As menctioned the fault was caused on installation, most showers now have a label over the terminal block teling the installer to check that all terminals are made secure.

The mcb will not trip as there is no overcurrent and the rccb/rcd will not trip as there is no fault to ground, so from arcing the cable heats up nicely melting insulation. So all that can be done is replace burnt cable and terminals


Top
 Profile  
 
 Post subject:
PostPosted: Thu Jan 10, 2008 2:30 pm 
Offline
Newly registered Member

Joined: Wed Jan 09, 2008 9:23 pm
Posts: 11
Has thanked: 0 times
Been thanked: 0 times
heating/sparking wrote:
As menctioned the fault was caused on installation, most showers now have a label over the terminal block teling the installer to check that all terminals are made secure.



sorry, wasn't disagreeing with you there in my badly worded reply, I was just saying that I had been to a clients house that had the same problem, for the same reason, and remarking on the coicidence of what appeared to be the same shower. What had shocked me was the fact that a plumber had previously been out to check the problem, and had walked away leaving the cables in that condition without warning them not to use the shower until they had someone else look at it at the very least.

I guess plumber would be a very loose term in this instance.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Sun Jan 27, 2008 11:28 pm 
Offline
Newly registered Member

Joined: Sun Jan 27, 2008 10:13 pm
Posts: 4
Has thanked: 0 times
Been thanked: 0 times
Should terminal blocks be used for 15amps?


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 18 posts ]  Go to page Previous  1, 2


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling