PostPosted: Sun Apr 08, 2018 11:41 am 
Offline
Senior Member

Joined: Thu Jan 27, 2011 10:17 am
Posts: 151
Has thanked: 14 times
Been thanked: 0 times
I have just got an electric shock from the lighting cct. No need to go into should have turned power off, I realise that.
The big shock, no pun intended is that no cct breaker/rcd tripped.
Is this because I was touching live and neutral and not earth?
I thought one would trip or was the shock not big enough or long enough to make them trip?

glassescase


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 12:06 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7684
Has thanked: 44 times
Been thanked: 1303 times
Depends what you were actually doing, and what you actually have by means of protection.

More info would help, including a picture of your consumers unit.

I suspect I know the answer, but it depends on what you post next

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 12:48 pm 
Offline
Senior Member

Joined: Thu Jan 27, 2011 10:17 am
Posts: 151
Has thanked: 14 times
Been thanked: 0 times
I was connecting a wall light.
As for attaching a picture, not sure how to do that as there is no insert option.
Now someone-else, your reply has made me go and look at the fuse box and I'm going to guess,
I wonder if it is what you suspect, so if I'm right, thank you for giving me the lead

The cct is protected by an MCB, not an RCD. There is the big on off switch on the left, then to the right is my light cct and some other MCB's, further right is an RCD and further right are more MCB's.

MCB is not as sensitive as RCD and I assume I did not draw more then 5 or 6 amps so the MCB did not trip

glassescase


Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 12:56 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7684
Has thanked: 44 times
Been thanked: 1303 times
Picture still required, and what exactly were you doing at the time. (I know you were connecting a wall light, but what were you doing? screwdriver in one hand? your fingers were?)

Question: Posting pictures, now where could you find help on doing that?

Answer: Read my signature

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 1:52 pm 
Offline
Senior Member

Joined: Thu Jan 27, 2011 10:17 am
Posts: 151
Has thanked: 14 times
Been thanked: 0 times
sorry someone-else I cant recall exactly but I think I was using a screwdriver to push a wire into a hole in the wall while holding the light fitting and or pushing another wire back into the hole with my other hand.

Damn, so easy to add a picture when you know how, thank you
hopefully fuse box picture now attached

glassescase


Attachments:
Fuse Box.JPG
Fuse Box.JPG [ 279.73 KiB | Viewed 744 times ]
Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 2:45 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7684
Has thanked: 44 times
Been thanked: 1303 times
glassescase wrote:
Damn, so easy to add a picture when you know how, thank you


................and its been in my signature for, must be a year now. :welcome:

Back to your question.

You have a misunderstanding of how consumers units and electricity work, no worries, I shall explain.

I would guess that you touched a live wire while another part of you was holding / touching the earthed light fitting. This is how you received the electric shock.

What I suspected ealier is true.
Your consumers unit does have an RCD (But we all knew that) what you didn't realise is that only your sockets (and the conservatory lights) are protected by the RCD as they are all on the right of said RCD. The lighting MCB's (and smoke detectors and garage) are NOT protected by the RCD. If it had of been protected by the RCD then yes, I would have expected it to trip.

All new consumers units (17th edition electrical wiring regulations onwards) have two RCD's so one is for lights and "stuff" and the other is for sockets and "stuff" You used to be able to get consumers units where everything was protected by one RCD (I had one) but the down side is if a lamp failed, sometimes they would take out the RCD, and so all the sockets would be switched off too. Like wise if there was a fault on the sockets at night all the lights would go out too :angryfire: (very annoying)

You are correct when you said
glassescase wrote:
I assume I did not draw more then 5 or 6 amps so the MCB did not trip
If you had, you would not be sitting there reading this, as it takes around 8mA (across the heart) to kill a human. (1000 mA to the Amp) I would also guess you said some unusual words :lol:

However I should point out that when you said
glassescase wrote:
MCB is not as sensitive as RCD
That is a total miss understanding. (Again, no worries, I shall explain)

An MCB (Miniature Circuit Breaker) in plain / simple English is designed to operate in an "overload" situation. Be that you have plugged in too much stuff, or nail through a cable, or a fault to earth etc (in any of the previous examples, more current flows than the MCB is meant to carry)

An RCD (Residual Current Device) in plain / simple English detects current flowing to earth, if this current exceeds 30mA it operates. Unlike an MCB, It will not "mind" if you are using, say 40Amps because all the 40Amps (remember 40A is only an example) are being used, and none are "leaking" to earth.

NOTE: Electricity has no prejudices, it will kill anyone. Always turn off the supply to the device / circuit you are going to work on, and before you touch it, Prove it is dead, not you.

As I said, the above is in plain / simple English, so I have left out the technical bits. :wink:

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here



For this message the author someone-else has received thanks - 4: arco_iris, dewaltdisney, NUFC1000, OnlyMe
Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 4:40 pm 
Offline
Senior Member

Joined: Fri Jan 20, 2006 5:51 pm
Posts: 8098
Location: Essex
Has thanked: 574 times
Been thanked: 1685 times
Good post SE, I found that very informative :thumbright: I am pretty useless with electric issues.

DWD

_________________
Painting with BIN



For this message the author dewaltdisney has received gratitude : someone-else
Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 7:01 pm 
Offline
Senior Member

Joined: Sat Apr 19, 2014 6:27 pm
Posts: 389
Has thanked: 44 times
Been thanked: 85 times
dewaltdisney wrote:
Good post SE, I found that very informative :thumbright:


:withstupid:


Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 7:42 pm 
Offline
Senior Member

Joined: Thu Jan 27, 2011 10:17 am
Posts: 151
Has thanked: 14 times
Been thanked: 0 times
Thank you someone-else that is a good explanation. One question, Can i replace the MCB's on the left with RCD's?

glassescase


Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 8:06 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7684
Has thanked: 44 times
Been thanked: 1303 times
The answer is in two parts.

1) No, because they will not physically fit. Look at the size of the one you have, and as I already said an RCD and an MCB do NOT do the same thing.

You may be thinking of an RCBO, which is a cross between an RCD and and MCB, and yes it does do both functions. But you have to get ones for your consumers unit (if they make them)

You would need to get a qualified electrician to change them.

2) You do not need them since you will turn the supply off when working on ANYTHING electrical. You are also going to buy a multi meter, learn how to use its basic functions to prove a circuit is dead, better it be dead than.........

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 9:06 pm 
Offline
Senior Member

Joined: Thu Jan 27, 2011 10:17 am
Posts: 151
Has thanked: 14 times
Been thanked: 0 times
I was doing electrics a couple of days ago on a house i just got as the seller had left wires dangling from ceiling. Did all the proper checks, power off, switch off, multi meter testing. Today..........I made a mistake and your right, not one I will make again.


Appreciate all the help and advice someone-else

glassescae


Top
 Profile  
Reply with quote  
PostPosted: Sun Apr 08, 2018 9:23 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7684
Has thanked: 44 times
Been thanked: 1303 times
Anytime. Happy to be of assistance.

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Wed Apr 11, 2018 7:03 pm 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 23784
Location: hants/dorset border
Has thanked: 1477 times
Been thanked: 3757 times
someone-else wrote:


If you had, you would not be sitting there reading this, as it takes around 8mA (across the heart) to kill a human. (1000 mA to the Amp)


Interesting that. I must have no heart... :roll: :roll: I took a 40 + Amp shock from my left hand to my right... and after picking myself up from the floor (and enquiring of Mrs.wine~o why it was still live when I had asked her to switch off) I found the shower circuit (separate CU via henley block ) The rcd was still on, the mcb (40A) had tripped.

I had a great big black burn under my right armpit.

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


Top
 Profile  
Reply with quote  
PostPosted: Wed Apr 11, 2018 8:31 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7684
Has thanked: 44 times
Been thanked: 1303 times
Not true. (about you not having a heart)
as I said its around 8mA across the heart. The voltage would have been 240, that with the high resistance of your body means "you felt it" but it wasn't 8mA across your heart.
If the voltage had of been higher then................

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Thu Apr 12, 2018 6:00 pm 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 23784
Location: hants/dorset border
Has thanked: 1477 times
Been thanked: 3757 times
someone-else wrote:
"you felt it" but it wasn't 8mA across your heart.
If the voltage had of been higher then................


Felt it alright. :shock: Took me 10 minutes to realise that I was on the floor...

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 15 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO