Hi All

We had an electrician in to wire up a 3A switched spur to our new Aqualisa shower pump situated in the loft. He wired it directly into the lighting circuit in the loft without an FCU. He says it is protected by the 6A lighting circuit and that it is safe and within regulations.

A number of questions arise as Aqualisa say this would break their guarantee if anything went wrong. I have thus disconnected it.

Firstly the 6A lighting circuit is actual on an MK LN5910 10B fuse. Isn't this a 10A fuse?

Aqualisa say the pump must be connected via a 3A switched spur via a 32A ring main and not a lighting circuit. Aqualisa also say it can't be on any other circuit due to fluctuations. If connected into an FCU connected to the lighting circuit does this matter as the electrician says that he can still do this?

Reading some of the forum I see that the FCU must be placed within the length of the flex from the unit, which is under 3m. Aqualisa recommend being able to switch the unit off when it's really hot outside like now. So I need an accessible switch in the airing cupboard. Can I actually just extend their cable so that the FCU is sited downstairs in the airing cupboard? Alternatively could I site the FCU next to the pump in the loft and then put a switch in the spur so that I can locate the switch in the airing cupboard?

Without having to lift carpets and floorboards, there is an easy accessible ring main downstairs that I could add a spur to and bring it up into the airing cupboard to site an FCU or switch. Reading the forums there are limits on the length of a spur. As I don't understand or have read the regulations about voltage drops I need to know whether this would work.

My alternative and a lot more work is to lift carpets and cut into flooring to connect into an upstairs ring main, which I'm trying to avoid at present.

Thanks


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Fri Jul 27, 2018 6:55 pm 
Online
Senior Member
User avatar

Joined: Sat Jan 10, 2009 3:49 pm
Posts: 23924
Location: hants/dorset border
Has thanked: 1485 times
Been thanked: 3791 times
:welcomeuhm:

First things first; The MI's always have to be followed.

Quote:
Aqualisa say the pump must be connected via a 3A switched spur via a 32A ring main and not a lighting circuit. Aqualisa also say it can't be on any other circuit due to fluctuations. If connected into an FCU connected to the lighting circuit does this matter as the electrician says that he can still do this?


The only possible difference is that the lighting circuit may not be connected to an RCD; (depends on your particular CU) they are talking out of they're arris regards fluctuation...

Most shower pumps will draw less than 150 Watts. so the lighting circuit can normally be employed.

However the SFCU is a must, so that in the event of a fault the shower pump can be easily isolated without isolating the lighting circuit. (fault may occur in the dark)

Other stuff to be considered... soo get back to us if you need more.

_________________
Verwood Handyman

Verwood Handyman


___________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk/


Top
 Profile  
Reply with quote  
PostPosted: Sat Jul 28, 2018 1:12 pm 
Online
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2696
Location: South Yorkshire
Has thanked: 166 times
Been thanked: 581 times
As wine~o says the RCD protection is probably a must.

I would probably fit a passive RCD switched fused spur and use the lighting circuit.


Top
 Profile  
Reply with quote  
PostPosted: Mon Jul 30, 2018 9:27 am 
Offline
Newly registered Member

Joined: Fri Jul 27, 2018 11:11 am
Posts: 2
Has thanked: 0 times
Been thanked: 0 times
Thanks for the advice.
I need the 5 year guarantee so will follow the MIs and definitely fit a switched FCU.


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

 

 




Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO