Hi

First post!

Any one know If I can extend a ring main into a new conservatory without falling foul of the dreaded Part P regs?

I have a bungalow and a single ring circuit for 13amp sockets with a 32amp mcb and the same for lighting!

I realise if I replace the consumer unit it would fall under the regs so understandably i'm trying to avoid this!

Cheers

Neil


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
 

You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Mon Mar 12, 2007 11:31 pm 
Offline
Newly registered Member

Joined: Mon Mar 12, 2007 11:15 pm
Posts: 11
Location: oxfordshire
Has thanked: 0 times
Been thanked: 0 times
Sorry not a 32amp mcb for lighting a 6amp!

Getting tired now! ::b

Neil


Top
 Profile  
 
 Post subject:
PostPosted: Mon Mar 12, 2007 11:38 pm 
Offline
Pro Handyman
User avatar

Joined: Sun Nov 19, 2006 4:31 pm
Posts: 3428
Location: North West, England, United Kingdom
Has thanked: 18 times
Been thanked: 26 times
Replacing the CU, I'd get a sparkie.

If you do it yourself, which you are entitled to, you have to inform Building Regs and they will charge for it, but they MUST appoint a spark to test your work. It's their responsibility not your, in fact it's against regulations for you to ask a spark to test your work for part p.

The only way round it is to do it and tell no one. :?

_________________
Jaeger.
Senior Member doesn't mean I'm OLD!

darrenc wrote:
I dont think its a stupid question but does show a lack of understanding of how paint works and reasons for certain applications, now dont jump down my throat Jaegar i'm not being funny its just a classic case in point of a well educated professionally trained painter against a general tradesman.

Image


Top
 Profile  
 
 Post subject:
PostPosted: Mon Mar 12, 2007 11:56 pm 
Offline
Newly registered Member

Joined: Mon Mar 12, 2007 11:15 pm
Posts: 11
Location: oxfordshire
Has thanked: 0 times
Been thanked: 0 times
Thanks for the quick reply :grin:

I wouldn't replace the cu If It wasn't neccessary and i guess what i'm trying to say is do I actually need to? ie. can i just extend the ring into the new conservatory? I mean is there any other factor apart from the 7200 watt limit on a ring main.I want to put in about seven double sockets!! :shock:

Regarding part p regs ::b
I seem to get differing advice from Gov web sites so am at a loss what is right or wrong! The way i see it i'm not adding a new circuit, just sockets and lights to an existing circuit. It does seem like a grey area to me!

Cheers

Neil


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 12:55 am 
Offline
BANNED
User avatar

Joined: Wed Jan 18, 2006 10:48 pm
Posts: 2137
Location: Leicestershire
Has thanked: 0 times
Been thanked: 1 times
sounds ok to me

its not a kitchen or a bathroom and you are adding to existing sockets

no need to notify


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 1:07 am 
Offline
Pro Handyman
User avatar

Joined: Sun Nov 19, 2006 4:31 pm
Posts: 3428
Location: North West, England, United Kingdom
Has thanked: 18 times
Been thanked: 26 times
One socket - Spur - Fine.

Changing existing for new - Fine

Extending the ring, a little different, it is covered under part p.

See the sticky thread at the top.

_________________
Jaeger.
Senior Member doesn't mean I'm OLD!

darrenc wrote:
I dont think its a stupid question but does show a lack of understanding of how paint works and reasons for certain applications, now dont jump down my throat Jaegar i'm not being funny its just a classic case in point of a well educated professionally trained painter against a general tradesman.

Image


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 7:29 am 
Offline
BANNED
User avatar

Joined: Wed Jan 18, 2006 10:48 pm
Posts: 2137
Location: Leicestershire
Has thanked: 0 times
Been thanked: 1 times
well thats not how I read it

extra sockets on an existing ring fine - no detail on how many

also regs dont determine a max number of sockets per ring, but do state a maximum ring length of 100m

imo the only notifiable work is

new circuits added to the board
a new board
any new work in a kitchen, bathroom or outside


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 8:10 am 
Offline
Senior Member

Joined: Wed Feb 28, 2007 12:17 pm
Posts: 268
Location: Newcastle T&W
Has thanked: 0 times
Been thanked: 1 times
Jaeger_S2k wrote:
If you do it yourself, which you are entitled to, you have to inform Building Regs and they will charge for it, but they MUST appoint a spark to test your work. It's their responsibility not your, in fact it's against regulations for you to ask a spark to test your work for part p.

So lets get this correct…..building control can appoint a spark to certify the work but me or you can’t….why’s that then.


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 8:21 am 
Offline
Pro Handyman
User avatar

Joined: Sun Nov 19, 2006 4:31 pm
Posts: 3428
Location: North West, England, United Kingdom
Has thanked: 18 times
Been thanked: 26 times
uncle buck wrote:
Jaeger_S2k wrote:
If you do it yourself, which you are entitled to, you have to inform Building Regs and they will charge for it, but they MUST appoint a spark to test your work. It's their responsibility not your, in fact it's against regulations for you to ask a spark to test your work for part p.

So lets get this correct…..building control can appoint a spark to certify the work but me or you can’t….why’s that then.


Because we are not the controlling authority, I guess.
They contract the spark to work under their authority and report to them.

Hopefully Ban All or Stoday will come along and confirm the Part P requirements. I'm no expert (as many will testify) but I'd air on the side of caution with this one.

_________________
Jaeger.
Senior Member doesn't mean I'm OLD!

darrenc wrote:
I dont think its a stupid question but does show a lack of understanding of how paint works and reasons for certain applications, now dont jump down my throat Jaegar i'm not being funny its just a classic case in point of a well educated professionally trained painter against a general tradesman.

Image


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 8:36 am 
Offline
Senior Member

Joined: Wed Feb 28, 2007 12:17 pm
Posts: 268
Location: Newcastle T&W
Has thanked: 0 times
Been thanked: 1 times
Well that’s just not on now is it….why should building control be allowed to sub-contract the testing out but the house owner can’t…..this is just another example of how part p is only concerned with taking money from you. :ag


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 8:52 am 
Offline
Site Admin
User avatar

Joined: Sat Jul 16, 2005 8:06 pm
Posts: 23116
Location: Darwen, Lancashire
Has thanked: 488 times
Been thanked: 726 times
uncle buck wrote:
Well that’s just not on now is it….why should building control be allowed to sub-contract the testing out but the house owner can’t…..this is just another example of how part p is only concerned with taking money from you. :ag


Exactly!

Part p does little to make electrics safer, in fact it make electrics more dangerous! IMHO

Before part p you could get a consumer unit changed for £150 all in, now this has shot up to £400 in some areas. I know people with old fuseboards that really need changing, but they won't do because of the cost. They could of afforded the £150 but are not prepared to pay out £400 and so they will just leave their dangerously overloaded fuse boards!

Ban-All-sheds has done a great post on part p, it can be found here-

http://www.ultimatehandyman.co.uk/forum ... php?t=1215

At the time of writing (April 2006), the following work was classed as not needing notification to LABC:


2. Work which -

(a) is not in a kitchen, or a special location,

(b) does not involve work on a special installation, and

(c) consists of -


(i) adding light fittings and switches to an
existing circuit or

(ii) adding socket outlets and fused spurs to an
existing ring or radial circuit.


The problem is that the rules are often open to interpretation.

By reading point (ii) above it would seem in my opinion that you are allowed to add to your existing ring main without notification.

_________________
Check out our nominated charity


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 10:46 am 
Offline
Pro Handyman
User avatar

Joined: Sun Nov 19, 2006 4:31 pm
Posts: 3428
Location: North West, England, United Kingdom
Has thanked: 18 times
Been thanked: 26 times
:thumbright:

_________________
Jaeger.
Senior Member doesn't mean I'm OLD!

darrenc wrote:
I dont think its a stupid question but does show a lack of understanding of how paint works and reasons for certain applications, now dont jump down my throat Jaegar i'm not being funny its just a classic case in point of a well educated professionally trained painter against a general tradesman.

Image


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 6:52 pm 
Offline
Newly registered Member

Joined: Mon Mar 12, 2007 11:15 pm
Posts: 11
Location: oxfordshire
Has thanked: 0 times
Been thanked: 0 times
Hi guys

thanks for all the input on this one. i'm inclined to agree with ultimatehandyman on this.

I even found a gov website which states in their FAQ that electrical installion into a conservatory is NOT notifieable unless the work extends to the provisions of a new circuit, or involves an extension to an existing circuit in a kitchen or bathroom. However, new socket-outlets in a conservatory should be provided with RCD protection, as in most cases it would be reasonable to expect that they may be used to supply portable equipment for use outdoors.

However I'm getting paranoid about future probs with selling the house etc etc Also 2 professional Sparkies failed to mention the above facts :? When pricing for a job.Do they know something other than the above facts or Is it the Bl**din obvious!
worries me a bit :sad:

I have done a lot of this type of work before the new regs and feel a bit let down by the industry on this one! ::b

Any Sparkies want to comment on the regs?

Cheers


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 10:07 pm 
Offline
Newly registered Member

Joined: Mon Mar 12, 2007 11:15 pm
Posts: 11
Location: oxfordshire
Has thanked: 0 times
Been thanked: 0 times
Hi just for the record, some gov websites are saying If the ring serves a kitchen or bathroom then an extension to the ring is indeed notifiable!

As it involves an extension to an existing circuit in a kitchen or bathroom.

you cant win can you! :roll:
cheers

Neil


Top
 Profile  
 
 Post subject:
PostPosted: Tue Mar 13, 2007 10:41 pm 
Offline
Senior Member

Joined: Wed Feb 28, 2007 12:17 pm
Posts: 268
Location: Newcastle T&W
Has thanked: 0 times
Been thanked: 1 times
Personally I would just do it & worry about certification when you need it…..you will more than likely find that if you haven’t got the correct certification when you come to sell the property there will be measures in place to obtain it.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 34 posts ]  Go to page 1, 2, 3  Next



Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 



phpBB SEO