Posted: Thu Oct 25, 2007 5:56 pm Post subject: Boiler Banging |
|
|
|
We had a new radiator added a while back but things have never really been correct since.
All the right valves in the airing cupboard have been opened but one, which i can't tell if off or on, but is stuck solid.
If we had the hot water on, the radiators would get hot, not just the towel rads. We are now trying to turn the heating on but the boiler or the pipework feeding the boiler are banging, and pretty loud at that. After the boiler turns off you can hear water running in the pipes as if these are not filled up correctly.
This valve that i can't open/close, would this have something to do with it?
The boiler is a Potterton Suprima 60
Can any pass any info on what maybe causing this to happen.
Thanks
Andy
in a slowly getting colder house in swindon |
|
| Back to top |
|
 |
|
|
 |
Hinton Heating Gas/Heating Expert

Joined: 16 Jan 2006 Posts: 4296 Location: Bournemouth
|
Posted: Thu Oct 25, 2007 6:01 pm Post subject: |
|
|
|
have you called back the company who fitted your new rad? _________________ www.hintonheating.com
 |
|
| Back to top |
|
 |
LyNx Junior Member
Joined: 10 May 2006 Posts: 16
|
Posted: Thu Oct 25, 2007 6:09 pm Post subject: |
|
|
|
it was a friend of a friend. He's been back to have a look but the boiler seemed fine then (5 months ago).
I think it's time to look at getting a new pair of eyes to look at it. |
|
| Back to top |
|
 |
Hinton Heating Gas/Heating Expert

Joined: 16 Jan 2006 Posts: 4296 Location: Bournemouth
|
Posted: Thu Oct 25, 2007 6:13 pm Post subject: |
|
|
|
what does the valve do, that you're not sure is open or closed?
have you checked the header tank is full? _________________ www.hintonheating.com
 |
|
| Back to top |
|
 |
LyNx Junior Member
Joined: 10 May 2006 Posts: 16
|
Posted: Thu Oct 25, 2007 6:13 pm Post subject: |
|
|
|
| Also to add. When the banging did happen whilst we was outside, water started running out of the Feed & Expansion Tank overflow pipe into the garden. |
|
| Back to top |
|
 |
LyNx Junior Member
Joined: 10 May 2006 Posts: 16
|
Posted: Thu Oct 25, 2007 6:14 pm Post subject: |
|
|
|
| To be honest mate, i couldn't tell you what this valve does, it's the only one not labeled up. |
|
| Back to top |
|
 |
Hinton Heating Gas/Heating Expert

Joined: 16 Jan 2006 Posts: 4296 Location: Bournemouth
|
Posted: Thu Oct 25, 2007 6:15 pm Post subject: |
|
|
|
sound like the boiler is overheating then.
could be the thermostats on the boiler, slow pump, boiler pcb, lack of water in system _________________ www.hintonheating.com
 |
|
| Back to top |
|
 |
LyNx Junior Member
Joined: 10 May 2006 Posts: 16
|
Posted: Thu Oct 25, 2007 6:21 pm Post subject: |
|
|
|
The header tank is full. I think this valve has something to do will the amount of water in the system, ie; not being topped up.
Does this sound right? |
|
| Back to top |
|
 |
Hinton Heating Gas/Heating Expert

Joined: 16 Jan 2006 Posts: 4296 Location: Bournemouth
|
Posted: Thu Oct 25, 2007 6:29 pm Post subject: |
|
|
|
it could be on the cold feed between the header tank & the system. If its closed then this could be casuing the problem. _________________ www.hintonheating.com
 |
|
| Back to top |
|
 |
LyNx Junior Member
Joined: 10 May 2006 Posts: 16
|
Posted: Thu Oct 25, 2007 6:33 pm Post subject: |
|
|
|
Thanks, i'll advice the plumber tomorrow then.
I can't open this valve for the life off me, so I can't check before hand
Thanks for the help |
|