Hi All

For info I have a Baxi Solo2 60 PF that heats my hot water and radiators.

Connected to this i also have a Heatrae Sadia Mega Flow and some sort of pressurised unit with Zilmet printed on it.

As you may guess I know nothing about plumbing/heating systems.

I have had a continual problem with the boiler stopping working. The boiler would not ignite. i have a contract with a company who came out and on several occasions replaced a PCB. This apepared to fix the problem for a short period of time but the problem (or similar problem) keeps ocurring.

Last week i had them out again. the rads whee bled and the 'pressure' increased in the system. Apparently the system was over heating due to poor flow.

For the past week the boiler has worked fine with both water and rads being heated.

Now the water is not being heated but I hasten to add that the boiler is firing to heat the central heating and is hot !

So, what is up with my hot water (or lack of it) ? Has the pressure dropped again? How do i tell? What should the pressure be and how do I set it? I also 'assume' that if my pressure in the system has again dropped in a week then I may have a leak?

Any advice and or suggestions as to where i may get hold of a baxi Solo 2 60 pf instruction manual would be fantastic.

Cheers

Steve


Top
 Profile  
 
 Post subject:
PostPosted: Sun Oct 04, 2009 11:21 am 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
A pic or two around the cylinder, showing the 3port valve etc would help.

Is there an air vent on the cylinder primary flow.


Attachments:
BAXI SOLO 2 60PF GCNo.41-077-74.pdf [1.7 MiB]
Downloaded 74 times

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: 3 port valve and vent
PostPosted: Sun Oct 04, 2009 11:50 am 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
Thanks for the response,

I can take some pics but not sure what I am taking pics of !

If you can give me a hint as to what sort of thing I should be looking for that would be good. Otherwise I'll just take some general pics

cheers

Steve


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: draining megaflow system
PostPosted: Sun Oct 04, 2009 12:00 pm 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
I also seem to remember reading (somewhere) that it may be an idea to drain the magaflow system - something to do with removing airlocks. Any thoughts?


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Oct 04, 2009 1:18 pm 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
Here are some general pics of my system....


Attachments:
File comment: no idea what this is (except for the immersion) !
IMG_0158.JPG
IMG_0158.JPG [ 146.35 KiB | Viewed 853 times ]
File comment: pipe work arround the Megaflow
IMG_0154.JPG
IMG_0154.JPG [ 131.85 KiB | Viewed 853 times ]
File comment: general pic of pump and pressure unit.
note both needles at approx 1bar.

IMG_0165.JPG
IMG_0165.JPG [ 180.97 KiB | Viewed 853 times ]
File comment: general picture of megaflow
IMG_0153.JPG
IMG_0153.JPG [ 130.91 KiB | Viewed 853 times ]
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 1:28 pm 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
if you need more pics just let me know


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 1:50 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 3577
Has thanked: 51 times
Been thanked: 230 times
Pic 0158. That is the 2 port HW zone valve.

I would suspect that either the motor has had it and it is not opening, or the microswitch has gone in the head so not firing the boiler.

If you turn on the ch, does the pipe work to the cylinder get hot? If so it will be the microswitch.

If it doesn't it will be the motor.

The motor can usually be changed but I always replacr the complete head as long as there is a metal 'spot' on the top of the valve cover at one end.

Sorry about the confusing post, but just got in from work and am totally knackered :roll:

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 2:09 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
The valve should be ok as it is connected through the thermal cut-out and nothing will work, or it should be.

In pic 158 is an air vent to the left of the stopcock, turn the pump off and let any air out, I reckon that will do it.

In pic 165 is a red valve, can you tell me if it is nearly closed as it looks like a by-pass valve, a pic showing what it's connected too would be good.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 2:11 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Don't touch the megaflow, unless it passing water through one of the safety valves.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 2:23 pm 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
thescruff wrote:
The valve should be ok as it is connected through the thermal cut-out and nothing will work, or it should be.

In pic 158 is an air vent to the left of the stopcock, turn the pump off and let any air out, I reckon that will do it.

In pic 165 is a red valve, can you tell me if it is nearly closed as it looks like a by-pass valve, a pic showing what it's connected too would be good.


Hi Apologies.
Can you confirm that you did mean pic 158?
Also, apologies for requesting details but I REALLY have no idea what I'm doing but happy to try out your ideas as long as I'm sure of what you are suggesting.

Can you suggest how i should turn the pump off? My initial reaction would be to turn off my boiler which in turn would turn the pump off.

Also, how do I let the air out as you suggest?

I'll post a pic of the connections you ask for asap.

Cheers

Steve


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject: red Valve
PostPosted: Sun Oct 04, 2009 2:37 pm 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
ok, the valve in pic 165 with the red screw handle to turn it on and off is fully open.

I have added some more pics for detail....


Attachments:
IMG_0167.JPG
IMG_0167.JPG [ 154.04 KiB | Viewed 816 times ]
IMG_0168.JPG
IMG_0168.JPG [ 178.53 KiB | Viewed 816 times ]
IMG_0166.JPG
IMG_0166.JPG [ 198.53 KiB | Viewed 816 times ]
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 3:19 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
Sorry the air vent is shown in Pic 154 and 153, a pipe sticking up in the air with a screw cap on the top

Can you turn that red valve off, and open it 11/2 turns.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 3:25 pm 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
ok, thanks

I have the air vent now !

I take it you mean 1 and a half turns? I'll do this now.

Cheers

Steve


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 3:51 pm 
Offline
OAP
User avatar

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39983
Has thanked: 187 times
Been thanked: 2113 times
the red valve wants to be open 11/2 turns.

The air vent you just open it to let the air out with the pump off.

_________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Oct 04, 2009 6:07 pm 
Offline
Newly registered Member

Joined: Sun Oct 04, 2009 10:45 am
Posts: 18
Location: Altrincham
Has thanked: 3 times
Been thanked: 0 times
ok,

Closed the red valve and then opened it 1.5 turns.

opened the air vent, air was released until water came out of it (like bleeding a radiator) then closed it back off.

noted that the pressure was now at about 0.5 bar.

Can you explain what the red valve does, is there a danger of it being either fully closed or fully open?

I have now put the hot water on ( I take it this would be the next step?)

Cheers

Steve


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 18 posts ]  Go to page 1, 2  Next


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling