I was preparing to paint a room in our house and went to loosen the screws on the two sockets there in order to keep them off the wall and not get paint on the sides when I noticed some green sticky oily substance on the wall on the edge underneath it. I took the socket screws out and pulled the socket out a bit for further inspection and saw that the contacts inside had a good bit of this green sludge on them. I then went to check the other socket but it was clean. The socket in question is working and has obviously been that way for a long time without a problem but I wondered where it comes from, what caused it and is it a worry and what should I do about it?. Thanks in advance for any replies.


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Mon Jul 17, 2017 2:11 pm 
Online
Senior Member

Joined: Sun Jan 31, 2010 9:21 pm
Posts: 1800
Location: Kent, Land of Apples and PYO
Has thanked: 35 times
Been thanked: 360 times
Is it the external wall ? is it damp ?, moisture and salts are the main cause of the "green crustys"


Top
 Profile  
Reply with quote  
PostPosted: Mon Jul 17, 2017 6:13 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 6328
Has thanked: 23 times
Been thanked: 1045 times
Its coming from the cables, it not common but its not unusual either.
Its the cables plasticiser, its used to make the cable sheath. It means that at some time your cable has got hot, and its now "leaking" The green stuff does not conduct electricity, but it does indicate the cable is breaking down. How long it will last for is any ones guess. The green stuff is not THAT bad for you, but don't eat it, or get it in your eyes, and do wash your hands.

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here



For this message the author someone-else has received thanks - 2: bluesjunior, OnlyMe
Top
 Profile  
Reply with quote  
PostPosted: Mon Jul 17, 2017 8:36 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2302
Location: South Yorkshire
Has thanked: 131 times
Been thanked: 472 times
someone-else wrote:
Its coming from the cables, it not common but its not unusual either.
Its the cables plasticiser, its used to make the cable sheath. It means that at some time your cable has got hot, and its now "leaking" The green stuff does not conduct electricity, but it does indicate the cable is breaking down. How long it will last for is any ones guess. The green stuff is not THAT bad for you, but don't eat it, or get it in your eyes, and do wash your hands.


I think that sums it up nicely.

It is the plasticiser that has reacted to an anti oxident that was used in some cables in the late 1960's. The only cure is a rewire, however if the symptoms are not too bad then the cable can be left in use and it is not considered by experts to be electrically unsafe. A Google of "green goo electrical cables" should find lot's of info on the subject.


Top
 Profile  
Reply with quote  
PostPosted: Tue Jul 18, 2017 10:47 pm 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 2364
Location: North Wales
Has thanked: 57 times
Been thanked: 494 times
This is what can happen however we don't have the temperatures the same as Australia so not quite as bad over here. I general the problems arise when the cable is flexed, so in a brick built house it does not flex much, where the timber frame buildings present something very different, both because they flex more and there is something to burn.


Top
 Profile  
Reply with quote  
PostPosted: Tue Jul 18, 2017 10:58 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 6328
Has thanked: 23 times
Been thanked: 1045 times
Sorry, I don't agree. That is regarding a problem of "Cheap cable" going brittle.
bluesjunior asked about green goo.

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 3 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO