Hi all,

I'd be grateful for some advice on how to wire in some new GU10 fittings. I bought these fire rated Minisun ones: https://www.amazon.co.uk/dp/B00GSPFK2O/ref=pe_3187911_185740111_TE_item

I will be removing the existing GU5.3 (MR16) fittings before starting. These fittings have a standard wiring: i.e. bulb to GU5.3 fitting to transformer to mains. The connection between the transformer and the mains uses wiring that's built into the transformer (i.e. two single wires, one each for live and neutral). The connection to the mains (which I assume is 2 core and earth) is done through a standard round junction box.

I'd like to know the best way to wire the mains to the new GU10 fittings once I've removed the transformer (and the GU5.3 fittings)

- Option 1: Is it safe to connect the mains directly into the choc box that is pre-attached to the GU10 fitting, i.e. removing the existing junction box and wiring the mains to the fitting? If I do this, the fittings are not class II, so I assume I would need to strip the mains wire sufficiently to be able to run the earth wire down to the metal body of the fitting. This doesn't seem very elegant to me, and I'm concerned that the external insulation will be gone and the choc box will only be gripping the wires themselves.

- Option 2: Would it be better to use Wago lighting connectors and a Wagobox? In which case, would I:

2A. Replace the choc box built into the GU10 fitting with a wagobox? I.e. by removing the existing junction box and then wiring both the mains and the bulb connector into the Wagobox. If so, would it matter that the wagobox was not fixed to the fitting, i.e. would this put stress on the connections? Or would it be better to attach the wagobox to the fitting, e.g. with a zip tie?

OR

2B. Use both a wagobox and the choc box on the GU10 fitting? I.e. by replacing the existing junction box with a wagobox, and then running a new wire between the wagobox and the choc box on the fitting. If so, what kind of wire would I need?

Thanks!!

Matt


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Wed Oct 25, 2017 5:43 pm 
Online
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 22423
Location: hants/dorset border
Has thanked: 1338 times
Been thanked: 3403 times
replace junction box with wagos unless the junction box is easily accessible. From there then 1mm twin and earth to each light using the connector blocks provided.

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/



For this message the author wine~o has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Wed Oct 25, 2017 8:05 pm 
Offline
Newly registered Member

Joined: Wed Oct 25, 2017 5:22 pm
Posts: 5
Has thanked: 0 times
Been thanked: 1 times
wine~o wrote:
replace junction box with wagos unless the junction box is easily accessible. From there then 1mm twin and earth to each light using the connector blocks provided.


Thanks for the advice! In which case I could pre-wire the new connector blocks with the twin and earth.

Why would I use twin and earth rather than 3 core flex? And is 1mm okay even if the existing mains cables are 1.5mm?

Thanks,

Matt



For this message the author Matteo2000 has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Wed Oct 25, 2017 9:29 pm 
Offline
BANNED

Joined: Wed Jun 14, 2017 8:38 am
Posts: 204
Has thanked: 696 times
Been thanked: 28 times
You can use flex as long it's at least 1mm in hindsight you could use less thickness wire if you was to use led bulbs however i always fit 1mm as I know when led blows most people don't have spare and end up fitting an halogen.

Sent from my LG-K100 using Tapatalk


Top
 Profile  
Reply with quote  
PostPosted: Wed Oct 25, 2017 10:11 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 6558
Has thanked: 32 times
Been thanked: 1100 times
The reason you use Twin and earth is because:

The answer is in the name, its flex (Flexible)
Twin and earth is for fixed items, such as wiring to ceiling roses, jbs etc
Flex is used for items that will be often moved.
Twin and earth is solid core, flex is multi stranded (which is why its flexible)

Also if you were to use flex it would have to be the same size as the supply cable (1mm minimum) but 1mm flex has all 3 cores insulated, (and its thicker insulation) so over all a flex is bigger than its counterpart Twin and earth

Since the fuse (protective device) is to protect the cable not what is on the end of it, it is for that reason that even if using LED lamps the cable must be the same size as the supply cable.

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Wed Oct 25, 2017 10:57 pm 
Offline
Newly registered Member

Joined: Wed Oct 25, 2017 5:22 pm
Posts: 5
Has thanked: 0 times
Been thanked: 1 times
Hi all,

Thanks for the advice with the cable. But I’m still not clear what I should be using. Someone-else, I don’t quite understand your logic. Surely GU10 fittings are the kind of thing that will be move more frequently (or at least at first) when you’re getting them into the ceiling?

I already have some 0.75 mm flex and wouldn’t make the mistake of putting a halogen in. But I won’t use it if it’s dangerous / against regs.

If I do end up using twin and earth then I don’t know how I can connect that to the blocks on the light fittings safely, as I’ll have to strip the exterior insulation for the earth wire.


Top
 Profile  
Reply with quote  
PostPosted: Wed Oct 25, 2017 11:15 pm 
Offline
Newly registered Member

Joined: Wed Oct 25, 2017 5:22 pm
Posts: 5
Has thanked: 0 times
Been thanked: 1 times
I’ve been reading about cable thickness and, since it’s on a 6 amp mcb, I think I’m fine to use 1 mm. 0.75 mm is rated at 6 amps so that might be cutting it too fine. I still don’t know whether to pick t&e or flex though!


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 26, 2017 5:32 am 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 6558
Has thanked: 32 times
Been thanked: 1100 times
Use twin and earth.

When you install twin and earth, yes you move it a bit, but once its in you never move it again.

Where as using an electric lawn mower for example (One with a flex) how often will the flex get moved in its life time? thousands, you walk up and down, side to side etc, then you coil up its lead, you couldn't do all that if it was twin and earth. (It would snap after a sometime any way)

When you install it on lights such as you have yes you strip it further than required to get the earth core, but then (ideally) you cut the surplus off before you connect it. (not forgetting to use earth sleeving.)

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here



For this message the author someone-else has received gratitude : multiman
Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 26, 2017 9:17 am 
Offline
Newly registered Member

Joined: Wed Oct 25, 2017 5:22 pm
Posts: 5
Has thanked: 0 times
Been thanked: 1 times
Hi someone-else,

Okay, thanks for the advice. And to be clear, we’re talking about the connection between the JB and the light fitting?

I can see that you don’t move the fittings that often, so why it would be fine to use twin and earth, but I still don’t understand what the advantage is of using twin and earth? The Wago light connectors assume there is flexible cable on the lighting side, and use levers rather than push in connectors on that side.


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 26, 2017 6:37 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 6558
Has thanked: 32 times
Been thanked: 1100 times
Matteo2000 wrote:
I still don’t understand what the advantage is of using twin and earth?


someone-else wrote:
Also if you were to use flex it would have to be the same size as the supply cable (1mm minimum) but 1mm flex has all 3 cores insulated, (and its thicker insulation) so over all a flex is bigger than its counterpart Twin and earth

Since the fuse (protective device) is to protect the cable not what is on the end of it, it is for that reason that even if using LED lamps the cable must be the same size as the supply cable.


Matteo2000 wrote:
The Wago light connectors assume there is flexible cable on the lighting side, and use levers rather than push in connectors on that side.


Wago's don't assume anything.
The fact is the wago's with levers are easier to use / re use.

_________________
Take it easy, a forum is only a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link. to find out more.

No such thing as "Thou shalt put this wire here, Thou shalt put that wire there" .............Take a picture BEFORE you do the job.

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here



For this message the author someone-else has received gratitude : multiman
Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Hilti


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO