Hi - hope someone can help me here before I have to call out the professionals!

About 7 months ago, I had a company round to fit a new boiler - Baxi SOLO. All has been running smoothly apart from it's needed to be reset a couple of times due to overheating.

However, it think this problem may be related. At the same time as fitting the boiler (in the kitchen) they also fitted a pipe stat in the airing cupboard next to the hot water cylinder (approx 25ft away from boiler).

I was told that the pipestat would make the pump run for a bit longer after the boiler had turned off to make sure there was no hot water sitting in the boiler. My CH/HW timer turns the boiler off at 8pm, however, sometimes at 2am or even 4am the pump is still running, which keeps my awake at night cause it's quite near the bedroom. I was sort of expecting 20 mins of extra pumping, not 6 hours.

Is this expected behaviour?

The pipestat is set for approx 25 degrees, so I'm guessing that once the temp in the water pipe comes down to the desired level, the pump will turn off. Or have I got this wrong and the pipe stat turns the pump off once the temp has gone UPTO a certain level i.e. for frost protection.

One night I played around with the pipe stat, turned it right up past 40 degrees and the pump stopped and I was able to get some sleep. However, this is one of the instances when the boiler over heated.

Any advice will be greatly appreciated!

thanks
Aidan


Top
 Profile  
 
 Post subject:
PostPosted: Wed Aug 12, 2009 4:19 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 4854
Location: Northampton
Has thanked: 65 times
Been thanked: 330 times
Last boiler I came across with these symptoms had been put in the wrong way round with the flow and return crossed over, might be worth seeing which pipe gets hot first at the boiler!

Which model is it exactly? Not all Solos need a pump overrun and if it does it's built into the boiler.

Only time the internal one doesn't get used is when theres not enough cores in the control cable and they can't be bothered to run a new one.

What does the installer have to say?


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 4:31 pm 
Offline
Newly registered Member

Joined: Wed Aug 12, 2009 3:23 pm
Posts: 6
Has thanked: 0 times
Been thanked: 0 times
It's a BAXI SOLO 3 PFL - I'm aware that it's not a super efficient boiler, but due to size and space restrictions this was acceptable to the installers - even received a Corgi certificate to explain this I think.

Installer needs to come round and have a look, but it's prooving hard to get them round at a suitable time.

Have called BAXI and they say it might be a PCB problem, so just arranging an engineer visit, but as it's an old boiler I'm hvaing to go through the process to prove the warranty.

thanks again!


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 5:21 pm 
Offline
OAP

Joined: Mon Mar 10, 2008 12:46 am
Posts: 39133
Has thanked: 181 times
Been thanked: 1983 times
Any reason they fitted an illegal boiler and space restriction is not an excuse. :wtf:

_________________
---------------------------------------------------------------------------------------------------

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

donnas-dream-house-charity-t52110.html


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 5:25 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 4854
Location: Northampton
Has thanked: 65 times
Been thanked: 330 times
Does sound somewhat dodgy, we had a nightmare getting an exemption to fit a BBU in a listed cottage, (first and last one I'll ever fit) and that was with the heritage people demanding it :shock:


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 5:26 pm 
Offline
Newly registered Member

Joined: Wed Aug 12, 2009 3:23 pm
Posts: 6
Has thanked: 0 times
Been thanked: 0 times
Not sure, I believed what they said, something about not having to fit a super efficient class A condensing boiler if the building, location etc were not fit for the super boiler.

They registered it with Corgi, and I received a certificate so I think it's all above board.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 6:04 pm 
Offline
Senior Member
User avatar

Joined: Fri Nov 14, 2008 4:47 pm
Posts: 1051
Location: surrey
Has thanked: 0 times
Been thanked: 4 times
sounds dodgy to me too :shock:

any chance of a picture of the installation, with some measurements added around the boiler?.........maybe something more up to date could have been fitted (WB,RI maybe :wink: )

also a picture of the flue on the outside please.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 7:07 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 3395
Has thanked: 43 times
Been thanked: 213 times
Solo 3 has a built in pump over run of approx 6-8 mins.

Pipe stat is not necessary for this purpose.

Sounds to me either it is interfering with the boiler pcb pump over run, or you have a didgy pcb.

I would go with the first one first.

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 7:51 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 4854
Location: Northampton
Has thanked: 65 times
Been thanked: 330 times
I'd bet the inbuilt overrun isn't being used there are enough lazy installers out there :-)


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 8:36 pm 
Offline
Senior Member

Joined: Mon Apr 13, 2009 8:03 pm
Posts: 3395
Has thanked: 43 times
Been thanked: 213 times
Good point.

Op, check there is a live for the pump from the pump/l terminal on the boiler.

You should have permanent live, sw/live and pump live all connected for this boiler to function properly :wink:

_________________
Dave

www.drlgas.co.uk


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Wed Aug 12, 2009 10:55 pm 
Offline
Newly registered Member

Joined: Wed Aug 12, 2009 3:23 pm
Posts: 6
Has thanked: 0 times
Been thanked: 0 times
I'm not sure how to check there is a live for the pump from the pump/l terminal on the boiler.

Photos as follows - as you can see the boiler is under the kitchen worktop, tucked right up into a corner between freezer and unit.

Dark outside tonight so cannot photo flue on outside just yet!

thanks for all help! much appreciated.

Images -
Image
Image
Image
Image
Image
Image
Image
Image


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Thu Aug 13, 2009 6:16 am 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 4854
Location: Northampton
Has thanked: 65 times
Been thanked: 330 times
If you turn the power off and remove the black plastic panel at the bottom left (2 screws) are there any wires in the first three terminals these are for the pump.


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Thu Aug 13, 2009 4:23 pm 
Offline
Senior Member
User avatar

Joined: Fri Nov 14, 2008 4:47 pm
Posts: 1051
Location: surrey
Has thanked: 0 times
Been thanked: 4 times
im sure that baxi will honour any guarantee with the pump not being wired directly to the boiler.

why couldnt a condensing boiler have been fitted on the wall above the worktop. the pics dont show us whats above at the moment, and you could have built a cupboard around it, if you didnt want the boiler on show.

I notice from the pics that the PRV & AAV are above the worktop, if finding a replacement boiler that fitted within that space was the main issue a WB,RI would have gone in there, with only the flue elbow above the worktop where
the PRV &AAV currently are.

get the installer to pull the power cable off of the gas pipe and clip it to the wall :roll:


the more I think about this post the fishier it becomes :scratch:


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Thu Aug 13, 2009 4:33 pm 
Offline
Senior Member
User avatar

Joined: Wed Nov 14, 2007 10:21 pm
Posts: 4854
Location: Northampton
Has thanked: 65 times
Been thanked: 330 times
I have to say the RI is my fave WB, I'd even fit one in me own house :wink:


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

 Post subject:
PostPosted: Thu Aug 13, 2009 4:42 pm 
Offline
Senior Member
User avatar

Joined: Fri Nov 14, 2008 4:47 pm
Posts: 1051
Location: surrey
Has thanked: 0 times
Been thanked: 4 times
Razor wrote:
I have to say the RI is my fave WB, I'd even fit one in me own house :wink:


you've said it now :lol:

the scruff & dave will be banging on about broags again in a minute :lol:

or will they be called 'broaxis' in the future. :roll: :lol:


Top
 Profile  
 
You may not be able to see the full post including pictures unless you register or log in

Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 23 posts ]  Go to page 1, 2  Next


Similar topics
   

Time zone: Europe/London


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  


News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO

 

Diy forum - Decking - plastering - Plumbing - DIY - Tiling