woodbutcher-rob
|
Posted: Wed Jan 18, 2012 10:12 pm |
|
 |
| Newly registered Member |
Joined: Wed Jan 18, 2012 10:05 pm Posts: 7 Has thanked: 2 times Been thanked: 0 times
|
Hi, I'm new here so please be gentle with me,I have probs with my glow worm 30 sx boiler, I keep losing pressure with water dripping throu the tundish, my plumber today replaced the PRV but it's still leaking . any ideas please. 
|
|
| Top |
|
 |
|
thescruff
|
Posted: Wed Jan 18, 2012 10:40 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39982 Has thanked: 187 times Been thanked: 2113 times
|
|
What does the pressure rise to when the heating is turned on, say starting at 1.3bar cold.
The plumb er should have checked it and the expansion vessel.
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
woodbutcher-rob
|
Posted: Thu Jan 19, 2012 7:23 pm |
|
 |
| Newly registered Member |
Joined: Wed Jan 18, 2012 10:05 pm Posts: 7 Has thanked: 2 times Been thanked: 0 times
|
0.9 cold going up to about 1.3/1.4 when running. what pressure should the expansion vessel be set at?
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
moggridgeplumbing
|
Posted: Thu Jan 19, 2012 7:56 pm |
|
 |
| Senior Member |
 |
Joined: Wed Mar 23, 2011 6:54 pm Posts: 388 Location: South London & Surrey Has thanked: 4 times Been thanked: 39 times
|
1.4 bar wouldn't trigger the PRV!  Are you sure he replaced it?
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Thu Jan 19, 2012 7:57 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39982 Has thanked: 187 times Been thanked: 2113 times
|
|
Did the plumber actually change the pressure relief valve or just play with it, they seldom reseal once they are set off.
If it's a new one, then it's either duff or the pressure is rising to above 3 bar.
best to get the plumber back to have another look
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
woodbutcher-rob
|
Posted: Thu Jan 19, 2012 8:59 pm |
|
 |
| Newly registered Member |
Joined: Wed Jan 18, 2012 10:05 pm Posts: 7 Has thanked: 2 times Been thanked: 0 times
|
|
No he deffo change it, I never left his side, I actually think I've got other problems, got home tonight and towels under boiler( in airing cup'd) were wet so leak is in boiler? Also water passing throu' tundish is stone cold so is this coming from elsewhere, PRV's from mains supply, pressurised cyl and boiler are all connected to same tundish.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Thu Jan 19, 2012 9:27 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39982 Has thanked: 187 times Been thanked: 2113 times
|
|
Agreed some pics would be useful
Could it be the cylinder letting by, the make and model of that as well please.
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
woodbutcher-rob
|
Posted: Fri Jan 20, 2012 6:42 am |
|
 |
| Newly registered Member |
Joined: Wed Jan 18, 2012 10:05 pm Posts: 7 Has thanked: 2 times Been thanked: 0 times
|
|
Wierder and wierder, all seams OK this morning, we are away for weekend so will see sunday evening. Thanks for your help. P.s. cyl. is Telford tornado.
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Fri Jan 20, 2012 8:28 am |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39982 Has thanked: 187 times Been thanked: 2113 times
|
|
Right so the problem is most likely to be the cylinder.
It has an internal expansion vessel, follow the instructions to reinstate it or get a plumber with a G3 unvented qualification.
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
woodbutcher-rob
|
Posted: Sat Jan 28, 2012 5:37 pm |
|
 |
| Newly registered Member |
Joined: Wed Jan 18, 2012 10:05 pm Posts: 7 Has thanked: 2 times Been thanked: 0 times
|
|
Have ordered a new expansion vessel. old one will not hold pressure (tried pumping it up), also having a non-return valve fitted on hot out of cylinder. how much should I pay for vessel? telford exp19
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
thescruff
|
Posted: Sat Jan 28, 2012 5:44 pm |
|
 |
| OAP |
 |
Joined: Mon Mar 10, 2008 12:46 am Posts: 39982 Has thanked: 187 times Been thanked: 2113 times
|
|
Would sooner see a pic or two and there shouldn't be a non-return valve on the hot out.
Are you meaning the white vessel.
_________________ If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here : donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
Razor
|
Posted: Sat Jan 28, 2012 6:30 pm |
|
 |
| Senior Member |
 |
Joined: Wed Nov 14, 2007 10:21 pm Posts: 5140 Location: Northampton Has thanked: 76 times Been thanked: 372 times
|
|
Ive seen lots of nrvs fitted on the outlet of UVs where the cold supply isn't taken off the balanced feed from the valve. Then someone fits a cheap mixer and the pressure backfeeds to the cylinder.
_________________ As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference. donnas-dream-house-charity-t52110.html
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
|
woodbutcher-rob
|
Posted: Wed Feb 01, 2012 11:21 am |
|
 |
| Newly registered Member |
Joined: Wed Jan 18, 2012 10:05 pm Posts: 7 Has thanked: 2 times Been thanked: 0 times
|
New expansion vessel and check valve fitted today , so far so good ( insert fingerscrossedsmiley) Cant locate leak in boiler but seems to be coming from black plastic manifold only a very slight drip takes about 3days to drop enough to stop boiler working. Got a piccy to upload but dont know how to. 
|
|
| Top |
|
 |
You may not be able to see the full post including pictures unless you
register or
log in
You may not be able to see the full post including pictures unless you
register or
log in