Hi all, I'm hoping I could get some help please.

I've been given half a dozen garden lights that I'd like to install though a bit confused as to the cable requirements. The lights are ip66 rated led floodlights, 10w each drawing 0.9amps at 12v and a spare (nothing to do with the set of lights) IP rated 80w led driver.

The plan was to operate these via a timed RCD socket in the garage, running the cable in black 20mm PVC conduit along the fence and the total cable run is approximately 15m though I planned to loop it back to the driver.

When I've tried to work out the cable gauge I need with online calculators it is suggesting 1awg/50mm2 cable which blows my plan of an inexpensive install out of the water. The calculator also suggested the load would exceed the driver spec.

Could anybody confirm the wire spec and load as correct please? By all means if what I'm proposing isn't sensible then likewise just say.

Any help very much appreciated. Cheers
Steve


Top
 Profile  
 
PostPosted: Fri Nov 18, 2011 11:02 am 
Offline
Senior Member
User avatar

Joined: Mon Mar 15, 2010 11:49 pm
Posts: 2309
Location: Oban
Has thanked: 62 times
Been thanked: 217 times
:lol:

methinks you've misplaced a decimal point somewhere.

1mm csa cable will be more than sufficient.

_________________
This post may contain nuts



For this message the author kellys_eye has received gratitude : sbis
Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

PostPosted: Fri Nov 18, 2011 11:38 am 
Offline
Newly registered Member

Joined: Wed Mar 03, 2010 2:21 pm
Posts: 13
Location: Bromley
Has thanked: 5 times
Been thanked: 0 times
Cheers kellys_eye - must admit I'd never seen anything chunky running to the LV light sets.

:thumbright:


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 3 posts ] 


Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling