Hi,

First post on here; will be looking through other posts too to see if there is anything similar to my problem.

We have a 6 year old Glow Worm combi boiler. Unsure of the model number at this time. The pressure happily sat around 1.1 bar, dropping occasionally over time, but nothing serious. We had the boiler serviced about a month ago and since then the pressure has been creeping up. After about a week or two it was up to 1.5 bar. It has since steadied about 1.7 bar. Yesterday we had the heating on and I thought about increasing the radiator water temperature. I went to have a look at noticed that there was water dripping from the outside pipe and that the boiler pressure was at 4.1 bar. I turned the heating off and it reduced to 1.7 bar again. I popped the heating on again this morning just to see what happened and it wasn't long before it was up at 3.5 bar.

I need to call the boiler chap, but could anyone possibly hazard a guess at what could be causing this? Thank you.


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 11:09 am 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6304
Has thanked: 724 times
Been thanked: 762 times
Expansion vessel gone flat

_________________
Dave

www.drlgas.co.uk



For this message the author gas4you has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 4:58 pm 
Offline
Senior Member
User avatar

Joined: Sat Nov 09, 2013 2:38 pm
Posts: 363
Has thanked: 22 times
Been thanked: 69 times
gas4you wrote:

Yup job for the installer, might work if re-pressurised but may need a new vessel.
Unlikely to be a result of the service as the only thing that might have caused it is if some twerp has bled the valve on the vessel, but that would have started straight away afterwards.
Sounds like just bad luck in this case :cb



For this message the author toolbox has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 5:09 pm 
Offline
BANNED

Joined: Wed Jun 14, 2017 8:38 am
Posts: 204
Has thanked: 696 times
Been thanked: 28 times
gas4you wrote:
+ 1

Sent from my LG-K100 using Tapatalk


Top
 Profile  
Reply with quote  
PostPosted: Mon Nov 06, 2017 6:33 pm 
Online
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 22423
Location: hants/dorset border
Has thanked: 1338 times
Been thanked: 3403 times
:welcomeuhm:

The pressure creeping up could be a couple of things, filler loop letting by (worth disconnecting if poss) or a pinholed heat exchanger.

It may well be that you have one issue causing the pressure to creep up whilst off and another causing the overpressure whilst running.

Best to get the guy that serviced it back...

EDIT bleed some water from a rad using a bleed key to get the pressure down to about 1.1 bar cold; fire up the heating. What does the pressure gauge rise to ??

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/



For this message the author wine~o has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Tue Nov 07, 2017 9:39 am 
Offline
Newly registered Member

Joined: Mon Nov 06, 2017 9:45 am
Posts: 4
Has thanked: 0 times
Been thanked: 0 times
Hi, thank you for the replies.

The problem with the pressure rising was immediately after the boiler had been serviced, but gradually appeared to slow down.

I bled the system down to 0.9 bar. I let a bit too much out to be honest but figured it's still in the ok-when-cold region. I put the heating on and it increased to 1.8, then crept up to 2.0 and stayed at 2.0 whilst the heating was on. One thing worth mentioning at this stage though is that 1 of the main radiators wasn't on last night because we'd just had some wallpapering done and were told to let it dry out naturally.

I checked the pressure again this morning and it was back down to 0.9, but today I'll fire up the system with the large radiator on again and see if it makes any difference.

It may be worth mentioning, I noticed the setting on the boiler for the radiator temperature was set on max (82 degrees) and I lowered it down to 75. Would this likely make any difference to the rate the pressure bar raises?


Top
 Profile  
Reply with quote  
PostPosted: Wed Nov 08, 2017 9:06 am 
Offline
Newly registered Member

Joined: Mon Nov 06, 2017 9:45 am
Posts: 4
Has thanked: 0 times
Been thanked: 0 times
So I turned the larger radiator back on yesterday, and upped the boiler radiator temperature to 80. After a couple of hours the pressure bar on the boiler had reached 2.5/2.6.

This morning the pressure on the boiler was sitting at 1.2; I'm not sure if that would be down to the fact there was still pressure in the system due to having the heating on, or if the pressure is just starting to creep up again.


Top
 Profile  
Reply with quote  
PostPosted: Wed Nov 08, 2017 4:46 pm 
Online
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 22423
Location: hants/dorset border
Has thanked: 1338 times
Been thanked: 3403 times
Dave (gas for you) will be able to advise further, but as the base pressure (cold pressure) increases after running the heating I would suspect a pinholed heat exchanger... :sad:

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


Top
 Profile  
Reply with quote  
PostPosted: Wed Nov 08, 2017 5:55 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 6304
Has thanked: 724 times
Been thanked: 762 times
If the plate was pin holed I would expect the pressure to increase all the time, regardless of whether the heating is on, as it would if the filling loop was letting by.

I still think the expansion vessel pressure needs checking, or the expansion vessel itself before anything else is considered.

If I ever go to a service where the customer says they are having to keep topping up the boiler, or the pressure rises too high I would always do this as a matter of course.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
Reply with quote  
PostPosted: Thu Nov 09, 2017 8:41 am 
Offline
Newly registered Member

Joined: Mon Nov 06, 2017 9:45 am
Posts: 4
Has thanked: 0 times
Been thanked: 0 times
Thanks again. I have our boiler engineer coming out on Tuesday morning. I explained the problem to him and his initial reply was also that it could either be the filling valves or the expansion vessel. Will update as he comes out.


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: D Hailsham and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO