PostPosted: Sun Aug 01, 2010 11:42 am 
Offline
Newly registered Member
User avatar

Joined: Sat Jul 31, 2010 9:03 pm
Posts: 78
Location: Wigan, NW
Has thanked: 108 times
Been thanked: 1 times
Right, pictures below - your step-by-step instructions were great, thanks.

The original cable that was/is causing concern is situated on the opposite side of the house (it is only a small house, mind), on the inside of the external wall and comes out from under the coving around the ceiling - which I was desperately hoping to leave intact. It could lead up and under the floorboards into either of the two front bedrooms.

Question - is the earth circuit and old wiring around the meter/fuse box potentially unsafe? I will phone the electricity company and ask (demand/beg) that they come and sort out the earth circuit to/from the meter/fuse box tomorrow.


Attachments:
File comment: The glut of wires in the top centre/right of the fuse box.
Wires coming into the fuse box.jpg
Wires coming into the fuse box.jpg [ 60.95 KiB | Viewed 75 times ]
File comment: The cable coming from the top of the fuse box runs up the wall to the right along the diagonal. Note the old light fitting just sitting there...
Single cable coming out the top of the fuse box.jpg
Single cable coming out the top of the fuse box.jpg [ 68.45 KiB | Viewed 75 times ]
File comment: Inside the fuse box - much neater than I expected!
Inside fuse box 1.jpg
Inside fuse box 1.jpg [ 79.34 KiB | Viewed 75 times ]
Top
 Profile  
 
PostPosted: Sun Aug 01, 2010 12:04 pm 
Offline
Newly registered Member
User avatar

Joined: Sat Jul 31, 2010 9:03 pm
Posts: 78
Location: Wigan, NW
Has thanked: 108 times
Been thanked: 1 times
I have just phoned Norweb and spoke to a very helpful lady who is sending an engineer out today! Hopefully this will solve all the problems.

Many, many thanks for all your replies and help. I will update later once the engineer has been. :-)


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 12:42 pm 
Offline
Senior Member
User avatar

Joined: Sat Aug 13, 2005 8:11 pm
Posts: 2038
Location: Staffordshire
Has thanked: 2 times
Been thanked: 94 times
Good show old chap. Are you friendly with your neighbours as it wold be an idea to see where your cable comes from. Another thought has come to me, is the pipe the cables are in like a steel pipe , that would also show as shiny when scratched ??? Is there any kind of thread in the end of this pipe ?? or a brass end to it ?? I know we are asking a lot of questions but without being there we cannot advise further as to the safety of your house without knowing.

Nick

_________________
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL



For this message the author sparkydude has received gratitude : dinx67
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:02 pm 
Offline
Newly registered Member
User avatar

Joined: Sat Jul 31, 2010 9:03 pm
Posts: 78
Location: Wigan, NW
Has thanked: 108 times
Been thanked: 1 times
As far as I can make out it is a metal casing with 2 cables inside - one red and one black. There is no inner sheath between the metal casing and the internal cables. The cables inside the metal casing are coated with what looks like rubber - it is coloured either red or black on the outside and is a sort of grubby white on the inside. Each of the red and black casings contains 7 metal strands of silver-coloured wire.

This house was built in the late 1940s so I presumed it was lead casing, I believe that was in common usage back then? The rubbery type casing around each of the wires inside is quite soft, with an almost plastic feel to it, but in places it is hard, cracked and broken.

Sorry for the quality of the pictures, best I can do with a crappy camera phone!


Attachments:
More old cable.jpg
More old cable.jpg [ 62.29 KiB | Viewed 55 times ]
Old cable inner.jpg
Old cable inner.jpg [ 42.17 KiB | Viewed 55 times ]
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:04 pm 
Offline
OAP

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39135
Has thanked: 181 times
Been thanked: 1983 times
sparkydude wrote:
Good show old chap. Are you friendly with your neighbours as it wold be an idea to see where your cable comes from. Another thought has come to me, is the pipe the cables are in like a steel pipe , that would also show as shiny when scratched ??? Is there any kind of thread in the end of this pipe ?? or a brass end to it ?? I know we are asking a lot of questions but without being there we cannot advise further as to the safety of your house without knowing.

Nick


I haven't seen any tube/conduit in any of the pics :scratch:

Seen some old lead cable. :roll:

_________________
---------------------------------------------------------------------------------------------------

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html



For this message the author thescruff has received gratitude : dinx67
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:11 pm 
Offline
Newly registered Member
User avatar

Joined: Sat Jul 31, 2010 9:03 pm
Posts: 78
Location: Wigan, NW
Has thanked: 108 times
Been thanked: 1 times
Forgot to answer your other questions! And please feel free to ask whatever you need to know. :-)

The end of the cable we found in the living room was cut off about 1 metre above floor level so there was no 'end' on it, it was just the severed, slightly flattened, end of the cable. I cannot see any thread inside the cable. The other bit of similar cable is the one in the meter cupboard and there is no 'end' on that - it has just had the casing cut back so that the red and black wires could be used to attach onto those other plastic box bits discussed in earlier posts.

I shall attempt to pull some floorboards up in the hallway upstairs and see what delights that reveals! Wish me luck...


Attachments:
Severed end of the cable.jpg
Severed end of the cable.jpg [ 61.98 KiB | Viewed 53 times ]
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:14 pm 
Offline
OAP

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39135
Has thanked: 181 times
Been thanked: 1983 times
It's just old Lead cable, Sparkydude was thinking you had conduit carrying some cables.

_________________
---------------------------------------------------------------------------------------------------

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html



For this message the author thescruff has received gratitude : dinx67
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:21 pm 
Offline
Senior Member
User avatar

Joined: Sat Aug 13, 2005 8:11 pm
Posts: 2038
Location: Staffordshire
Has thanked: 2 times
Been thanked: 94 times
Scruff the conduit i was thinking of was the mains tails. Its possible they have used a steel conduit between mains incomers and then just put an earth clamp round it to obtain an earth.

All will be revealed when Norweb have been and we will know whats happening. The fuse box looks in very good condition and is pretty neat and tidy , so at least we know its been rewired. It may be wise to have a look at a few switches/sockets just to make sure they all have PVC cables in them and none have brittle rubber sheathed cables in them. It is a possibility that somewhere along the ine the fusebox may have been replaced, cables extended and joined to old cables somewhere. That was the only thing i could think of could have caused the RCD to trip. Maybe its joined to new wiring and only the neutral is connected so when chirted to earth led to the RCD to trip.

Look forward to the report later of their findings.

Nick

_________________
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL


Last edited by sparkydude on Sun Aug 01, 2010 1:38 pm, edited 1 time in total.

Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:23 pm 
Offline
Newly registered Member
User avatar

Joined: Sat Jul 31, 2010 9:03 pm
Posts: 78
Location: Wigan, NW
Has thanked: 108 times
Been thanked: 1 times
Thanks Scruff - you guys are very thorough! And extremely helpful too.

So is it possible that by using old lead cable as part of an earth circuit for the meter/fuse box, this has somehow made the old cabling live? Would that be a reasonable explanation for why the old cable in the living room is live?

I really should hang my head in shame... but I do only teach primary so my knowledge of electricity doesn't go much past making basic circuits!


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:24 pm 
Offline
Senior Member
User avatar

Joined: Tue Oct 27, 2009 8:55 pm
Posts: 3074
Location: St Helens Merseyside
Has thanked: 33 times
Been thanked: 174 times
All will be revealed when Norwedb have been and we will know whats happening.


Don't count on it Dude!

_________________
Measure twice, cut once!



For this message the author Simon Site Manager has received gratitude : dinx67
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:32 pm 
Offline
OAP

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39135
Has thanked: 181 times
Been thanked: 1983 times
I don't think the old cables are live, but they are causing an earth fault and the tripping somehow.

_________________
---------------------------------------------------------------------------------------------------

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html



For this message the author thescruff has received gratitude : dinx67
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:39 pm 
Offline
Newly registered Member
User avatar

Joined: Sat Jul 31, 2010 9:03 pm
Posts: 78
Location: Wigan, NW
Has thanked: 108 times
Been thanked: 1 times
Mr Norweb-engineer has just left! He looked at the gubbins in the meter cupboard and tested the earth circuit - the reading was 0.11, which he said was fine. He said that the sub-main from next door needs to be replaced but that it isn't urgent - someone will phone to make arrangements to come and do that in the next week or so.

He said we need to get a spark in to find out where the cable in the living room goes to and get it capped off properly.


Last edited by dinx67 on Sun Aug 01, 2010 1:47 pm, edited 2 times in total.

Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:43 pm 
Offline
OAP

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39135
Has thanked: 181 times
Been thanked: 1983 times
dinx67 wrote:

He said we need to get a spark in to find out where the cable in the living goes to and get it capped off properly.


Did he test it to see whether it was live or not :scratch:

_________________
---------------------------------------------------------------------------------------------------

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html



For this message the author thescruff has received gratitude : dinx67
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:45 pm 
Offline
Newly registered Member
User avatar

Joined: Sat Jul 31, 2010 9:03 pm
Posts: 78
Location: Wigan, NW
Has thanked: 108 times
Been thanked: 1 times
He didn't test it, Scruff. I have a multimeter (that I have never actually used) - will that do the job?


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Sun Aug 01, 2010 1:50 pm 
Offline
OAP

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39135
Has thanked: 181 times
Been thanked: 1983 times
dinx67 wrote:
He didn't test it, Scruff. I have a multimeter (that I have never actually used) - will that do the job?


Yes it would be perfect if you have the instruction manual or know how to use it.

Looking at the state of the wires in the pic, I think you can guarantee it's not live.

I'm not a sparky by the way, just an retired plumber. :roll:

_________________
---------------------------------------------------------------------------------------------------

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html



For this message the author thescruff has received gratitude : dinx67
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 119 posts ]  Go to page Previous  1, 2, 3, 4, 5, 6 ... 8  Next


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: dittohead, Google [Bot] and 5 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling