Got woke up with alarm going off, was just the internal alarm sound from the main control pad.

Had to enter my code to stop, it had a red light on the little hammer sign which indicates tamper.

I've had it a few times over the years now. Few months ago I went around all PIRs, removed covers, dusted checked micro switch, and was ok for a while.

I've had the main battery changed 3 years ago.

So to be honest the tamper probably isn't needed as if they are going to mess about with the outside alarm box which is high up in in trouble then anyway!

So is it easy to link out if it's this? Is the tamper worth it? Is it just one wire in the main box. Could it be anything else you think?

Thanks


Share on FacebookShare on TwitterShare on DiggShare on Delicious
Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 25, 2018 9:43 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 8695
Has thanked: 41 times
Been thanked: 1480 times
Depends what panel it is.
Some panels have "global tamper" others have a tamper for each circuit.

The idea of tamper is to protect all device on the alarm from...............being tampered with.
It could be that a joint is going high resistance or that a cable is damaged.
Dissconecting the tamper solves the problem, it does not solve the cause, ideally, you should get your multimeter out (you have got one, haven't you?) and check the resistance of the tamper circuit and take it from there.
As an aside, the external sounder usually has its own tamper, so linking out the tamper in the panel still leaves the sounder tamper working.

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Thu Oct 25, 2018 10:53 pm 
Offline
Senior Member

Joined: Thu Mar 28, 2013 5:57 pm
Posts: 180
Has thanked: 17 times
Been thanked: 2 times
someone-else wrote:
Depends what panel it is.
Some panels have "global tamper" others have a tamper for each circuit.

The idea of tamper is to protect all device on the alarm from...............being tampered with.
It could be that a joint is going high resistance or that a cable is damaged.
Dissconecting the tamper solves the problem, it does not solve the cause, ideally, you should get your multimeter out (you have got one, haven't you?) and check the resistance of the tamper circuit and take it from there.
As an aside, the external sounder usually has its own tamper, so linking out the tamper in the panel still leaves the sounder tamper working.

Sorry thought I'd put it in, it's a Scantronic 9448+ i believe with a remote keypad 9427 style.

It won't fix the cause your correct if linking it out, but is the tamper worth it in a house, can understand in business premises but not important in houses?


Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 26, 2018 5:19 am 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 8695
Has thanked: 41 times
Been thanked: 1480 times
MrMrMr wrote:
but is the tamper worth it in a house,


Yes.

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 26, 2018 5:21 am 
Offline
Senior Member

Joined: Thu Mar 28, 2013 5:57 pm
Posts: 180
Has thanked: 17 times
Been thanked: 2 times
someone-else wrote:
MrMrMr wrote:
but is the tamper worth it in a house,


Yes.

Why, if to stop tamper inside, it's too late, if for the bell box I can understand more, but if they decide to get ladders, mess with alarm box outside front of my house, I'm in trouble by then anyway.

So it's not a massive risk to link out in my scenario?


Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 26, 2018 2:38 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2786
Location: South Yorkshire
Has thanked: 177 times
Been thanked: 597 times
MrMrMr wrote:
someone-else wrote:
MrMrMr wrote:
but is the tamper worth it in a house,


Yes.

Why, if to stop tamper inside, it's too late, if for the bell box I can understand more, but if they decide to get ladders, mess with alarm box outside front of my house, I'm in trouble by then anyway.

So it's not a massive risk to link out in my scenario?


Half the alarm boxes I see have the tamper already shorted out. There are normally two tampers. One for the detectors and one for the bell box. The remote keypad (on the Veritas stuff I fit) does not have a tamper loop but it still has a tamper.


Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 26, 2018 3:09 pm 
Offline
Senior Member

Joined: Thu Mar 28, 2013 5:57 pm
Posts: 180
Has thanked: 17 times
Been thanked: 2 times
OnlyMe wrote:
MrMrMr wrote:
someone-else wrote:
MrMrMr wrote:
but is the tamper worth it in a house,


Yes.

Why, if to stop tamper inside, it's too late, if for the bell box I can understand more, but if they decide to get ladders, mess with alarm box outside front of my house, I'm in trouble by then anyway.

So it's not a massive risk to link out in my scenario?


Half the alarm boxes I see have the tamper already shorted out. There are normally two tampers. One for the detectors and one for the bell box. The remote keypad (on the Veritas stuff I fit) does not have a tamper loop but it still has a tamper.

Ok I'll have a look over the Weekend and no doubt ask what to link out ha ha..

When you say the remote keypad hasn't got a tamper loop but has a tamper what does this mean please? Anything I can check on this?

Thanks


Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 26, 2018 5:52 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 8695
Has thanked: 41 times
Been thanked: 1480 times
MrMrMr wrote:
When you say the remote keypad hasn't got a tamper loop but has a tamper what does this mean please?


It means what it says. That the RKP has a tamper, but it is not wired into the tamper loop.

May I also ask when you reply PLEASE stop using the quote button for everything that has been said.

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Fri Oct 26, 2018 10:58 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2786
Location: South Yorkshire
Has thanked: 177 times
Been thanked: 597 times
MrMrMr wrote:
When you say the remote keypad hasn't got a tamper loop but has a tamper what does this mean please? Anything I can check on this?

Thanks


All you can do is check that the lid on the keypad is secure. There is a microswitch behind the lid. You cannot link it out as there are no user terminals for it. The keypad communicates with the panel using data signals.


Top
 Profile  
Reply with quote  
PostPosted: Mon Dec 24, 2018 10:54 pm 
Offline
Senior Member

Joined: Thu Mar 28, 2013 5:57 pm
Posts: 180
Has thanked: 17 times
Been thanked: 2 times
So I linked out the tamper, according to the manual, for the PIRs. Just had the alarm go off for tamper again....was ok for a few days as well before this.

So does this mean its the bell box or the keypad? (I doubt that keypad as seems secure).

I couldn't work out the bell box tamper to link it out, could someone help with this please?

I'll take the remote keypad off again but as already mentioned you can't link this out think anyway.


Top
 Profile  
Reply with quote  
PostPosted: Mon Dec 24, 2018 11:50 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 8695
Has thanked: 41 times
Been thanked: 1480 times
You put a link between 0v and Tr

But if there is a problem with the sounder itself, it will still activate, because all the link does is tell the panel not to activate, but at least you will have a better idea of what is what.

Question: How exactly did you link out the global tamper?

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Mon Dec 24, 2018 11:57 pm 
Offline
Senior Member

Joined: Thu Mar 28, 2013 5:57 pm
Posts: 180
Has thanked: 17 times
Been thanked: 2 times
I linked the A/T (anti tamper) on the main box out together, as in the pic now from the manual in the grey link. This will link out all the PIRs. Is this correct? If so I've filled out the PIR tamper have a problem?

Image

The sounder/bell box wasn't sure how to link out, the drawings shown below is from the manual if you can help?
Image


Top
 Profile  
Reply with quote  
PostPosted: Tue Dec 25, 2018 12:53 am 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 8695
Has thanked: 41 times
Been thanked: 1480 times
No idea what you mean when you said "If so I've filled out the PIR tamper have a problem?"



My answer to linking out the external sounder tamper still stands

You put a link between 0v and Tr

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here


Top
 Profile  
Reply with quote  
PostPosted: Tue Dec 25, 2018 2:01 am 
Offline
Senior Member

Joined: Thu Mar 28, 2013 5:57 pm
Posts: 180
Has thanked: 17 times
Been thanked: 2 times
someone-else wrote:
No idea what you mean when you said "If so I've filled out the PIR tamper have a problem?"

Typo, meant to say "... Linked out the"

someone-else wrote:
My answer to linking out the external sounder tamper still stands

You put a link between 0v and Tr

Didn't realise this was for external sounder sorry, thought was referencing the PIR.

Thanks


Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 12, 2019 10:15 am 
Offline
Senior Member

Joined: Thu Mar 28, 2013 5:57 pm
Posts: 180
Has thanked: 17 times
Been thanked: 2 times
Well went away but last 2 days it's went off lots.

Is there a way to just disable tamper altogether? Everytime it's went off its been unarmed and the tamper light is only one that comes on.

Yesterday it took a few goes before it stopped sounding.

I'm off today so need to try and do something a bit more permanent. I presume from above I've linked out the PIR tamper, above says I can't link out remote keypad, but can I link out the outside siren? I can't with out how to.

Thanks


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 33 posts ]  Go to page 1, 2, 3  Next

 

 




Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO