Hi
I hope you can advise.
I have a Grant Vortex 21e Oil Fired combi boiler approx 4yrs old.

I have a pressure loss, the pressure in the boiler keeps dropping off too zero, very regularly.
I re-pressure the boiler to over 1 bar, sometimes up too 2 bar.
Turn off water inlet valves, boiler works fine for a while, but pressure soon starts too drop.

A ha I hear you say " you must have a leak", yep but doesn't seem to be a interior pipe or radiator as all seems dry, where it can be viewed, no wet patches etc.

BUT!, there is a pipe that comes out the back of the boiler, exits thru' the exterior wall, and this is dripping water sometimes slowly, sometimes a little quicker!

Does anyone know what this is? is it supposed to do this?

I live in a hard water area, but have had filter fitted to help, not replaced recently :oops:

Any help advice would be much appreciated.

I know i need a "proper" plumber, but would like too know the problem to explain, and what is needed for a repair, roughly!!

Thanks, hope for some excellent replies! :cheers:


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+

For this message the author vortex21 has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 12:13 pm 
Offline
Senior Member

Joined: Fri Jan 20, 2006 5:51 pm
Posts: 7317
Location: Essex
Has thanked: 432 times
Been thanked: 1472 times
Not an expert but this sounds like a pressure release valve letting by. The PRV prevents the pressure in the boiler getting above the dangerous level. If they are triggered at some point then crud can get into the valve seat and it will drip by dropping pressure. It might need replacing. The other issue is the expansion vessel needs pressurising maybe.

DWD

_________________
Painting with BIN



For this message the author dewaltdisney has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 1:12 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6307
Has thanked: 724 times
Been thanked: 763 times
:withstupid:


Remove dust cap from expansion vessel schrader valve and press. If water comes out the vessel has had it.

If just air or flat, isolate boiler, drain boiler, leave drain open whilst repressurising expansion vessel with air to approximately 1 bar.

Close drain, open isolation valves and fill system.

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : multiman
Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO