Cool Rads on an unvented pressurised CH system

 
Post new topic   This topic is locked: you cannot edit posts or make replies.   Thank Post    www.ultimatehandyman.co.uk Forum Index -> Plumbing Forum -> Central Heating & Boilers
 View previous topic :: View next topic  
Author Message
fellmaster
Junior Member


Joined: 12 Oct 2007
Posts: 3

PostPosted: Fri Oct 12, 2007 12:11 pm    Post subject: Cool Rads on an unvented pressurised CH system Add User to Ignore List Reply with quote

hello Hello

For no apparent reason my Ch system is losing pressure ,noisy and the rads are only luke warm even after bleeding
symptoms
The pressurised ex vessel loses water pressure even after charge up to correct limit.
There is is loss of water thro the tun dish and to the over flow pipe. This is not unusal as I normally have drain the entire system once a year and its coming up for its annual drain.
the whole system inc the WSP pump is nosiy

system
ideal mexico 2 gas non condensing
altechnic expansion vessel
tribune pressurised HW cylinder

can anyone help cos I am stumped
thanks fell
Back to top
View user's profile Send private message
Hinton Heating
Gas/Heating Expert


Joined: 16 Jan 2006
Posts: 4296
Location: Bournemouth

PostPosted: Fri Oct 12, 2007 5:27 pm    Post subject: Add User to Ignore List Reply with quote

1st of all can the mexico go on a sealed system? maybe it can!

Which expansion vessel is lossing presure? the white or the red?

Why do you drain the system? which sytem, the rads, or the hot water?

Is the boiler PRV also routed into the tundish?

If your pumping up the red expansion vessel, and its loosing air, i'm guessing its loosing it into the system, casuing your nosie & air problems.

The boiler/rad system PRV is dischaging as the expansion isn't being talen up by the faulty expansion vessl, the diaphragm is spilt.

_________________
www.hintonheating.com



Back to top
View user's profile Send private message Send e-mail
fellmaster
Junior Member


Joined: 12 Oct 2007
Posts: 3

PostPosted: Thu Oct 18, 2007 11:53 am    Post subject: Add User to Ignore List Reply with quote

Hinton Heating wrote:
1st of all can the mexico go on a sealed system? maybe it can!

Which expansion vessel is lossing presure? the white or the red?

Why do you drain the system? which sytem, the rads, or the hot water?

Is the boiler PRV also routed into the tundish?

If your pumping up the red expansion vessel, and its loosing air, i'm guessing its loosing it into the system, casuing your nosie & air problems.

The boiler/rad system PRV is dischaging as the expansion isn't being talen up by the faulty expansion vessl, the diaphragm is spilt.


1..yes

2..red

3..Th Hw cos the instrcution say that if the system discharges cold water thro the tundish to completely drain of HWand refill , this usually prevents water loss for about 6-12 months

4..yes

5. think your right

6..which diaphrapm . this sounds like i require a corgi heating engineer to fix what do you think
Back to top
View user's profile Send private message
Hinton Heating
Gas/Heating Expert


Joined: 16 Jan 2006
Posts: 4296
Location: Bournemouth

PostPosted: Thu Oct 18, 2007 4:36 pm    Post subject: Add User to Ignore List Reply with quote

the diaphagm is within the expansion vessel, and stops the water & air mixing.

If you press the center of the air valve, does water come out? If so you definatly need a new expansion vessel.

Its ok to drain & refill the unvented cylinder of hot water on an annual basis... just dont do this with a heating system!

_________________
www.hintonheating.com



Back to top
View user's profile Send private message Send e-mail
fellmaster
Junior Member


Joined: 12 Oct 2007
Posts: 3

PostPosted: Fri Oct 19, 2007 1:30 pm    Post subject: Add User to Ignore List Reply with quote

Hinton Heating wrote:
the diaphagm is within the expansion vessel, and stops the water & air mixing.

If you press the center of the air valve, does water come out? If so you definatly need a new expansion vessel.

Its ok to drain & refill the unvented cylinder of hot water on an annual basis... just dont do this with a heating system!


Cannot see the air valve on the exp vessel All there is is the fill loop and the red twist valve behing the dial
Is that the the valve you refer to??
thnaks
fell
Back to top
View user's profile Send private message
Hinton Heating
Gas/Heating Expert


Joined: 16 Jan 2006
Posts: 4296
Location: Bournemouth

PostPosted: Fri Oct 19, 2007 5:19 pm    Post subject: Add User to Ignore List Reply with quote

the air valve is on the opposite side to the pipe, and is the same as a car tyre valve.

You need to drain/depressurise radiatior system, then pump up air side of red expansion vessel to 1bar (with the drain off still open!)

then refill system

_________________
www.hintonheating.com



Back to top
View user's profile Send private message Send e-mail
Display posts from previous:   
Post new topic   This topic is locked: you cannot edit posts or make replies.    Thank Post    www.ultimatehandyman.co.uk Forum Index -> Plumbing Forum -> Central Heating & Boilers All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum

 

 

 



ultimatehandyman privacy policy

Powered by phpBB © 2001, 2005 phpBB Group
phpBB SEO

Diy forum - Decking - plastering - Plumbing - DIY - Tiling