I had a condensing boiler installed six years ago. It has run without a fault since then and has been serviced annually by the installer. This winter, water was seen dripping from the condensate trap on to the kitchen work surface. I contacted the installer who said it was due to freezing in the external condensate pipe and told me to use hot water to clear the blockage. This seemed to do the trick.

Yesterday I had the boiler serviced - not by the installer, but by another engineer I had used in the past. Everything was going well until he came to check the combustion, which was miles out. One figure (I think it was CO) was up in the thousands. The engineer though it was due to a dirty hex, so he stripped it down, cleaned and reassembled. This had no effect. He thought he could see signs of water damage so he spoke to the manufacturer's tech support, who agreed with his conclusions. The result is that I am faced with a bill around £1000 to repair the boiler, or more if it cannot be repaired.

That's the background; now for my questions.

The condensate pipe is external and piped as shown in the left hand diagram. This would appear to be wrong as it does not leave an air gap between the 22mm pipe through the wall and the 32mm pipe connecting to the drain. The correct way would seem to be is as shown in the diagram on the right.

1. Is this correct?
2. Do I have a claim against the installer for the cost of repair/replacement?

Attachment:
Condense Drain.png
Condense Drain.png [ 3.14 KiB | Viewed 721 times ]


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Wed May 16, 2018 6:49 pm 
Offline
Senior Member

Joined: Wed Feb 26, 2014 9:35 pm
Posts: 3199
Has thanked: 44 times
Been thanked: 698 times
What is the pipe that it drains into, where does that go? I don't see why you would need/want an air gap.


Top
 Profile  
Reply with quote  
PostPosted: Wed May 16, 2018 7:28 pm 
Offline
Senior Member

Joined: Tue Oct 02, 2007 11:45 am
Posts: 1288
Has thanked: 28 times
Been thanked: 139 times
Rorschach wrote:
What is the pipe that it drains into, where does that go? I don't see why you would need/want an air gap.

1. It's a 32mm plastic pipe which goes into the same external drain as the kitchen sink.
2. The Installation Instructions recommends an air break to prevent freezing.


Top
 Profile  
Reply with quote  
PostPosted: Wed May 16, 2018 8:25 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6960
Has thanked: 840 times
Been thanked: 933 times
I know you are quite well versed with your heating/boiler so apologies in advance if any questions seem too basic!

The existing condensate pipe and diagram, could you confirm if the overflow is just dropped into the 32mm or connected/sealed with a fitting?

Also, I can’t remember, what make is your boiler?

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
PostPosted: Wed May 16, 2018 9:58 pm 
Offline
Senior Member

Joined: Wed Feb 26, 2014 9:35 pm
Posts: 3199
Has thanked: 44 times
Been thanked: 698 times
I can't see how an air gap will stop freezing, if anything it will let more cold air blow up the condensate pipe and start the freeze further up.


Top
 Profile  
Reply with quote  
PostPosted: Thu May 17, 2018 9:35 am 
Offline
Senior Member

Joined: Tue Oct 02, 2007 11:45 am
Posts: 1288
Has thanked: 28 times
Been thanked: 139 times
gas4you wrote:
I know you are quite well versed with your heating/boiler so apologies in advance if any questions seem too basic!

The existing condensate pipe and diagram, could you confirm if the overflow is just dropped into the 32mm or connected/sealed with a fitting?

Also, I can’t remember, what make is your boiler?


It's just dropped in - about 5mm.

It's a Remeha Avanta open vented. Last year's service shows 8.8%, 50ppm and 0.0005 so I'm really p'd off that this has happened. I do wonder if the installer knows he made a mistake, which is why he didn't reply to my phone calls about having the boiler serviced.


Top
 Profile  
Reply with quote  
PostPosted: Thu May 17, 2018 4:30 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 7459
Location: Northampton
Has thanked: 316 times
Been thanked: 960 times
The second way is definitely wrong as the wind chill over the end of the pipe will cause freezing. Remehas are quite prone to this as they drip rather than store it up and release in one go as some boilers do and they also condense quite a lot as they are efficient.

It depends what is in the Manufacturers Instructions that came with the boiler as to whether it's incorrectly terminated or not, personally I upgrade the pipe before it goes through the wall.

After 6 years I wouldn't bother to pursue a claim against the installer just put it down to life!

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html


Top
 Profile  
Reply with quote  
PostPosted: Thu May 17, 2018 5:23 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6960
Has thanked: 840 times
Been thanked: 933 times
Then the first one has an air gap. Cant see nothing wrong that way. If it freezes below in the 32mm then the condensate can still get out by spilling over.

My Remeha installs just have a tundish, well an upturned R16 actually, straight under the condensate outlet under the boiler. The condensate trap on these is do big you will never get POC out if it.

I would get a fixed price repair from Baxi to sort it. Around £350 IIRC

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : D Hailsham
Top
 Profile  
Reply with quote  
PostPosted: Thu May 17, 2018 7:26 pm 
Offline
Senior Member

Joined: Tue Oct 02, 2007 11:45 am
Posts: 1288
Has thanked: 28 times
Been thanked: 139 times
Razor wrote:
After 6 years I wouldn't bother to pursue a claim against the installer just put it down to life!

That's what I would expect an installer to say.

gas4You wrote:
I would get a fixed price repair from Baxi to sort it. Around £350 IIRC

Thanks for that excellent suggestion; I phoned them immediately. It's going to cost £381, spread over 12 months. We'll have to wait a week, which is acceptable as some of the delay is due to our unavailability.


The cheapest price I could find online for the hex is £540 inc VAT.



For this message the author D Hailsham has received gratitude : gas4you
Top
 Profile  
Reply with quote  
PostPosted: Thu May 17, 2018 8:06 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6960
Has thanked: 840 times
Been thanked: 933 times
I am often moaned about for recommending fixed price repairs for customers, but I work on the principle of being honest with the customer and tbh most come back to me for further servicing etc afterwards.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
PostPosted: Fri May 18, 2018 11:57 am 
Offline
Senior Member

Joined: Tue Oct 02, 2007 11:45 am
Posts: 1288
Has thanked: 28 times
Been thanked: 139 times
The Baxi scheme is a really an insurance policy normally costing about £20 per month, with an additional premium for repairing the existing fault. So I must thank all the policy holders who haven't made any claims on their insurance for contributing to the repair of my boiler!

When I lived in Croydon my heating system was covered by a plan provided by a local firm of heating engineers. They still provide the same service for £20 per month. Why don't other engineers do the same - even sole traders?


Top
 Profile  
Reply with quote  
PostPosted: Fri May 18, 2018 1:34 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 7459
Location: Northampton
Has thanked: 316 times
Been thanked: 960 times
D Hailsham wrote:
Razor wrote:
After 6 years I wouldn't bother to pursue a claim against the installer just put it down to life!

That's what I would expect an installer to say.




Actually I'm the lead breakdown engineer for a boiler manufacturer not an installer.

Still your comment is exactly what I'd expect a t*at to say :thumbright:

_________________
As always help on here is free, however if you think you have saved a decent sum of money why not click the link to find out about the charity we're currently supporting? A couple of quid makes a real difference.

donnas-dream-house-charity-t52110.html



For this message the author Razor has received thanks - 2: Gadget, OchAye
Top
 Profile  
Reply with quote  
PostPosted: Fri May 18, 2018 7:02 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6960
Has thanked: 840 times
Been thanked: 933 times
D Hailsham wrote:
The Baxi scheme is a really an insurance policy normally costing about £20 per month, with an additional premium for repairing the existing fault. So I must thank all the policy holders who haven't made any claims on their insurance for contributing to the repair of my boiler!

When I lived in Croydon my heating system was covered by a plan provided by a local firm of heating engineers. They still provide the same service for £20 per month. Why don't other engineers do the same - even sole traders?



Its a numbers game.

If I could get 1000 customers paying £20+ per month I would. Even with 50% for parts you would still make a good living.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
PostPosted: Thu May 24, 2018 6:46 pm 
Offline
Senior Member

Joined: Tue Oct 02, 2007 11:45 am
Posts: 1288
Has thanked: 28 times
Been thanked: 139 times
Update

The Baxi engineer turned up today. He checked the combustion and found the CO was extremely high. So he decided the first thing to do was change the gas valve. He did that, then checked again. CO almost back to normal. He spent a few minutes adjusting the gas valve to get the correct numbers for High and Low. Job done. Didn't bother to change the hex.

I've probably spend more on the insurance than the actual cost of replacing the gas valve, but it's less than the independent engineer wanted to change both valve and hex; and I'm still covered if the hex goes in the next year.


Top
 Profile  
Reply with quote  
PostPosted: Thu May 24, 2018 8:05 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6960
Has thanked: 840 times
Been thanked: 933 times
You’re not too much out of pocket.

I would charge around £220+vat to replace a gas valve on your boiler if local to me and you would only get a warranty on the new part

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : D Hailsham
Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 15 posts ] 

 

 




Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO