PostPosted: Thu Jan 10, 2008 1:43 pm    Post subject: Add User to Ignore List Reply with quote

As menctioned the fault was caused on installation, most showers now have a label over the terminal block teling the installer to check that all terminals are made secure.

The mcb will not trip as there is no overcurrent and the rccb/rcd will not trip as there is no fault to ground, so from arcing the cable heats up nicely melting insulation. So all that can be done is replace burnt cable and terminals
Back to top
View user's profile Send private message Send e-mail
Oddbod
Junior Member


Joined: 09 Jan 2008
Posts: 11

PostPosted: Thu Jan 10, 2008 2:30 pm    Post subject: Add User to Ignore List Reply with quote

heating/sparking wrote:
As menctioned the fault was caused on installation, most showers now have a label over the terminal block teling the installer to check that all terminals are made secure.



sorry, wasn't disagreeing with you there in my badly worded reply, I was just saying that I had been to a clients house that had the same problem, for the same reason, and remarking on the coicidence of what appeared to be the same shower. What had shocked me was the fact that a plumber had previously been out to check the problem, and had walked away leaving the cables in that condition without warning them not to use the shower until they had someone else look at it at the very least.

I guess plumber would be a very loose term in this instance.
Back to top
View user's profile Send private message
zaax
Junior Member


Joined: 27 Jan 2008
Posts: 3

PostPosted: Sun Jan 27, 2008 11:28 pm    Post subject: Add User to Ignore List Reply with quote

Should terminal blocks be used for 15amps?
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   This topic is locked: you cannot edit posts or make replies.    Thank Post    www.ultimatehandyman.co.uk Forum Index -> General DIY forum -> DIY Disasters All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You can attach files in this forum
You can download files in this forum

 



ultimatehandyman privacy policy

Powered by phpBB © 2001, 2005 phpBB Group
phpBB SEO

Diy forum - Decking - plastering - Plumbing - DIY - Tiling