Hi folks. Probably an impossible question to get an answer to but my elderly parents are struggling with this and 3 electricians who've been out haven't done anything apart from take money off them. My dad has Parkinsons and needs a lot of care from my mother so this is last thing they need

Am not in mood for any trolls or forum-guardians making smart remarks so please only answer if you have something constructive to add.

Situation:

  • when fuse blows boiler and downstairs sockets don't work. upstairs sockets. all lights and cooker-switch work
  • you can't quickly check if fuse has blown as they are cartridge type so we've spent nearly £20 on replacements already
  • 1st one lasted a few hours, 2nd one a bit less, 3rd and 4th a few minutes
  • strangely more appliances were plugged in (tv, lamps, sky router etc) when fuses were lasting longer. only thing plugged in when last one blew was alarm thing to social services (thing that monitors if a pensioner has fallen or something)
  • today I removed all the faceplates from the sockets to check for loose wires. found none but one socket (washing machine) was full of slugs and gunge and earth plate was rusty. I cleaned it, dried it out and re-connected it
  • no improvement after cleaning the slug-filled box


So what's next? Electricians tearing up the house to re-wire it (as floated by one of the guys who came this morning) or can someone with the right diagnostic gear home-in on the problem without that.

Also. One of the electricians said it's an appliance that's causing it. Why doesn't the (lower-rated) fuse in the appliance plug (eg 13 amp) blow before the 30amp one?


Share on FacebookShare on TwitterShare on DiggShare on DeliciousShare on Google+
Top
 Profile  
Reply with quote  
PostPosted: Thu Apr 19, 2018 11:56 pm 
Offline
Senior Member

Joined: Sat Sep 01, 2012 7:03 pm
Posts: 7955
Has thanked: 45 times
Been thanked: 1358 times
foy9999 wrote:
Also. One of the electricians said it's an appliance that's causing it. Why doesn't the (lower-rated) fuse in the appliance plug (eg 13 amp) blow before the 30amp one?


Different type of fuse.

The cartridge fuses often used in power distribution / consumers unit fuse carriers are designed to "blow" quickly, where as a plugtop fuse isn't.

With that in mind, i would suggest you unplug one appliance for say 2 days and see what happens, then plug that back in and un plug something else.

I am not sticking up for any of the electricians in particular, but finding an intermittent fault such as this, can and often is a PITA, and unless the fault is there at the time, its doubtful they will find it in minutes, hence unplug things and see.

The other thing to do is to note what is on / being used at the time.

Also, don't bother with stuff that works after the fuse has gone as that is on another circuit (I believe you said its only the down stairs sockets that stop, so it must be something plugged in downstairs)

Also note what IS plugged in, and what is ON when the fuse blows.

As an aside its NOT the number of items plugged in that cause problems, its how much current the plugged in items are using. e.g. I could have 15 mobile phone chargers plugged in all over the place, but they would use less than just one electric fire.

_________________
Fret not, a forum is a collection of opinions. Above, are mine.

Which is correct? Metre or Meter? Click the link to find out more.

Working on anything electrical? have you got a multi meter? why not? Would you hit a nail with a shoe?

If gloom had a voice, it would be me. :mrgreen:

:idea1: How to post a picture on this forum Click here



For this message the author someone-else has received gratitude : foy9999
Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 2:25 pm 
Offline
Senior Member
User avatar

Joined: Tue May 10, 2011 3:43 am
Posts: 2675
Location: North Wales
Has thanked: 64 times
Been thanked: 543 times
Not many houses still use fuses, and it will depend on make of fuse box, but Wilex did a converter so you can replace the fuse with a MCB, so when it trips it is a simple turn it back on again.

I have just had a problem with garage, the guy fitting roof was hammering and power went off, I replaced fuse (13A) reset RCD and MCB and it went off again, got out multi-meter no fault shown, got insulation tester out and within spec. So took a guess and swapped supply cable and all OK.

Be it a mouse, rat, squirrel, rotting cable, cable with water in, finding the fault can be hard. Again dad's house I knew when fitting a RCD the wiring was faulty, it would regularly trip the RCD, but when rewiring no fault found.



For this message the author ericmark has received gratitude : foy9999
Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 7:30 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2697
Location: South Yorkshire
Has thanked: 166 times
Been thanked: 581 times
someone-else wrote:
foy9999 wrote:
Also. One of the electricians said it's an appliance that's causing it. Why doesn't the (lower-rated) fuse in the appliance plug (eg 13 amp) blow before the 30amp one?


Different type of fuse.

The cartridge fuses often used in power distribution / consumers unit fuse carriers are designed to "blow" quickly, where as a plugtop fuse isn't.


Maybe a different type of fuse but the cartridge fuse is NOT a quick blow fuse.

Plug top fuses are BS 1362 and the OP probably has BS88 or BS 1361 fuses in the fuse box.



For this message the author OnlyMe has received gratitude : foy9999
Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 7:33 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2697
Location: South Yorkshire
Has thanked: 166 times
Been thanked: 581 times
You have a LN or LE fault (ie a damaged cable). A sparks should be able to at least decide which you have and track down a rough area where the fault lies.



For this message the author OnlyMe has received gratitude : foy9999
Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 7:59 pm 
Offline
Senior Member

Joined: Fri Oct 09, 2009 12:04 am
Posts: 162
Location: East Kilbride
Has thanked: 53 times
Been thanked: 5 times
OnlyMe wrote:
someone-else wrote:
foy9999 wrote:
Also. One of the electricians said it's an appliance that's causing it. Why doesn't the (lower-rated) fuse in the appliance plug (eg 13 amp) blow before the 30amp one?


Different type of fuse.

The cartridge fuses often used in power distribution / consumers unit fuse carriers are designed to "blow" quickly, where as a plugtop fuse isn't.


Maybe a different type of fuse but the cartridge fuse is NOT a quick blow fuse.

Plug top fuses are BS 1362 and the OP probably has BS88 or BS 1361 fuses in the fuse box.


Good to get a 2nd opinion as I can't agree or disagree any points made as I'm not an electrician. Still finding it hard to understand why the bigger fuse would blow before the smaller one.

Anyway to address your comment more directly...

I've just looked at the fuses I brought home in my pocket yesterday. Original is marked MEM 30LC 30A BS1361 and the ones I put in (from B&Q) are LAWSON LD 30A BS1361 240V so you're spot-on with that :salute:


Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 8:07 pm 
Offline
Senior Member

Joined: Fri Oct 09, 2009 12:04 am
Posts: 162
Location: East Kilbride
Has thanked: 53 times
Been thanked: 5 times
Bit of an update (text from my brother)....

Says electrician has been and thinks he's fixed it: "changed the socket and stripped some of the wire off the washing machine socket"

Am not sure if that means two sockets were involved (washing machine and another) but am thinking now the slug-filled box was mb the problem after all.

I took it apart, cleaned & dried it and scraped the corrosion off the earth bridge thing. Like a thin metal strap that connects the two contacts the top pins of the plugs go into. I didn't think to do anything to the 3 wires leading to it other than clean all the gunk off them. Sounds like the electrician went in a little deeper


Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 8:20 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2697
Location: South Yorkshire
Has thanked: 166 times
Been thanked: 581 times
foy9999 wrote:
OnlyMe wrote:
someone-else wrote:
foy9999 wrote:
Also. One of the electricians said it's an appliance that's causing it. Why doesn't the (lower-rated) fuse in the appliance plug (eg 13 amp) blow before the 30amp one?


Different type of fuse.

The cartridge fuses often used in power distribution / consumers unit fuse carriers are designed to "blow" quickly, where as a plugtop fuse isn't.


Maybe a different type of fuse but the cartridge fuse is NOT a quick blow fuse.

Plug top fuses are BS 1362 and the OP probably has BS88 or BS 1361 fuses in the fuse box.


Good to get a 2nd opinion as I can't agree or disagree any points made as I'm not an electrician. Still finding it hard to understand why the bigger fuse would blow before the smaller one.

Anyway to address your comment more directly...

I've just looked at the fuses I brought home in my pocket yesterday. Original is marked MEM 30LC 30A BS1361 and the ones I put in (from B&Q) are LAWSON LD 30A BS1361 240V so you're spot-on with that :salute:



A 30A BS1361 fuse takes about 125A to trip in about 5 seconds.

A 13A plug top (BS1362) fuse trips in about 0.4 sec at 100A and 5 seconds at 60A.



For this message the author OnlyMe has received gratitude : foy9999
Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 8:39 pm 
Offline
Approved Electrician

Joined: Sun Apr 24, 2011 7:01 pm
Posts: 2697
Location: South Yorkshire
Has thanked: 166 times
Been thanked: 581 times
foy9999 wrote:
Bit of an update (text from my brother)....

Says electrician has been and thinks he's fixed it: "changed the socket and stripped some of the wire off the washing machine socket"

Am not sure if that means two sockets were involved (washing machine and another) but am thinking now the slug-filled box was mb the problem after all.

I took it apart, cleaned & dried it and scraped the corrosion off the earth bridge thing. Like a thin metal strap that connects the two contacts the top pins of the plugs go into. I didn't think to do anything to the 3 wires leading to it other than clean all the gunk off them. Sounds like the electrician went in a little deeper


Hopefully that is job done.



For this message the author OnlyMe has received gratitude : foy9999
Top
 Profile  
Reply with quote  
PostPosted: Fri Apr 20, 2018 8:42 pm 
Offline
Senior Member

Joined: Fri Oct 09, 2009 12:04 am
Posts: 162
Location: East Kilbride
Has thanked: 53 times
Been thanked: 5 times
OnlyMe wrote:

A 30A BS1361 fuse takes about 125A to trip in about 5 seconds.

A 13A plug top (BS1362) fuse trips in about 0.4 sec at 100A and 5 seconds at 60A.


Now that makes sense to me but am still confused as to why the appliance fuses didn't blow before the cartridge. Don't suppose it matters as long as it's fixed.

I was thinking if the fault lay in the socket/wiring the fuse could (theoretically) blow with no appliances attached to the circuit. But then do you not need something connected to draw current round the circuit?

Thing is the boiler (well the wiring to it) is on the same circuit as the sockets and I think that's hard-wired (ie no plug or switch) so mb even with all the appliances (lamps/router/tv) unplugged it was drawing current.

Forgive my ramblings, but I like to understand these things :scratch:


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 

 

 




Similar topics
   

Time zone: Europe/London [ DST ]


Who is online

Users browsing this forum: No registered users and 3 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Visit Solent plastics


 

 

 

News News Site map Site map SitemapIndex SitemapIndex RSS Feed RSS Feed Channel list Channel list
ultimatehandyman privacy policy

Contact

 

Powered by phpBB® Forum Software © phpBB Group

phpBB SEO