Just doing a bit of reading for my own amusement, I came across these rules for putting cables in walls. I'm a little confused, so would welcome some clarification.

"A cable concealed in a wall or partition must

a) be at least 50mm from the surface [note 1]

b) have earthed armouring or an earthed metal sheath (eg SWA, a BS 8436 cable or MICC cable)

c) be enclosed in earthed steel conduit or trunking

d) be provided with mechanical protection (3mm steel is deemed sufficient to meet this requirement)"

http://wiki.diyfaq.org.uk/index.php/Cable_Routes_and_Protection

So, fitting a light switch in a brick wall does the cable need to be encased in earthed conduit?

Some years ago I installed a light switch on a solid wall in preparation for plastering. I covered it with a thin strip of steel purpose made for the job. It wasn't 3mm thick nor was it earthed. Is this now illegal?


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Sat Oct 28, 2017 2:30 pm 
Offline
Senior Member
User avatar

Joined: Wed Feb 25, 2015 7:20 pm
Posts: 2967
Has thanked: 895 times
Been thanked: 885 times
Read it all.
ie.

OR
e) be installed in a safe zone .
The 17th edition also requires cables in the safe zone to have 30mA RCD protection if not installed as per a, b, c or d.
Note 1 - If the wall or partition is made from or partially made from metal then the cable will require RCD protection or be installed as b), c) or d) above


Top
 Profile  
Reply with quote  
PostPosted: Sat Oct 28, 2017 4:15 pm 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 2431
Location: North Wales
Has thanked: 61 times
Been thanked: 507 times
As said some ands and so ors so when protecting with a 30 mA RCD which will operate within 40 mS and having cables in the safe zones then it does not need an outer earthed covering.

Where is does require it, then the covering has to comply, I don't know why YY cable is not included on the list, much is common sense but some bits don't seem to follow that idea.


Top
 Profile  
Reply with quote  
PostPosted: Sat Oct 28, 2017 5:39 pm 
Offline
Senior Member
User avatar

Joined: Sun Aug 18, 2013 8:04 pm
Posts: 7509
Location: Fife
Has thanked: 941 times
Been thanked: 1738 times
In reality 99% of sparkles run cabling in the loft that’s covered by glass wool. They run cables in stud partitions that are covered in glass wool. Never see conduit used in domestic instances nowadays or new build houses.


Top
 Profile  
Reply with quote  
PostPosted: Sat Oct 28, 2017 6:16 pm 
Offline
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 22411
Location: hants/dorset border
Has thanked: 1337 times
Been thanked: 3402 times
Permitted zones are horizontally and vertically within the width/height of the socket/switch whatever and require no protection. outside of that over 50mm depth and/or protected by suitable conduit/capping.

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


Top
 Profile  
Reply with quote  
PostPosted: Sat Oct 28, 2017 8:48 pm 
Offline
Senior Member

Joined: Thu Jan 22, 2009 9:53 am
Posts: 189
Has thanked: 33 times
Been thanked: 1 times
Cheers, guys. When I read 'safe zone' I immediately thought of the bathroom zones, so didn't think it applied to stud walls. I guess as long as there's an RCD back at 'base' then you're pretty well covered.


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO