Cable to a shed down the Garden

 
Post new topic   Reply to topic   Thank Post    www.ultimatehandyman.co.uk Forum Index -> Electric Forum UK
 View previous topic :: View next topic  
Author Message
Rapier503
Junior Member


Joined: 18 Sep 2007
Posts: 18

PostPosted: Thu Oct 09, 2008 12:26 pm    Post subject: Cable to a shed down the Garden Add User to Ignore List Reply with quote

Hi,
I want to run a cable from the house to a shed about 25m down the garden. Do I need any special cable (Artic or anything else) or can I get standard 3 core cable.

I was just thinking of running the cable under the paving stones to the shed. Is that ok?

Where is the cheapest place to get the cable from?

Thanks in advance,

Rapier
Back to top
View user's profile Send private message
IDontBelieveIt
Senior Member


Joined: 29 Jul 2008
Posts: 934
Location: North Hampshire

PostPosted: Thu Oct 09, 2008 3:17 pm    Post subject: Add User to Ignore List Reply with quote

No you MUST not use artic!

Yes 'anything else' is what you want it is called Steel Wire Armoured cable (SWA) and the one I have used in the analysis is the XPLE type.

You probably need 3-core and unless you are familiar with making the ends off (of SWA) thne don't bother doing it yourself. The installation must have high integrity and waterproof.

Assuming 6kW consumption peak at the shed (you do not mention expected loadings, the analysis results are as follows -

Required Cable Size 4 mm
Voltage Drop 6.52 Volts.
Percentage Drop 2.8%
Current Load 26.0 Amps

That 4 mm is a MINIMUM, I would actually use 6 mm.

Now -

1. What type of earthing arrangement is at the house (TN-S, TN-C-S/PME or TT)?

2. Where are you proposing to install the RCD protective device?

3. You are aware that this work comes under the building regulations? I trust and that you have applied to your local council before proceeding.

_________________
Never lie - that way you don't have to remember what you said.
Back to top
View user's profile Send private message
Rapier503
Junior Member


Joined: 18 Sep 2007
Posts: 18

PostPosted: Thu Oct 09, 2008 6:08 pm    Post subject: Add User to Ignore List Reply with quote

What is the gland for that comes with SWA Cable?

Thanks

Rapier
Back to top
View user's profile Send private message
IDontBelieveIt
Senior Member


Joined: 29 Jul 2008
Posts: 934
Location: North Hampshire

PostPosted: Thu Oct 09, 2008 6:26 pm    Post subject: Add User to Ignore List Reply with quote

How odd...

The glands don't 'come with' SWA you buy them separately and for external use you require CW 20mm.

So you know it (SWA) needs glands then, what made you think Artic flex would do the job then?

_________________
Never lie - that way you don't have to remember what you said.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    Thank Post    www.ultimatehandyman.co.uk Forum Index -> Electric Forum UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You can attach files in this forum
You can download files in this forum

 



ultimatehandyman privacy policy

Powered by phpBB © 2001, 2005 phpBB Group
phpBB SEO

Diy forum - Decking - plastering - Plumbing - DIY - Tiling