 pm 
Offline
Newly registered Member

Joined: Sat Oct 14, 2017 6:44 pm
Posts: 10
Has thanked: 0 times
Been thanked: 1 times
Multiman - sorry - thought I'd reolied to this. Yes definitley Gas Safe registered.

A bit of an update on this. As I said when the installer came round it worked perfectly. I later noticed something and I can now replicate it. Switch heating on and let boiler come up to temp - then run a hot water tap for at least 30 secods. It seems that running hot water then triggers the constant firing cycle until the heat call is stopped which we do quite quickly because of the fumes from the flu.

Ian


Top
 Profile  
Reply with quote  
PostPosted: Thu Nov 09, 2017 5:17 pm 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 22411
Location: hants/dorset border
Has thanked: 1337 times
Been thanked: 3402 times
Call Baxi as dave (gas4you) suggests. in the meantime spend £20 or so on a carbon monoxide alarm.

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


Top
 Profile  
Reply with quote  
PostPosted: Thu Nov 09, 2017 5:44 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6304
Has thanked: 723 times
Been thanked: 762 times
Something definitely needs professional attention.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 14 posts ] 


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO