Hinton Heating Gas/Heating Expert

Joined: 16 Jan 2006 Posts: 4296 Location: Bournemouth
|
Posted: Thu Mar 29, 2007 11:08 pm Post subject: Fused Spur |
|
|
|
I recently installed a cylinder & boiler. I asked the customer to get a spark in to supply 2 fused outlets in the airing cupboard.
He ran a cable from the old immersion spur, to the two new patress boxes, which he joined in series from the same cable, effectivily running two outlets from the one cable, I thought you could only have one outlet on each spur?
can a spark confirm this, or say what would be the correct way of supplying two fused oulets in an airing cupboard? _________________ www.hintonheating.com
 |
|
| Back to top |
|
 |
|
|
 |
ultimatehandyman Site Admin

Joined: 16 Jul 2005 Posts: 9740 Location: Darwen, Lancashire
|
Posted: Thu Mar 29, 2007 11:17 pm Post subject: |
|
|
|
I'm not a spark, so can't confirm it- But as long as the cable is the correct thickness then it is quite acceptable I believe  _________________ DIY | DIY Video |
|
| Back to top |
|
 |
sparkydude Approved Electrician

Joined: 13 Aug 2005 Posts: 942 Location: Staffordshire
|
Posted: Fri Mar 30, 2007 7:11 am Post subject: |
|
|
|
Morning Hinton, just got in from a night shift so checking in to see whats happening. Are you saying he has just used the circuit for the immersion to supply your two outlets? if so than as long as the immersion circuit is a radial, ie on its own feed from the fuse board , then it can feed as many outlets as you like. If however the immersion is a spur from the ring main already , then it cannot be used to supply two outlets, as the second would in effect be a spur from a spur which is not acceptable and contravenes the wiring regulations.
Off to beddy byes now i feel , 14 hour shift is enough for me.
Night Night
:grin: :grin:
Nick _________________ If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL |
|
| Back to top |
|
 |
Hinton Heating Gas/Heating Expert

Joined: 16 Jan 2006 Posts: 4296 Location: Bournemouth
|
Posted: Fri Mar 30, 2007 10:27 am Post subject: |
|
|
|
I think its a radial from diectly from the CU... I knew there was an issue with spuring a spur from a spur! _________________ www.hintonheating.com
 |
|